how to calculate the multiplying factor for energy meter
with CT ratio given
Answers were Sorted based on User's Feedback
Answer / sunil
MF= (main PT ratio x main CT ratio x meter constant)/
(meter PT ratio x meter ct ratio)
| Is This Answer Correct ? | 365 Yes | 82 No |
Answer / mazhar
Suppose CT ratio 100/5 then MF will be 20
then If you want to know the consumption so you
(Total Reading *MF)= Total Consuption
| Is This Answer Correct ? | 229 Yes | 84 No |
Answer / ashok
Line CT Ratio/Meter CT Ratio*Line PT Ratio/Meter PTratio
| Is This Answer Correct ? | 129 Yes | 35 No |
Answer / sukhdev
If C.T Ratio is 150:5 Amp Than,
=150/5
=30
Now,M.F= 30*(Difference in meter reading)
It means if Previous reading is 11226
Current reading is 11626
Difference is 400 &
M.F=30*400
M.F =12000
| Is This Answer Correct ? | 159 Yes | 86 No |
Answer / ruksana
if given CT ratio is 100/5 than multiplication factor will be 20.should multiply with displayed kWh
| Is This Answer Correct ? | 76 Yes | 29 No |
Answer / sangamesh
M.F.= (Connected PTR/meter PTR) X (Connected CTR/Meter CTR)
| Is This Answer Correct ? | 66 Yes | 25 No |
Answer / naeem zafar
M.F= (CONEECTED PT RATIO/METER PT RATIO * CONNCTED CT
RATIO/METER CT RATIO)* METER CONSTANT
| Is This Answer Correct ? | 38 Yes | 14 No |
Answer / ramesh
M.F=(CT Ratio/Meter)* (PT Ratio/Meter)
(33/11)*(40/5)=?
like this
| Is This Answer Correct ? | 50 Yes | 27 No |
Answer / dave
Metar ct retio 2oo/5 and li ne ct retio 2oo/1 what is a Metar mf
| Is This Answer Correct ? | 34 Yes | 14 No |
Answer / j.p.
CT Ratio = CT RATIO OF CT*PT RATIO OF PT
-----------------------------------
METER RATIO OF CT*METER RATIO OF PT
| Is This Answer Correct ? | 33 Yes | 16 No |
What is Torque Vector Control in VVVF Drives?
How to calculate approximate load loss of a distribution transformer by knowing %ge imp of transformer?
what is the frequency of direct current(dc)?
12 Answers Cognizant, University,
6.6Kv feeder feeding tow step down transformers-415V-,what the possible consideration for parrellel operation?
Why 1/3 is used in symmetrical components?
how much mininmum length required to conduct a DC Hipot Test on 33kV AC Cable with 45kV DC? Is it 20meter or Less then 20?
what is the difference between LT & HT Motors
What are the Return ( Monthly / quarterly/ Annual submitted to Electical Inspector for an establishment (Factory in Maharashtra-- Small scale category having seperate HT line of 22KV ) as per Maharashtra Electricity Act
why ct secondary side shortlink provided? its open what will happen?while running ?
what should be the no load current of an induction motor
what is the pre charge circuit,what will be work which function it will be use plz tell me
how can we know the size of cable cross-section from current rating ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)