Answer / rehan sajid dharme
There are the difference set of curves for which the MCB is programmed to take the initial inrush of current I.e. Starting current of the load
B curve MCB: 2-3 times of full load current
C curve MCB: 5-7 times of full load current
D curve MCB: 10-12 times of full load current
So depending upon the type of load i.e. Resistive or inductive we can make the selection appropriately
| Is This Answer Correct ? | 2 Yes | 0 No |
what happens to current , when voltage drops .?
what is the formulae for selcting capacitor bank to increas pf
Bus-bar is made of which material & name of mostly used material in bas-bar design ?
what is different between buchhoz relay and pressure relife devices in transformer
Why is shaft current insulation required on large motors & when should it be checked i.e. before or after assembly?
How we can calc. the Backup time of a battery Bank???
In hydro plant,generally we install vertical hydro generators..why dont we recommend horizontal one??
What is the meaning of BREAKING and MAKING CAPACITY in case of CIRCUIT BREAKERS.
How to calculate VCB rating for 33KV ,25 MW Power line?
15 kva dg set single phase takes 63amp( approximate) while same rating 15kva three phase takes 35amp approximate. why ? and what will be per phase current for 15 kva
if the load is 80 amp for main fuse and 100 amp for breaker so how can we calculate the cable size (cooper ) .
transmisssion type
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)