How to take Vector group test of Transformer?
Answers were Sorted based on User's Feedback
Answer / dinesh kumar
Assumed the transformer vector group is DYn11;
1.1U1V1W-which is primary -Delta Connection
2.2U2V2W- Which is secondary-Star connection
3.join 1U& 2U terminals
4.Supply 1U-1V-1W 440v Measured
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
TO CHECK
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
From above check(1,2,3) the vector group of transformer is
verified
Is This Answer Correct ? | 225 Yes | 28 No |
Assumed the transformer vector group is DYn11;
1.1U1V1W-which is primary -Delta Connection
2.2U2V2W2N- Which is secondary-Star connection
3.By connecting terminals 1U& 2U
4.Then three phase Supply is given to 1U-1V-1W
5.By measuring the terminal given below
We get
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
THE BELOW GIVEN CONDITION IS SATISFIED THEN DYn11 IS
CONFIRMED
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
Is This Answer Correct ? | 121 Yes | 26 No |
Answer / vinod
Vector group is punched on the name plate based on the user
requirement by the manufacture. Aim of vector group test is
at site is to check if their is any damage in the windings
during transportation and erection.
3 -phase AC supply is given on HV side. R-Phase HV and r-
phase LV shorted for all vector group of transformer
Then to qualify the test following conditions are to be
satisfied after measurement of voltages.
nR+nY=RY, By>> Bb and Yb=Yy.
Is This Answer Correct ? | 19 Yes | 5 No |
Answer / srinivas
can anyone say me hoe to draw vector group and what is the
use of different vector group and its application plz
Is This Answer Correct ? | 18 Yes | 8 No |
Answer / adi
Procedure given by Mr. dinesh kumar & Mr. E.saravanan is
correct but is there any explanation for this three
conditions.
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
Is This Answer Correct ? | 13 Yes | 3 No |
Answer / prasad talada
1.1U1V1W-which is primary -Delta Connection
2.2U2V2W- Which is secondary-Star connection
3.join 1U& 2U terminals
4.Supply 1U-1V-1W 440v Measured
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
TO CHECK
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
From above check(1,2) the vector group of transformer is
verified
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / vinay kumar
can anybody tell hw u r writing this is the vector group
calculation for this one.....
what happens if the voltages r not satisfied for the
specified vector group and if so what to do.......
Is This Answer Correct ? | 7 Yes | 3 No |
HOW TO CALCULATE LV CABLE SIZING?
Why we Specify Transformer rating 433 V Instead of 415V ?
Can we inject more current in ct primary paralleling 2 loading transformers/Injection kit at a time?let ct ratio be (5000/1A)(per kit rating 2000A range),i need to inject 5000A,if this cant b done means wat is d optional?
for compensate 315mh inductance ,how many capaciance required?
Is there any abbrevation for STUB in Stub bus protection
Why Stabilising Resistor used in REF circuit ?
what is difference between isolation and ultra isolation transformer?, what is the method of testing ?
WHAT IS THE DIFFERENCE BETWEEN GENERAL INVERTER AND SOLOR INVERTER TELL ME PLZ
before synchronizing an alternator,power factor is leading ,why?
which types of relay used in acb and vcb?
What is the differance between a converter duty transformer and normal power transformer?
selection of conductor in different voltage?