Hi questioner,
Earthing T/F or T/Fs are not required in distubution S/S.
For example, here in Nigeria the distribution volage for
the T/F is either 11/0.415kV or 33/0.415kV detla-star.
However, in Transmission S/S where there are 132/33kV star-
delta connected T/F or T/Fs earthing T/F or T/Fs are
necessary. The earthing T/F is connected on the 33kV side
of the main T/F while the star-point of earhing T/F is
connected to ground to provide an artificial star-point for
the main T/F. This so because 33kV distribution ground-
fault current must flow back to the main T/F. Earth fault
protection for the main T/F must sense this current and
isolate the main T/F otherwise the earthing T/F will roast
i.e. burn.
| Is This Answer Correct ? | 12 Yes | 3 No |
Further to my answer,note that a ground fault at the
distribution S/S must be sensed fast by the relay so as to
trip the disribution cb before the cb for the 132/33kV in
the Transmission S/S is trip by its relay as a back-up.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / deep
in delta connected t/f winding has not neutral point to connect to ground and beacuse LG,LLG fault is sensed by zero sequence current so providing earting on delta side we use earthing t/f.
| Is This Answer Correct ? | 0 Yes | 0 No |
Please define ampere?
diff.between servo motor and ac motor
we have a rewind motor of 2Hp,2800Rpm, 220Volt AC. how can we choose the running capacitor for this motor, any formula for that?
WHY BREAKER ARE USED IN SUBSTATIONS?
motor work in hat principle generator work in what principle transformer work in what principle pls explain with details or answered to ramadoss.sepc@gmail.com
what is the formula for calculation of sac?
how does calculate loss correction factor in transformer
How to calculate percentage impedance of a power transformer.
Shall I use 40A semiconductor Fuses in 32 A SFU ? Frame size is same. What Happen if Fuses burn on SFU?
There is one 40MVA oil cooled transformer (yet to commission), filled with 95% oil and we are trying to fill 5% Nytrogen in that transformer so that there should not be any foreign component inside. But even though there is no leakage, nytrogen is not withstanding inside transformer, within a day or two pressure guage is showing 0. Why is it soooo? Pls reply.
Rules and standards of electrical control wiring ?
WHAT IS THE THUMB RULE FOR DECIDING THE CURRENT RATING OF COPPER WIRES SAY 2.5/4/6/10 MM SQUARE SIZES??
14 Answers Dubai Group, Saudi Delta Groups, Savitha Electricals,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)