Answer / pravin sathalpara
it is depend upon the load beacause trasformer equistion
is
kva=VICOS
SO,OUR VOLTAGE AND CURRENT(LOAD) IS DECIDE FIRST
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / bhagaban barik
KW=KVA*P.f
i.e- KVA=KW/p.f
It also depends on Utilisation factor & maintenance factor
we have to consider 30% margin for future expansion
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / papuraj
Its purely depends upon your maximum demand nothing else.For an example if you have the connected load is 700kva and maximum demand is only 350kva, hence we could select 500kva transformer to be with 20% future additional load.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rajani
SIZE OF TRANSFORMER DEPENDS THE FOLLOWING
CONNECTED LOAD EX:2500KVA
MAXIMUM DEMAND EX:1500KVA
STARTING LOAD EX: 500KVA
LOAD FACTOR EX:0.9
FUTURE LOADS EX: 20% EXTRA TO MAXIMUMDEMAND
SO TRANSFORMER SIZE IS (1500+500+20%(1500))*0.9=2070KVA
SO 2200KVA TRANSFORMER IS ADEQUATE FOR MAX DEMAND OF
1500KVA LOAD.
Is This Answer Correct ? | 19 Yes | 20 No |
Answer / abhishek ranjan
transmer size can be calculated according to load.
its also depend on the material used.
if we use HRS in the place of CRGOS then its size will increse
Is This Answer Correct ? | 12 Yes | 20 No |
Answer / mitul
Transformer size ,we can consider what is the maximum load and for future expansion 25% shall be considered
Is This Answer Correct ? | 1 Yes | 9 No |
Answer / v v s reddy
Check the following conitions
1. Rating of transformer is sufficient to totao load
2. Thermal loading on the transformer during motor starting
3.Voltage available at motor terminal during motor starting
4.Voltage available at bus during motor starting
Is This Answer Correct ? | 7 Yes | 16 No |
Answer / vladimir tutulaku
WE HAVE A OLD TRANSFORMER WITHOUT TARGET
HOW WE CAN DECIDE THE POWER OF TRANSFORMER
Is This Answer Correct ? | 4 Yes | 13 No |
Answer / u.chandarasekar
It is Very Very Simple take one Measurment Tape
Is This Answer Correct ? | 1 Yes | 10 No |
Answer / rajesh
Transformer size is decided based on the following factor.
--> Load details
--> Load factor
--> coincidence factor
--> BKW value
--> Other than this it required power factor of the loads.
By using the following formulas we can calculate the
kva rating.
cosф * KW = KVAr
(KVA)2 =( KW)2 +( KVAr)2
Is This Answer Correct ? | 8 Yes | 24 No |
What is the difference between a 3 winding and 2 winding Potential Transformer
what will happen to give a dc supply in ac motor?
why constant voltage transformer should be start without load? and if started then what will happen?
what is the working of air drayar
internally connection of photvoltic module
What is meant by operating sequence of VCB : 0–0.3sec.–CO– 3min.-CO
how do we calculate length of starting time and repeated starting of a direct online starter?
how electricity is generated through electeic generator ?
why generator is star connected ?
Importance of fault current in power transformers and how to monitor the same? How is it different from winding temperature?
We have a 12MW power plant & we inject 5-6MW power to Orissa GRID. For this we have a 33KV/11KV switch yard having 12.5MVA power transformer. Some times we draw power during emergency. It is observed that during Export or Import for load less than 500Kw the power factor is decreasing to 0.3 . This is happening only during export or import. During island condition TG power factor OK.Our capacitor bank is provided with our Power plant auxilliary load. Please suggest how I can we improve our power factor during low load (GRID).
What is purpose of APFC panel?
7 Answers Techno Electric and Engineering,