Answer / prodip das
1. we have to select cable
for that first calculate current=12X1000/1.73x400x.95
=19 Amps
Type of cables= single core NYY(Red/Yellow/Blue/Green)
Cable size3x1CNYY
NYY 2.5 sq.mm
(ccc)=19.61A
Group rating=.68
sand bed=.90
Rating factor=.68x.90=.61
Actual CCC OF 2.5SQ.MM CABLE
=19.6X.61=11.96A
=26.20x.61=15.98
=33.63x.61=20.5143(OK)6 sq.mm
Votlage drop as per IEE regulation
Distance=10m(more)
=5.9x10x.152=8.968V(ok)
Finally SWG=6sq.mm
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / abdulsubur
FROM THE FORMULA P=ROOT3 VICOS PHI
12/ROOT3*400*.85 WE GET I=20
VD= MV*L*I/1000
WE GET 10 SQR MM+EARTH CABLE 6 SQR MM
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / phanendra babu
the selected cable should have the capability of
withstanding the over load /short ckt currents upto before
operating the protecting device. so assume 0.81 p.f,the load
current is given by apprx 20A .very safe working of copper
cable is 4A to 6A per 1sqmm ,so the size of the cable
suitable for 12kw motor is 6sqmm. copper cable or 16 sqmm
aluminum cable.
the above calculation is for lo current ratings if current
rating increases capacity will decrease.
Is This Answer Correct ? | 4 Yes | 1 No |
The cable size will depend on the you rated voltage and
cable route you can reffered to
IEC 60364-5-52 Electrical installations of buildings -
Selection and erection of electrical equipment - Wiring
systems
or from electrical installation guid from schneider site.
Is This Answer Correct ? | 5 Yes | 4 No |
How can maintain our H.T. motors used in cement plant. please send me procedure.
how many voltage or current enough to kill a person?
is KVAR (not reverse power) relay necessary to protect from excitor field failure on a brushless, synchroneus generator? Some people with previos experince tell me no but the manufacturers tell me it is designed for that purpose. Is it that it is only necessary for brushless generators and not the older style with the slip rings and brushes?
defined power system?
Explain the working principle of Vacuum circuit breaker and Air circuit breaker
10 Answers HP, Trinidad and Tobago Electricity Commission T TEC,
BSNL TTA EXAM QUESTION
During underground cabling in landscape area what did we cover the cable with to prevent the electric shock & protect the cable?
why the crow do not feel the current in overhead line when it sits on the wire??????
difference between local breaker backup relay or backup protection relay ?
can any tell me why slope 40% and 80% is calculated in differential protection?
how u measure/calculate renge of capacitor,capacitor has no any rating tag.what is the theory of measure of capacitons.
We are preparing another project which involves Waste heat recovery from a 1 MW GE Engine. The Engine in particular gives out flue gas at 487Deg C with a flow rate of 5650 kg/hour and this can be cooled to 180 Deg C. This gives a thermal output of ~ 594 KW that is available for input to VAM via heat exchanger / boiler. Additionally 581 KW will be available from engine jacket water (temperature profile 80/ 80 Deg C and a flow rate of 50m3/hr) Our estimation is that 300 TR of cooling is possible with a suitable VAM machine(s). Please advise what is the most suitable arrangement with maximum TR and min Capital expenditure. plz reply me as early as possible