Hi questioner,
Earthing T/F or T/Fs are not required in distubution S/S.
For example, here in Nigeria the distribution volage for
the T/F is either 11/0.415kV or 33/0.415kV detla-star.
However, in Transmission S/S where there are 132/33kV star-
delta connected T/F or T/Fs earthing T/F or T/Fs are
necessary. The earthing T/F is connected on the 33kV side
of the main T/F while the star-point of earhing T/F is
connected to ground to provide an artificial star-point for
the main T/F. This so because 33kV distribution ground-
fault current must flow back to the main T/F. Earth fault
protection for the main T/F must sense this current and
isolate the main T/F otherwise the earthing T/F will roast
i.e. burn.
| Is This Answer Correct ? | 12 Yes | 3 No |
Further to my answer,note that a ground fault at the
distribution S/S must be sensed fast by the relay so as to
trip the disribution cb before the cb for the 132/33kV in
the Transmission S/S is trip by its relay as a back-up.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / deep
in delta connected t/f winding has not neutral point to connect to ground and beacuse LG,LLG fault is sensed by zero sequence current so providing earting on delta side we use earthing t/f.
| Is This Answer Correct ? | 0 Yes | 0 No |
how to calculate the multiplying factor for energy meter with CT ratio given
23 Answers Bhel, Dalmia Group, DIFC, Fedco, Hindustan Unilever Limited, Lupin, MahaDiscom, MAL Pakistan, Myunghwa Automotive, Panchshil Infrastructure, Regala, RVPN, VIPL,
Dear sir, I am working in wind mill division , pls explain Pls explain in details with formula My question is Wind speed 3.5 M/s Gen RPM is 1500 ( 25 K/w Production ) Wind speed 12 M/s Gen RPM is 1500 ( 220 K/w Production ) Why in 3.5 m/s generation was low , why in 12 m/s generation was high , Pls dont explain wind force or wind density , that one already i know For the above question RPM was same why the KW was different Answer : 1. Its depends on the density ( Force ) of the air Sir , Pls explain wit Formula sir
What are the methods used to improve powerfactor ?
what is F.A.P in fire alarming system?
When we use air circuit breaker, it has O/L protection ,time delay SC protection, Instataneous SC protection & ground fault protection. They all have some setting range. But what is the suitable/allowable setting for the above protection which will be safe for the equipment? For example-O/L protection setting have a range of (0.4,0.45,0.5,0.55,0.6,0.65,0.7,0.8,0.9,1.0)xIn Time delay SC protection have a range of (1.25,1.5,2,3,4,6,8,10,12)xIn Time delay setting is 0.02,0.1,0.2,0.3,0.4 Instataneous setting is fixed to 20xIn Gound fault setting is given 100A,300A,600A,900A,1200A This setting are for 2500A ACB. So what will be the basic allowable setting for the above protection? is there any formulae to calculate this<
In a single how much maximum current and watts using
What is RMU, and what it's function?
how can we calculate ct ratings ?its any formula ?
You required 5A from the transformer but you get 8A. How do you minimize this?
if receiving voltage is higher than sending ones what will be the effect of receiver
what is the function of cooling tubes in transformer
If SFU is Switch Fuse Unit, What is the expansion for FSHF in Electrical Engineering?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)