what do u mean by knee point voltage?
Answers were Sorted based on User's Feedback
Answer / abhinaav saikia
It is the value of voltage above which there is a sudden
increase of current,below this voltage the V/I
charachteristics is almost linear(ohmic charachteristics).
A mark increase in current is observed beyond this knee
voltage.
| Is This Answer Correct ? | 33 Yes | 1 No |
Answer / bakyalakshmi nisha
It is the value of voltage above which there is a sudden
increase of current,below this voltage current is zero or
very low(leakage current).
| Is This Answer Correct ? | 23 Yes | 6 No |
Answer / lussubilo mwakibinga
this is the point at which the current start increasing
sharply after the minimum voltage for device to conduct in
foward bias is reached.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / rod
Knee point relates to current transformers it is the point
on the curve where it starts to flaten out and the
transformer starts to saturate
| Is This Answer Correct ? | 9 Yes | 5 No |
Answer / ashish jain
in case of C.T. It is the value of voltage above which
there is a sudden increase of current i.e. with 10%
increase in voltage, there is 30% increase in current
(approx). below this voltage the V/I
charachteristics is almost linear.
| Is This Answer Correct ? | 5 Yes | 5 No |
Answer / raju_
IN SEMI CONDUCTOR DEVICES WHEN THE VOLTAGE IS GENRETED THEN
SEMI CONDUCTOR INCRISE THE SOME CURRENT IT HAVE SOME NUMBER
OF ELECTRONS ITS'CALL KNEE VOLTAGE..
| Is This Answer Correct ? | 2 Yes | 6 No |
Answer / jsenthamizh
knee point voltage also called as cut in voltage.espicially
its said to be in semiconductor. semiconductor matrial made
up of silicon or germanium. Its depens upon what type of
semiconductor material is used for silicon cuting voltage
is 0.7 for germanium 0.3.
| Is This Answer Correct ? | 3 Yes | 9 No |
Pure inductive ckt takes power from AC when 1. Applied voltage and Current increases 2. applied voltage and current decreses 3. voltage decreases and current decreases please justify
why the transformer was not rotating like a motor?
why the generator operating along with the infinte bus bar should never be under_excited?
what will happen if a cw rotating altenator being synchronized to ccw rotating altenator
we have two 11/.433 kv. distribution Transformer rating as 1000 kva & 500 kva , i wants to run parallel both transformer. both transformer impendence voltage is 5.24%, How can we run both t/f, & how sharing the load
CBCT selection
What is the method & formula of Fault level calculation in power Transformesr.
how we can save the power ? suppose the electricity board gives 11 kw , but the machine require only 8 kw means how we can save the exese energy
DOES AN EARTH FAULT CURRENT ON THE DELTA SIDE OF A 6.6/33KV STEP UP STAR-DELTA CONNECTED TRANSFORMER REFLECT ON THE STAR SIDE? IF YES, THEN HOW AND WHAT IS THE AMOUNT OF CURRENT REFLECTED?
Will The Rated Capacity of 20 MVA ,220/6.6 KV, ONAN cooling Power Tranformer be increased up to 25 MVA with respect to its %Impedence by ONAF cooling with same rating..?
what are the differences between 'exhaust fan', 'heavy-duty exhaust fan' & 'super heavy duty exhaust fan'. what are their power ratings ?
Why we are putting off the APFC(automatic power factor control) panel while the generator is running?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)