What is the difference between ACB & MCCB?
Answers were Sorted based on User's Feedback
Answer / j. a
Actually the ACB is abbreviation of Air circuit breaker,
which is normally used for LV switchgears and high current
(normally more than 400A). The switching contacts are
operating in the air. MCCB is abbreviation of moulded case
circuit breker which is normally used for switching of load
less than 630 A.
| Is This Answer Correct ? | 22 Yes | 0 No |
Answer / satya dev
As per IE Rule Below than 1000 Amp. Load we can use MCCB &
Above than 1000 Amp. Load we must be use ACB.another reason
is the Range of Short Ckt Capacity of ACB is Greater Than
the MCCB.
| Is This Answer Correct ? | 9 Yes | 4 No |
Answer / mahadikpramod
1)Differencfe between ACB & MCCB is mainly,ACB we can use
for large load and MCCB we can not.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / srabon1059
ACB(Air circuit breaker):
1.ACB provide over load,under voltage and short ckt protection.
2.mainly used in industrial are.
MCCB(oulded case circuit breker):
1.Provide over load ,short ckt protection.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / aravind
ACB :Air circuit breaker is available from 400A to 6300A .
They are generally used for O/L,S/C,E/f and metering
protection.
The breaking capacity is generally 35kA/50kA/60/75KA
MCCB:Moulded case circuit breaker is available from 32A to
1600A.
They offer all the protection as offered by ACB.
However MCCB are compact when compared to ACB for
respective ratings.
MCCB are difficult to repair and life is less when compared
to ACB.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mohammed yousuf khan
ACB stands for Air Circuit Breaker whereas MCCB stands for Moulded Case Circuit Breaker. Generally MCCBs are used for loads upto 630A but if the load is higher say beyond 630A then the ACBs are used.
1)Also ACB is long lasting when compared to MCCB.
2)The switching contacts of ACB operate in air, whereas the switching contacts of MCCB operate in a case. Hence the name ACB & MCCB.
3)Apart from Overload, Short Circuit & Earth fault protection, other protections such as Under voltage protection can be achieved using ACB.
4)MCCBs are very compact, whereas ACBs are large in size when compared to MCCBs.
5)MCCBs needs to be replaced after a certain operations but ACBs can be re-used with little maintenance, as the spares are easily available for ACBs such as Contacts,arc chute etc...
| Is This Answer Correct ? | 0 Yes | 0 No |
what kinds of Transformer oil grade is better for power transformer ?
A motor running with lenze frequiency inverter stops if I REDUCE SPEED with 25% load.If I run it in High speed and medium speed running smoothly with full load.please help me to solve it.
What is the difference between circuit breaker and isolator
who can measure the size of power cable?
What is the 415V AC Soft starter? Explain with an example?
what does hapen if suddently frequency doubled
Define phase lag and phase lead?
Where is servomechanism used?
what is the disadvantage if earth is connected to neutral
What is the frequency of dc current????
What is the deffirant between EARTH, GROUND AND NUTRAL
9.The material used for coating the electrode is called........
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)