Answer / prodip das

1. we have to select cable
for that first calculate current=12X1000/1.73x400x.95
=19 Amps

Type of cables= single core NYY(Red/Yellow/Blue/Green)
Cable size3x1CNYY
NYY 2.5 sq.mm
(ccc)=19.61A
Group rating=.68
sand bed=.90
Rating factor=.68x.90=.61
Actual CCC OF 2.5SQ.MM CABLE
=19.6X.61=11.96A
=26.20x.61=15.98
=33.63x.61=20.5143(OK)6 sq.mm

Votlage drop as per IEE regulation
Distance=10m(more)
=5.9x10x.152=8.968V(ok)
Finally SWG=6sq.mm

Is This Answer Correct ?    7 Yes 3 No

for 12KW motor which cable size has to select for ex.10 meter...

Answer / abdulsubur

FROM THE FORMULA P=ROOT3 VICOS PHI

12/ROOT3*400*.85 WE GET I=20
VD= MV*L*I/1000
WE GET 10 SQR MM+EARTH CABLE 6 SQR MM

Is This Answer Correct ?    5 Yes 2 No

for 12KW motor which cable size has to select for ex.10 meter...

Answer / phanendra babu

the selected cable should have the capability of
withstanding the over load /short ckt currents upto before
operating the protecting device. so assume 0.81 p.f,the load
current is given by apprx 20A .very safe working of copper
cable is 4A to 6A per 1sqmm ,so the size of the cable
suitable for 12kw motor is 6sqmm. copper cable or 16 sqmm
aluminum cable.

the above calculation is for lo current ratings if current
rating increases capacity will decrease.

Is This Answer Correct ?    4 Yes 1 No

for 12KW motor which cable size has to select for ex.10 meter...

Answer / m.mousa

The cable size will depend on the you rated voltage and
cable route you can reffered to
IEC 60364-5-52 Electrical installations of buildings -
Selection and erection of electrical equipment - Wiring
systems
or from electrical installation guid from schneider site.

Is This Answer Correct ?    5 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

How can maintain our H.T. motors used in cement plant. please send me procedure.

0 Answers  


how many voltage or current enough to kill a person?

12 Answers  


is KVAR (not reverse power) relay necessary to protect from excitor field failure on a brushless, synchroneus generator? Some people with previos experince tell me no but the manufacturers tell me it is designed for that purpose. Is it that it is only necessary for brushless generators and not the older style with the slip rings and brushes?

1 Answers  


defined power system?

3 Answers   Spanco,


Explain the working principle of Vacuum circuit breaker and Air circuit breaker

10 Answers   HP, Trinidad and Tobago Electricity Commission T TEC,






BSNL TTA EXAM QUESTION

0 Answers   BSNL,


During underground cabling in landscape area what did we cover the cable with to prevent the electric shock & protect the cable?

0 Answers  


why the crow do not feel the current in overhead line when it sits on the wire??????

6 Answers  


difference between local breaker backup relay or backup protection relay ?

1 Answers  


can any tell me why slope 40% and 80% is calculated in differential protection?

0 Answers  


how u measure/calculate renge of capacitor,capacitor has no any rating tag.what is the theory of measure of capacitons.

0 Answers   Marriott,


We are preparing another project which involves Waste heat recovery from a 1 MW GE Engine. The Engine in particular gives out flue gas at 487Deg C with a flow rate of 5650 kg/hour and this can be cooled to 180 Deg C. This gives a thermal output of ~ 594 KW that is available for input to VAM via heat exchanger / boiler. Additionally 581 KW will be available from engine jacket water (temperature profile 80/ 80 Deg C and a flow rate of 50m3/hr) Our estimation is that 300 TR of cooling is possible with a suitable VAM machine(s). Please advise what is the most suitable arrangement with maximum TR and min Capital expenditure. plz reply me as early as possible

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)