Why we are putting off the APFC(automatic power factor
control) panel while the generator is running?
Answers were Sorted based on User's Feedback
Answer / ns
we are putting in APFC off condition in Generator running
because capacitor bank added in dg running condition power
factor increase and kva is more then its rated DG kva bcz
all generators desigen in 0.8 pf with rated Kva.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / k.prakashchandra
APFC is for use while gen is running only.It is not
preferred as it may lead to voltage rise whenever there is
sudden network failure.
Is This Answer Correct ? | 1 Yes | 4 No |
Answer / k.prakashchandra
Add that APFC is to be used only when gen is connected to
grid or network.
Is This Answer Correct ? | 0 Yes | 3 No |
operation principle of a generator? Gss, Diesel and HFO which is better and why?
how ti maintain the power factor in power generation
Anyone who can recommend an equivalent to Envirotemp FR3 of Cooper?
What is the purpose of taking Capacitance and Tan Delta Test in Transformer bushing?
what is the meaning of cable Glanding can you explain brifly?
Can we manually synchronize two DG sets of same ratings manually without using speed biasing ? If yes then how?
HOW TO CALCULATE HV TEST VOLTAGE FOR ELECTRICAL EQPT.
There are different classes of protections in power plants.class a,b,c are clear..is there any class d and e r there..and elaborate class b protection.
if we have a industrial load of 400 kilowatts with 415 volt AC then how much total harmonic distortion (thd%) should be acceptable for steady power system.
why secondary of open delta pt (two element pt) centre tap is earth what happen when this earth is removed
how the 6.6KV motor can be used with 11KV?
how we calculate the dick for a pole?