How to take Vector group test of Transformer?
Answers were Sorted based on User's Feedback
Answer / dinesh kumar
Assumed the transformer vector group is DYn11;
1.1U1V1W-which is primary -Delta Connection
2.2U2V2W- Which is secondary-Star connection
3.join 1U& 2U terminals
4.Supply 1U-1V-1W 440v Measured
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
TO CHECK
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
From above check(1,2,3) the vector group of transformer is
verified
| Is This Answer Correct ? | 225 Yes | 28 No |
Assumed the transformer vector group is DYn11;
1.1U1V1W-which is primary -Delta Connection
2.2U2V2W2N- Which is secondary-Star connection
3.By connecting terminals 1U& 2U
4.Then three phase Supply is given to 1U-1V-1W
5.By measuring the terminal given below
We get
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
THE BELOW GIVEN CONDITION IS SATISFIED THEN DYn11 IS
CONFIRMED
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
| Is This Answer Correct ? | 121 Yes | 26 No |
Answer / vinod
Vector group is punched on the name plate based on the user
requirement by the manufacture. Aim of vector group test is
at site is to check if their is any damage in the windings
during transportation and erection.
3 -phase AC supply is given on HV side. R-Phase HV and r-
phase LV shorted for all vector group of transformer
Then to qualify the test following conditions are to be
satisfied after measurement of voltages.
nR+nY=RY, By>> Bb and Yb=Yy.
| Is This Answer Correct ? | 19 Yes | 5 No |
Answer / srinivas
can anyone say me hoe to draw vector group and what is the
use of different vector group and its application plz
| Is This Answer Correct ? | 18 Yes | 8 No |
Answer / adi
Procedure given by Mr. dinesh kumar & Mr. E.saravanan is
correct but is there any explanation for this three
conditions.
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
| Is This Answer Correct ? | 13 Yes | 3 No |
Answer / prasad talada
1.1U1V1W-which is primary -Delta Connection
2.2U2V2W- Which is secondary-Star connection
3.join 1U& 2U terminals
4.Supply 1U-1V-1W 440v Measured
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
TO CHECK
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
From above check(1,2) the vector group of transformer is
verified
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / vinay kumar
can anybody tell hw u r writing this is the vector group
calculation for this one.....
what happens if the voltages r not satisfied for the
specified vector group and if so what to do.......
| Is This Answer Correct ? | 7 Yes | 3 No |
why motor rating in KW?
what would happen if u assume to insulate all the overhead lines and no insulators....??do you think it to b an advantag or a disadvantage??justify.
Who is the first Bangladeshi Everest climber? Where is his home district?
What will be result if we connect LT votage to the terminal of HT Transformer?
what is the internal fuction of a ceiling fan?
Why should be the frequency 50 hz 60hz only why not others like 45, 95 56 or anything , why should we maintain the frequency constant if so why it is only 50 hz 60hz?
how to calculate capacitor bank value to maintain unity power factor plz xplain with some suitable xample?
waht is the working principle of saft starter & what is the difference in vfd & saft starter
Why use in ht motore
what is VSWR?
How 48-relay (incomplete sequence) functions?
What is meant by system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)