Answer / m.faisal siddiqui.
The selection of a cable size for a given value of current
can be done using the cables & tables provided by the cable
manufacturer. The selection of cable size also depends upon
the lenght of cable from source to load. The total voltage
drop should not exceed 2.5% of rated voltage. Following
factors shall be considered while selecting a cable for
required load.
1. Rated Current.
2. Capacity of Protective Circuit Breaker used.
3. Total Length of cable.
4. Total voltage drop.
5. Laying Method.i.e. underground,in conduit,in trays etc.
6 No. of cables.i.e. grouping factor.
7. Ambient Temperature of installed area.
Temperature Correction Factor to be applied.
8. Type of cable. i.e. singel core,multicore,PVC insulated,
Armoured, XLPE insulated etc.
Is This Answer Correct ? | 25 Yes | 2 No |
Answer / shrikant muthineni
For an aluminium conductor we can load approximately 2.5
amperes and for a copper conductor aroundf 6 amps
Is This Answer Correct ? | 20 Yes | 7 No |
Answer / vasu
Two things are very much common on the power system engineering field while doing a cable sizing, these are:
1)LT
2)HT
Cables are separately sized based on voltage levels as said above.
Formulas used for LT side:
Full load current = KW/(KV x sqrt3 x PF x η)
Voltage Drop =
sqrt 3*IFL*(R COS Ø + X SIN Ø)*L/(KV*10000*N.R.)
where
IFL = Full load current of the Load connected in Amps
KW = Rating of the Load connected
KV = System Voltage
R = Resistance of the cable in Ohm/Ph/KM
X = Reactance of the cable in Ohm/Ph/KM
L = Length of the cable in meters
N.R = No of Runs of the cable
cosØ = Power factor of the system
PF = Power factor
η =efficiency
Voltage Drop =
sqrt 3*Ist*(R COS Ø + X SIN Ø)*L/(KV*10000*N.R.)
where Ist=starting current which can be 6 times the FLA of current.In technical term it is called as LRC(locked rotor current)
HT side:
Full load current = KVA / KV x sqrt 3
Short circuit current :
A = Ish x sqrt(t)/ k
Where
t = short circuit time in sec
k = constant
A = Conductor size in Sqmm
Ish = Short circuit current in Amps
Derating Factor :
Ambient temperature correction factor for cables laid in 0.9 Trays at 50 degree C = 0.9
Group derating factor:
Multi Core cables
Cables are laid with a spacing of one Diameter and routed in cable trays and trays in tiers by 300mm =0.9
Ageing factor= 0.95
Therefore the Total derating factor = 0.9 x 0.9 x 0.95 = 0.7695
Total Derating Factor= 0.77
The rest calculation for voltage drop are same as that of LT side
Is This Answer Correct ? | 8 Yes | 3 No |
Answer / bijumone.g
roughly you can take it as 1.5 times of the conductor
size.eg. 300 sqmm can conduct 450 A approximately and
moreover it also depends on the application like
underground or overhead.
if you want in detail you can check it in finolex website.
Is This Answer Correct ? | 12 Yes | 9 No |
In a transformer ,when voltage decreases current increases. but this is a violation of oms law.why?
We all have seen transmission and Distribution lines In transmission lines the voltage is high and current is low(to reduce I^2r loss) and in distribution lines voltage is low but current is high however the size of transmission wires is bigger than that of distribution wires even though the amount of current carried by the distribution lines is more than that of transmission lines why?
when is the Ohms law is applicable?
What is the advisble power factor to be maintained in grid connecting power generation plnats without any effecting the generator.
To attain a powerfactor more than .95, how much kvr should we use for 100 HP of current
4 Answers Bhel, Scooters India,
How to model "IF ELSE" statement in matlab simulink?
design a LV scheme for a 15 storied building?
How to calculate the sag on transmission Lines.
How to check the thermocouple is correctly connected to cable for K type? (i,e positive pole is connected to non magnetic conductor and negative pole is connected to magnetic conductor)
what is disadvantages of high power factor
what will hapen if we give ac supply to dc motor?
Describe the test procedure to determine the vector group