for 12KW motor which cable size has to select for ex.10
meter.
Answers were Sorted based on User's Feedback
Answer / prodip das
1. we have to select cable
for that first calculate current=12X1000/1.73x400x.95
=19 Amps
Type of cables= single core NYY(Red/Yellow/Blue/Green)
Cable size3x1CNYY
NYY 2.5 sq.mm
(ccc)=19.61A
Group rating=.68
sand bed=.90
Rating factor=.68x.90=.61
Actual CCC OF 2.5SQ.MM CABLE
=19.6X.61=11.96A
=26.20x.61=15.98
=33.63x.61=20.5143(OK)6 sq.mm
Votlage drop as per IEE regulation
Distance=10m(more)
=5.9x10x.152=8.968V(ok)
Finally SWG=6sq.mm
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / abdulsubur
FROM THE FORMULA P=ROOT3 VICOS PHI
12/ROOT3*400*.85 WE GET I=20
VD= MV*L*I/1000
WE GET 10 SQR MM+EARTH CABLE 6 SQR MM
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / phanendra babu
the selected cable should have the capability of
withstanding the over load /short ckt currents upto before
operating the protecting device. so assume 0.81 p.f,the load
current is given by apprx 20A .very safe working of copper
cable is 4A to 6A per 1sqmm ,so the size of the cable
suitable for 12kw motor is 6sqmm. copper cable or 16 sqmm
aluminum cable.
the above calculation is for lo current ratings if current
rating increases capacity will decrease.
| Is This Answer Correct ? | 4 Yes | 1 No |
The cable size will depend on the you rated voltage and
cable route you can reffered to
IEC 60364-5-52 Electrical installations of buildings -
Selection and erection of electrical equipment - Wiring
systems
or from electrical installation guid from schneider site.
| Is This Answer Correct ? | 5 Yes | 4 No |
why transformer rating is always in KVA
What is Peterson coil? Where it is used?
in soft starter system for 375 KW 3 ph induction motor for multi stage vertical pump, two thyristers failed causing shorting of thyrister. the motor winding failed while starting.What is the cause and what is the effect in above case
how to calculate the megger values for motors and cables?
what is the use of switch disconnector fuse
If the Brush of DC motor is shifted by 90 deg, then what happens to voltage and torque? Both voltage and torque are zero. how to justify the answer?
neutral earth resistance testing is it possible for transformer while in load condition
what modulation is used in landline telephone signals?
If we give the 440 V supply at secondary winding of the transformer then what will affect at primary winding???????
Why SF6,VCB,Oil Ckt Breakers are use in HT Side need brief information ?
How to select the earthing transformer,for DELTA TO DELTA TRANSFORMER OR ALTERNATOR SIDE.Pls post your answers and calculation.
3Cx240 & 3Cx300 sqmm Al. cable from lv side. What is the calculation for this cable??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)