for 12KW motor which cable size has to select for ex.10
meter.
Answers were Sorted based on User's Feedback
Answer / prodip das
1. we have to select cable
for that first calculate current=12X1000/1.73x400x.95
=19 Amps
Type of cables= single core NYY(Red/Yellow/Blue/Green)
Cable size3x1CNYY
NYY 2.5 sq.mm
(ccc)=19.61A
Group rating=.68
sand bed=.90
Rating factor=.68x.90=.61
Actual CCC OF 2.5SQ.MM CABLE
=19.6X.61=11.96A
=26.20x.61=15.98
=33.63x.61=20.5143(OK)6 sq.mm
Votlage drop as per IEE regulation
Distance=10m(more)
=5.9x10x.152=8.968V(ok)
Finally SWG=6sq.mm
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / abdulsubur
FROM THE FORMULA P=ROOT3 VICOS PHI
12/ROOT3*400*.85 WE GET I=20
VD= MV*L*I/1000
WE GET 10 SQR MM+EARTH CABLE 6 SQR MM
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / phanendra babu
the selected cable should have the capability of
withstanding the over load /short ckt currents upto before
operating the protecting device. so assume 0.81 p.f,the load
current is given by apprx 20A .very safe working of copper
cable is 4A to 6A per 1sqmm ,so the size of the cable
suitable for 12kw motor is 6sqmm. copper cable or 16 sqmm
aluminum cable.
the above calculation is for lo current ratings if current
rating increases capacity will decrease.
| Is This Answer Correct ? | 4 Yes | 1 No |
The cable size will depend on the you rated voltage and
cable route you can reffered to
IEC 60364-5-52 Electrical installations of buildings -
Selection and erection of electrical equipment - Wiring
systems
or from electrical installation guid from schneider site.
| Is This Answer Correct ? | 5 Yes | 4 No |
Why we choose 400kv,220kv,132kv,66kv,33kv transmission voltages for transmitting power. Why not other voltage levels.
21 Answers College School Exams Tests, HC, HCL, Jaypee, JPMorgan Chase,
why sometime we get electrical shock while touching the ballon of dish tv connection ? which we should not get.
What should be the percentage increase in length of the dead end clamp for bus bar conductor (Hawthorn) after hydraulic pressing and what should be the applied pressure?
how to calculation increase capacitor,increase power factor for three phase.
What are various power system instabilities and what are their effects on power system operation?
In Slip ring Induction Motor we use Liquid Rotor Starter for Starter Every Time Liquid Filling we need add Soda Sodium Carbonate or only Distilled water is Enough.
why we use 3 phase in our country?..why no 4,5 or 2??
We have 2 no. 4MW DG set. and GEB supply. But, we running, only 1 DG set. when we done APFC/Power factor setting : 0.90, then winding temp. Low. but when setting done : 0.83, then Winding temp. increase. WHY Why ? ? ?, plz give me answer.
Is single load(eg: three phase motor) having all the components like positive,negative,zero sequence components during fault condition?
how dc load convert to ac load
What is the difference between Neutral and Eatrh?
In diesel generator how AVR get voltage to excitation. And basic diagram DG EXCITATION CIRCUIT.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)