Why we are putting off the APFC(automatic power factor
control) panel while the generator is running?
Answers were Sorted based on User's Feedback
Answer / ns
we are putting in APFC off condition in Generator running
because capacitor bank added in dg running condition power
factor increase and kva is more then its rated DG kva bcz
all generators desigen in 0.8 pf with rated Kva.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / k.prakashchandra
APFC is for use while gen is running only.It is not
preferred as it may lead to voltage rise whenever there is
sudden network failure.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / k.prakashchandra
Add that APFC is to be used only when gen is connected to
grid or network.
| Is This Answer Correct ? | 0 Yes | 3 No |
in 3phase 50kva dg what is the full load current for single phase laod
what happened if power factor is "1"
Is it possible to measure correct value of earth resistance & cable insulation ristance with out disconncting earth lead & both sides of cable ends? If not, any other method to measure ER & CIR with out disconneting from the system.
why should we have to maintain pf in our site 0.9????????
What is the difference between an insulator and a dielectric?
What is electrical grounding?
What is RMU, and what it's function?
A circuit breaker is a
can any one tell me the formula for calculating the power and unit consumpetion
How will polarity test of Dy5 Transformer ?
why ct mensioned 0.5/5p20 plese any reply to me
1kva=how many kw & amps
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)