Answer / m.faisal siddiqui.
The selection of a cable size for a given value of current
can be done using the cables & tables provided by the cable
manufacturer. The selection of cable size also depends upon
the lenght of cable from source to load. The total voltage
drop should not exceed 2.5% of rated voltage. Following
factors shall be considered while selecting a cable for
required load.
1. Rated Current.
2. Capacity of Protective Circuit Breaker used.
3. Total Length of cable.
4. Total voltage drop.
5. Laying Method.i.e. underground,in conduit,in trays etc.
6 No. of cables.i.e. grouping factor.
7. Ambient Temperature of installed area.
Temperature Correction Factor to be applied.
8. Type of cable. i.e. singel core,multicore,PVC insulated,
Armoured, XLPE insulated etc.
Is This Answer Correct ? | 25 Yes | 2 No |
Answer / shrikant muthineni
For an aluminium conductor we can load approximately 2.5
amperes and for a copper conductor aroundf 6 amps
Is This Answer Correct ? | 20 Yes | 7 No |
Answer / vasu
Two things are very much common on the power system engineering field while doing a cable sizing, these are:
1)LT
2)HT
Cables are separately sized based on voltage levels as said above.
Formulas used for LT side:
Full load current = KW/(KV x sqrt3 x PF x η)
Voltage Drop =
sqrt 3*IFL*(R COS Ø + X SIN Ø)*L/(KV*10000*N.R.)
where
IFL = Full load current of the Load connected in Amps
KW = Rating of the Load connected
KV = System Voltage
R = Resistance of the cable in Ohm/Ph/KM
X = Reactance of the cable in Ohm/Ph/KM
L = Length of the cable in meters
N.R = No of Runs of the cable
cosØ = Power factor of the system
PF = Power factor
η =efficiency
Voltage Drop =
sqrt 3*Ist*(R COS Ø + X SIN Ø)*L/(KV*10000*N.R.)
where Ist=starting current which can be 6 times the FLA of current.In technical term it is called as LRC(locked rotor current)
HT side:
Full load current = KVA / KV x sqrt 3
Short circuit current :
A = Ish x sqrt(t)/ k
Where
t = short circuit time in sec
k = constant
A = Conductor size in Sqmm
Ish = Short circuit current in Amps
Derating Factor :
Ambient temperature correction factor for cables laid in 0.9 Trays at 50 degree C = 0.9
Group derating factor:
Multi Core cables
Cables are laid with a spacing of one Diameter and routed in cable trays and trays in tiers by 300mm =0.9
Ageing factor= 0.95
Therefore the Total derating factor = 0.9 x 0.9 x 0.95 = 0.7695
Total Derating Factor= 0.77
The rest calculation for voltage drop are same as that of LT side
Is This Answer Correct ? | 8 Yes | 3 No |
Answer / bijumone.g
roughly you can take it as 1.5 times of the conductor
size.eg. 300 sqmm can conduct 450 A approximately and
moreover it also depends on the application like
underground or overhead.
if you want in detail you can check it in finolex website.
Is This Answer Correct ? | 12 Yes | 9 No |
IN SINGLE PH TRANSFORMER IF LEKAGE IMPEDANCE DROP IS NEGLECTED ,THE FLUX IN THE MAGNETIC CORE and the lekage flux linking a winding are a)proportional to the applied v to the winding i respectively.
WHAT IS THE MEANING CREEPAGE DISTANCE
DG use Rating KVA why
Differentiate between power relay and reverse power relay?
it is clear that volts equal to the current as per ohms law. is it appliable to the AC power or only for DC. if it is appliacable to AC in transformers when voltage increases the voltage decreases ????? why??????????????
Electrical Design specifications
whow we find out dc motor field aur armature resistance
what & how to check the lightning arrester
We have 2 11kv/433v transformers for 2saperate acb for mv panels and 1 bus coupler acb. Suppose I’ll close bus coupler what will happen or it will be share the load. Please suggestion and any modification required.
We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Suppose we have long 2 core DC cables running from our DCDB in control room to the load (length of around 2 to 3 km). Do we need to protect these long DC cables from earth leakages or not? If yes how?
For load of 1 nos 3 TR Air Conditioners,6nos of 60 Watt Tibe Lights, 2 nos 200 W Outdoor Lights,1 no Coffee maker.All may work at the same timehow do I select DG Set Rating ,pLease advise the calculations
Role of active and reactive Power sharing in between two synchronized Generators, Droop Setting role ?