What is the method & formula of Fault level calculation in
power Transformesr.
Answers were Sorted based on User's Feedback
Answer / dinesh
since %impedance is the per unit value, u can get the short circuit fault current level by,
Ifault = Irated (phase current) / %z..
Similar method if u need fault level MVA....
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / k.prakashchandra
% impedance( Say P )= I rated x Z x 100 /V rated. Hence Z =
P x Vr /Ir x 100. Fault current If = Vr /Z .Then If= Ir x100/P
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
I think you have to multiply by 100 ,in the above answer as
otherwise the fault current will be less than the rated.
| Is This Answer Correct ? | 1 Yes | 0 No |
as ac supply is given 2 the transformer why it doesnot depends upon powerfactor????
WHAT IS MEANT BY SHEATH VOLTAGE IN 132Kv cable?
Whether earthmat designning is done only for sub station or it can be done for multy residential complexes also? What is the size, type & arrangement of the earth grid to be done?
why ac wave is sinusoidal not square or triangular wave what will be reason
15hp motor wound by 0.9mm & 0.95mm magnet wire. at no load test it draw 4.2A current. Another motor with same condition draw 9.2A current. How can that occur? pls help
IAM GOING TO ERECT THE STREET LIGHT.,, I NEED HOW TO CALCULATE LUX., ILLUMINATION.,AND ALL
Advantage of 11KV ring main system with open point
1 Answers Alam Group of Companies,
what is bus duct and what is differance between bus duct and bus bar
What safety precaution are to be taken for avoiding electric hazards ?
What is reactance, reluctance,capistance, pls give answeer in hinglish and be simply Jo asani we smajh m aa jaye
I am having a DG set.The 415 V from Generator is step up to 460 v and then the same is used for Induction furnace. before Step up, I am connecting LT load to my factory use. When Induction furnace is in service from DG, when i try to start a motor, the generator is tripped.Please tell me the reason.
What should be the dielectric strenght value of transformer oil of 11/0.433KV distribution transformer and 33/11KV tranmission transformer ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)