Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

for 12KW motor which cable size has to select for ex.10
meter.

Answer Posted / phanendra babu

the selected cable should have the capability of
withstanding the over load /short ckt currents upto before
operating the protecting device. so assume 0.81 p.f,the load
current is given by apprx 20A .very safe working of copper
cable is 4A to 6A per 1sqmm ,so the size of the cable
suitable for 12kw motor is 6sqmm. copper cable or 16 sqmm
aluminum cable.

the above calculation is for lo current ratings if current
rating increases capacity will decrease.

Is This Answer Correct ?    4 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What does the a,b,c of 95a,95b,95c relays denotes?

2647


what is the grounding Calculation formula? spouse i want to provide grounding to 3phase 18kw motor or i want to provide ground to 3phase 10kva dry type transformere or you give me any exemple...... Thanks.

1863


Could u pls tell me the NPCIL electrical engineering interview questions for Executive trainee, and also guide me how to face the interview.

4477


kindly send me 11KV MV motor differential protection procedure by primary injection method.

1427


Ceiling Fan and Storage type water heater. Discuss

1956


Why we use auxillary relay ? what is function of differential relay, directional o/c relay?

2185


Z transform is use when system is not a) converges b) diverges

1666


what will happen if OLR CT in all phases are short circuted

2180


volts=230 c=10mf a=??

2025


why starting current is high and resistance is almost 0 during the starting of motor dc motor...?

1730


how oltc works in rectiformers of higher rating (27 mva,200v dc,120kamps) please provide me full information with diaggram.

2132


explain the Trip supervision circuit

2145


What is the previous name of Cox's Bazar

2238


What is marx circuit?

1119


when ac current flows thru d coil of a contactr,it energizes,magnetic field attracts d contact of the coil...nw wont dt ac current in d contct induce current back on to d coil thru mutual inductance leading to high currnt in d coil

1703