What is the method & formula of Fault level calculation in
power Transformesr.
Answers were Sorted based on User's Feedback
Answer / dinesh
since %impedance is the per unit value, u can get the short circuit fault current level by,
Ifault = Irated (phase current) / %z..
Similar method if u need fault level MVA....
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / k.prakashchandra
% impedance( Say P )= I rated x Z x 100 /V rated. Hence Z =
P x Vr /Ir x 100. Fault current If = Vr /Z .Then If= Ir x100/P
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
I think you have to multiply by 100 ,in the above answer as
otherwise the fault current will be less than the rated.
Is This Answer Correct ? | 1 Yes | 0 No |
which phase is preferred for connecting 1 phase vt used for synchronizing OHL? WHY?
what would happen if reactive power (kvar)is increased (more)or decreased (less)? how much exact reactive power should be maintained? and what should be done for that
how to find the 2500 KVA transformer rated primary and secondary volt and current?
how MW increase when steam input increase in turbine.
In aircraft,why we use 400 htz equipment.and use common earthing
Why dry type cast resin transformers tap link blast in HV side while power shut down times on load?
what happens to a turbo alternator if it get trip and 1 out of 3 poles of circuit breaker in close condition
We've 2 diffrent DG's with same capacity (500 KVA). Can we sync them ?
what is difference b/w bus duct & bus bar.
what is cause of static electricity? I experience shock when i touch metal equipment in a room ,furher check shows earth leakage showing 80ma at the DB near to the 400 MCCB?
how to calculate the size of the cable for a particular rating 3phase induction motor?
1 Answers Godrej, Megatron Solutions,
what are inductive and capacitive voltage transformers.what are their applications