Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


for 12KW motor which cable size has to select for ex.10
meter.

Answers were Sorted based on User's Feedback



for 12KW motor which cable size has to select for ex.10 meter...

Answer / prodip das

1. we have to select cable
for that first calculate current=12X1000/1.73x400x.95
=19 Amps

Type of cables= single core NYY(Red/Yellow/Blue/Green)
Cable size3x1CNYY
NYY 2.5 sq.mm
(ccc)=19.61A
Group rating=.68
sand bed=.90
Rating factor=.68x.90=.61
Actual CCC OF 2.5SQ.MM CABLE
=19.6X.61=11.96A
=26.20x.61=15.98
=33.63x.61=20.5143(OK)6 sq.mm

Votlage drop as per IEE regulation
Distance=10m(more)
=5.9x10x.152=8.968V(ok)
Finally SWG=6sq.mm

Is This Answer Correct ?    7 Yes 3 No

for 12KW motor which cable size has to select for ex.10 meter...

Answer / abdulsubur

FROM THE FORMULA P=ROOT3 VICOS PHI

12/ROOT3*400*.85 WE GET I=20
VD= MV*L*I/1000
WE GET 10 SQR MM+EARTH CABLE 6 SQR MM

Is This Answer Correct ?    5 Yes 2 No

for 12KW motor which cable size has to select for ex.10 meter...

Answer / phanendra babu

the selected cable should have the capability of
withstanding the over load /short ckt currents upto before
operating the protecting device. so assume 0.81 p.f,the load
current is given by apprx 20A .very safe working of copper
cable is 4A to 6A per 1sqmm ,so the size of the cable
suitable for 12kw motor is 6sqmm. copper cable or 16 sqmm
aluminum cable.

the above calculation is for lo current ratings if current
rating increases capacity will decrease.

Is This Answer Correct ?    4 Yes 1 No

for 12KW motor which cable size has to select for ex.10 meter...

Answer / m.mousa

The cable size will depend on the you rated voltage and
cable route you can reffered to
IEC 60364-5-52 Electrical installations of buildings -
Selection and erection of electrical equipment - Wiring
systems
or from electrical installation guid from schneider site.

Is This Answer Correct ?    5 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

DOES AN EARTH FAULT CURRENT ON THE DELTA SIDE OF A 6.6/33KV STEP UP STAR-DELTA CONNECTED TRANSFORMER REFLECT ON THE STAR SIDE? IF YES, THEN HOW AND WHAT IS THE AMOUNT OF CURRENT REFLECTED?

1 Answers  


Power Factor Controller

1 Answers  


Please clarify, 1. Is it required to lay two runs of GI wire along with Armoured LT cable if it is laid between one big mains (63Amps TPN SDF) to small main (32A TPN SDF) with proper glanding termination? 2. If the armoured cable with proper glanding is laid from DB to CNC machine, is it required to run two runs of body earthing to the Machine from DB? 3.If the armoured cable with proper glanding is laid from Substation to Hangar, distance is approx. 100 mtrs, is it required to do earthing at shop area though the primary termination at substation is earthed through gland.

0 Answers   HAL,


When is lag lead compensator is required?

0 Answers  


I AM DOIN MY 3RD YEAR IN ELECTRICAL ELECTRONICS. PLEASE SUGGEST WHAT DO I DO NEXT AFTER MY B.E? AND I WANT TO GET INTO ANY PSU IS DER ANY EXAMS PLASE SUGGEST EVEN THAT.

3 Answers  


Is there any relation between transformer capacity and its bdv?

1 Answers  


Why generator is not connecting in delta ..why connecting in star ?

4 Answers   Bhel, Foretec Engineers,


what is bus coupler? and how many type? which one is big advantage ?

2 Answers   Essar,


what is the electrical?

0 Answers  


what are the points to be consider for MCB(miniature circuit breaker selection?

3 Answers  


if we use fuse in neutral what will happen?

9 Answers   L&T,


how to select the mpcbs and contactor for 3 phase 30 hp star delta motors.for plc control.and tell me the calaculation for future use.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)