how can we know cable size for a given current?
if any one have catalogue plz mail to
vijay_raju369@yahoo.co.in
Answers were Sorted based on User's Feedback
Answer / m.faisal siddiqui.
The selection of a cable size for a given value of current
can be done using the cables & tables provided by the cable
manufacturer. The selection of cable size also depends upon
the lenght of cable from source to load. The total voltage
drop should not exceed 2.5% of rated voltage. Following
factors shall be considered while selecting a cable for
required load.
1. Rated Current.
2. Capacity of Protective Circuit Breaker used.
3. Total Length of cable.
4. Total voltage drop.
5. Laying Method.i.e. underground,in conduit,in trays etc.
6 No. of cables.i.e. grouping factor.
7. Ambient Temperature of installed area.
Temperature Correction Factor to be applied.
8. Type of cable. i.e. singel core,multicore,PVC insulated,
Armoured, XLPE insulated etc.
| Is This Answer Correct ? | 25 Yes | 2 No |
Answer / shrikant muthineni
For an aluminium conductor we can load approximately 2.5
amperes and for a copper conductor aroundf 6 amps
| Is This Answer Correct ? | 20 Yes | 7 No |
Answer / vasu
Two things are very much common on the power system engineering field while doing a cable sizing, these are:
1)LT
2)HT
Cables are separately sized based on voltage levels as said above.
Formulas used for LT side:
Full load current = KW/(KV x sqrt3 x PF x η)
Voltage Drop =
sqrt 3*IFL*(R COS Ø + X SIN Ø)*L/(KV*10000*N.R.)
where
IFL = Full load current of the Load connected in Amps
KW = Rating of the Load connected
KV = System Voltage
R = Resistance of the cable in Ohm/Ph/KM
X = Reactance of the cable in Ohm/Ph/KM
L = Length of the cable in meters
N.R = No of Runs of the cable
cosØ = Power factor of the system
PF = Power factor
η =efficiency
Voltage Drop =
sqrt 3*Ist*(R COS Ø + X SIN Ø)*L/(KV*10000*N.R.)
where Ist=starting current which can be 6 times the FLA of current.In technical term it is called as LRC(locked rotor current)
HT side:
Full load current = KVA / KV x sqrt 3
Short circuit current :
A = Ish x sqrt(t)/ k
Where
t = short circuit time in sec
k = constant
A = Conductor size in Sqmm
Ish = Short circuit current in Amps
Derating Factor :
Ambient temperature correction factor for cables laid in 0.9 Trays at 50 degree C = 0.9
Group derating factor:
Multi Core cables
Cables are laid with a spacing of one Diameter and routed in cable trays and trays in tiers by 300mm =0.9
Ageing factor= 0.95
Therefore the Total derating factor = 0.9 x 0.9 x 0.95 = 0.7695
Total Derating Factor= 0.77
The rest calculation for voltage drop are same as that of LT side
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / bijumone.g
roughly you can take it as 1.5 times of the conductor
size.eg. 300 sqmm can conduct 450 A approximately and
moreover it also depends on the application like
underground or overhead.
if you want in detail you can check it in finolex website.
| Is This Answer Correct ? | 12 Yes | 9 No |
In Energy meter How many rotation Equal to one unit.
why there is no current in the rotor body althrough the flux linking with it also get changes. why current only flows in windinds not in rotor
In a dc series motor increases in lord current results in
How many points does a Circuit can have?
EXPLAIN THE APPLICATION OF RECIPROCITY THEOREM
why ten delta testing is carried out on power transformer
what is the opencircuit tes &short circuit test in transformers ,why you need this test, in poen your connecting which votmeter why?
IF ANY MATERIAL AVAILABLE IN MARKET FOR MOTOR PROTECTION INSTEAD OF OLR & CONTACTOR ?
If two generator running parallel, at that condition both ngr Taken in line or taken any one ngr, but why any one or both Ngr in line? Ngr is use for which purpose?
if we keep frequency constant can we cal a synchronous generator as a dc generator
what is the difference between old fan regulator and new fan regulator
Can any one give an explanation about rating factors of cable? if we are laying the cable on the air with an temp 15 degree then rating factors will be 1.15 and if we are laying the cable on the air an temp 60 degree then rating factor will be 0.76 please describe it and what is the difference between rating factor and derating factor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)