How to take Vector group test of Transformer?
Answers were Sorted based on User's Feedback
Answer / ambrish
Pl. show the standard formula to check vector group tst for
any type of transformer.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / tansford
Superimpose the HV & LV vectors with 1U & 2U as common it
clearly shows the relation between the phasors
Every vector group will have a different relation &
equation to be evaluated
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / raj_singh_0376
Procedure of vector group test of transformer
Let’s have a YNd11 transformer.
1) Connect neutral point of star connected winding with earth.
2) Join 1U of HV and 2W of LV together.
3) Apply 415V, three phase supply to HV terminals.
4) Measure voltages between terminals 2U – 1N, 2V – 1N, 2W – 1N, that means voltages between each LV terminal and HV neutral.
5) Also measure voltages between terminals 2V – 1V, 2W – 1W and 2V – 1W.
For YNd11 transformer, we will find,
2U – 1N > 2V – 1N > 2W – 1N
2V – 1W > 2V – 1V or 2W – 1W
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ponnudura
can anyone say me hoe to draw vector group and what is the
use of different vector group and its application plz
Is This Answer Correct ? 17 Yes 8 No submit
srinivas
Answer
# 8 1.1U1V1W-which is primary -Delta Connection
2.2U2V2W- Which is secondary-Star connection
3.join 1U& 2U terminals
4.Supply 1U-1V-1W 440v Measured
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
TO CHECK
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
From above check(1,2) the vector group of transformer is
verified
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / balaji
1) Can i know why we are making short of any phase during vector group test ?
for Example R-r,Y-y Like that
2) while doing the vector group why the neutral earth should be removed ?
| Is This Answer Correct ? | 0 Yes | 0 No |
How does HT work & Voltage required?
Why dnt we generate 5-ph or 7-ph supply like as 3-ph supply
Why the rating of the HT breakers are in 1250 Amp, while the load on the breaker is around 50 Amp. ?
what is the last range of mccb in amp?
how motor should be connected i.e star-delta or star-star or delta-delta ?
What are the advantages of speed control using thyristor?
What is broken wire condition in transmission line?
If the t/f capacity is 500KvA then what is Amps ratting of the main breaker.
which VFD is better ( LT or HT)
How to calculate voltage drop loss in HT 11000 Volts XLPE Aluminium conductor cable. Any specific formula or Thumb rule
What happens when ac supply is given as excitation voltage instead of dc supply
WHY IS RESTRICTED EARTH FUALT PROTECTION NEEDED?? WHY CANT DEIFFERENTIAL PROTECTION SUFFICE???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)