Why earthing transformer used in Distribution Sub-Station?
Answers were Sorted based on User's Feedback
Hi questioner,
Earthing T/F or T/Fs are not required in distubution S/S.
For example, here in Nigeria the distribution volage for
the T/F is either 11/0.415kV or 33/0.415kV detla-star.
However, in Transmission S/S where there are 132/33kV star-
delta connected T/F or T/Fs earthing T/F or T/Fs are
necessary. The earthing T/F is connected on the 33kV side
of the main T/F while the star-point of earhing T/F is
connected to ground to provide an artificial star-point for
the main T/F. This so because 33kV distribution ground-
fault current must flow back to the main T/F. Earth fault
protection for the main T/F must sense this current and
isolate the main T/F otherwise the earthing T/F will roast
i.e. burn.
| Is This Answer Correct ? | 12 Yes | 3 No |
Further to my answer,note that a ground fault at the
distribution S/S must be sensed fast by the relay so as to
trip the disribution cb before the cb for the 132/33kV in
the Transmission S/S is trip by its relay as a back-up.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / deep
in delta connected t/f winding has not neutral point to connect to ground and beacuse LG,LLG fault is sensed by zero sequence current so providing earting on delta side we use earthing t/f.
| Is This Answer Correct ? | 0 Yes | 0 No |
why the earth pin in a 3-pin socket is longer and thickest?
what is the purpose of reactor in electrical substations ?
How to test and satisfy the conditions of the vector group YNd1 for power transformer?
how would you come to know if a transformer is double wound or auto? note that there is no tag. you are given only a multimeter.
In Which vector group power transformers are mostly manufactured?
Why does inductive loads consume KVARs?
what is the principal of braker
The advantages of Magnetic flux leakage technique over Ultrasonic technique for non distructive testing of material.
what is destructive and non-destructive testing of welding
Differentiate between real and apparent power?
what is the Pickup/drop off ratio in BCPU relays
what is the earth to neutral voltage(maximum and minimum) according to ieee standards
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)