How to calculate the diesel generator efficiency? what
details are required to identify the running diesel
generator sets with 1000 kVA & 180 kVA?
Answers were Sorted based on User's Feedback
Answer / m.s.srinivasan
The diesel generating set efficiency is calculated interms
of units generated per liter of diesel consumed.
To monitor either you need to have a diesel flow meter
fitted in the supply as well as the return line after the
governer and the KWHr ( Units )generated.
For less accurate measurement a dip readings can be take
along with the units generated predetermined time.
Is This Answer Correct ? | 63 Yes | 33 No |
Answer / rajendra marathe
Efficiency is the ratio of Outpur/Input. In terms of
Generator, it is considered the efficiency is 80%. 1000KVA
is the Vertual power of Generator. KiloWatt is the actual
power of the generator.On basis of KW the ampere rating
load capacity is calculated. For 1000 KVA , KW is 800. The
ampere rating is =1000x KW/240 for Single phase and for 3
phase =1000xkw/440. The Efficiency can be calculated on the
basis of load ampere it can withstand.
Is This Answer Correct ? | 25 Yes | 14 No |
Answer / jag
The generator efficiency is calculated by units
generated/diesel consumed.
Is This Answer Correct ? | 16 Yes | 8 No |
Answer / faisal
Step 1
Determine the amount of fuel consumed in an hour by the generator. You can use a diesel fuel consumption chart to calculate how much fuel is used in an hour by generators of various sizes.
Step 2
Determine the total electrical power load consumed during an hour. This can be done by connecting a kilowatt-hour meter to the output of the generator, or by referencing the electrical output label on the generator.
Step 3
Convert the amount of fuel used to British Thermal Units, or BTUs. The Oak Ridge National Laboratory has a chart that has the number of BTUs in various types of fossil fuels.
Step 4
Convert the fuel's BTU value to kilowatt-hours by using the conversion factor of 1 kWh = 3413 BTU.
Step 5
Divide the output of the generator in kWh by the input value of the fuel used in kWh. Multiply this figure by 100 to express it as a percent.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / naresh kumar
dear all i want to know the effiency of 250kva dg set
Is This Answer Correct ? | 8 Yes | 5 No |
You did not say what efficiency, whether you get good KWH/ diesel consumption or whether the genset is loaded efficiently
Whatever, you need a KWH METER AND DIESEL CONSUMPTION METER.If you run your 1000KVA gen set for 20 hrs.your genset say at 0.8 pf it could have generated;
1000kva x 0.8 =800KWH per hr .SO FOR 20 Hrs s 16000KWH. If YOUR KWH generated reading says 12000kwh than your generator usage effiociency is 12000/16000 =75%
If the diesel consumption was 600ltrs than kwh/l is
12000/600 =20KWH/Litre diesel. you have to calculate seperately for both of them.
Is This Answer Correct ? | 36 Yes | 34 No |
Answer / sanat khan
Answer
# 4 Units generate/litres consumed
Thanks for Marking this Answer
Answer
# 1 The diesel generating set efficiency is calculated
interms
of units generated per liter of diesel consumed.
To monitor either you need to have a diesel flow meter
fitted in the supply as well as the return line after the
governer and the KWHr ( Units )generated.
For less accurate measurement a dip readings can be take
along with the units generated predetermined time.
Thanks for Marking this Answer 0 M.s.srinivasan
Is This Answer Correct ? | 8 Yes | 9 No |
Answer / manjunatha ac
units generated/ diesel consumed
EX=1000 units generated /350 ltrs consumed
1000/350=3.5 IS dg efficiency.
Is This Answer Correct ? | 3 Yes | 9 No |
Answer / p prudvi krishna
dg set efficiency can be caluclated using forumala that number of units generated divided by total disel consumption ,
disel consumption include on time disel level + pumping during set running-offtime disel level any generator from 320 kva gives an average efficiency of 3.6 to3.8 units per litere
Is This Answer Correct ? | 3 Yes | 10 No |
30 kVA and voltage 380/220VAC how to find out kA?
Why semi-conducting insulation is used in XLPE cables?
length of 4 core cable 95mm from substation LV VFD panel to Motor at field approximately 150 meter. Motor stop and power has been isolated from LV MCC ( Substation )to disconnect Motor for services. After Motor completed service propose to reinstall and reconnect Motor Cable, found earth cable sparkling during touching at metal / motor body. Inspect by clamp meter found earth cable have current flow AC 1-2amps and all earth cable at MCC LV also have current flow as same value. why it is happen?
how step up transformer step up the voltage and what is the reason behind it?
Can anybody tell the formula to calculate temparature rise in the cable with respect to current?
Why we do 2 types of earthing on transformer (ie:)body earthing & neutral earthing , what is function. I am going to install a oo kva transformer & 380 kva dg set what should the earthing value?
How much should be the specific gravity of a DG set battery Electrolyte.
PRV (Pressure relief valve) Trip with oil splash outside power transformers
WHAT INSTRUMENT IS USED TO MEASURE THE MAGNETIC FLUX?
Why do we give DC excitation to AC Synchronous motor??
9 Answers Lance, MBM, Polycab,
how to convert 1 phase power to 3phase power by using induction motor. . . .
is there any phase difference occurs while primary and secondary side mutual induction occurs?