Answer / dinesh

since %impedance is the per unit value, u can get the short circuit fault current level by,

Ifault = Irated (phase current) / %z..

Similar method if u need fault level MVA....

Is This Answer Correct ?    3 Yes 1 No

What is the method & formula of Fault level calculation in power Transformesr...

Answer / k.prakashchandra

% impedance( Say P )= I rated x Z x 100 /V rated. Hence Z =
P x Vr /Ir x 100. Fault current If = Vr /Z .Then If= Ir x100/P

Is This Answer Correct ?    1 Yes 0 No

What is the method & formula of Fault level calculation in power Transformesr...

Answer / k.prakashchandra

I think you have to multiply by 100 ,in the above answer as
otherwise the fault current will be less than the rated.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

which phase is preferred for connecting 1 phase vt used for synchronizing OHL? WHY?

0 Answers   Siemens,


what would happen if reactive power (kvar)is increased (more)or decreased (less)? how much exact reactive power should be maintained? and what should be done for that

0 Answers   ABB, Siemens,


how to find the 2500 KVA transformer rated primary and secondary volt and current?

4 Answers  


how MW increase when steam input increase in turbine.

1 Answers  


In aircraft,why we use 400 htz equipment.and use common earthing

1 Answers  






Why dry type cast resin transformers tap link blast in HV side while power shut down times on load?

0 Answers  


what happens to a turbo alternator if it get trip and 1 out of 3 poles of circuit breaker in close condition

1 Answers   wbsedcl,


We've 2 diffrent DG's with same capacity (500 KVA). Can we sync them ?

1 Answers  


what is difference b/w bus duct & bus bar.

2 Answers  


what is cause of static electricity? I experience shock when i touch metal equipment in a room ,furher check shows earth leakage showing 80ma at the DB near to the 400 MCCB?

0 Answers  


how to calculate the size of the cable for a particular rating 3phase induction motor?

1 Answers   Godrej, Megatron Solutions,


what are inductive and capacitive voltage transformers.what are their applications

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)