How to calculate the diesel generator efficiency? what
details are required to identify the running diesel
generator sets with 1000 kVA & 180 kVA?
Answers were Sorted based on User's Feedback
Answer / m.s.srinivasan
The diesel generating set efficiency is calculated interms
of units generated per liter of diesel consumed.
To monitor either you need to have a diesel flow meter
fitted in the supply as well as the return line after the
governer and the KWHr ( Units )generated.
For less accurate measurement a dip readings can be take
along with the units generated predetermined time.
| Is This Answer Correct ? | 63 Yes | 33 No |
Answer / rajendra marathe
Efficiency is the ratio of Outpur/Input. In terms of
Generator, it is considered the efficiency is 80%. 1000KVA
is the Vertual power of Generator. KiloWatt is the actual
power of the generator.On basis of KW the ampere rating
load capacity is calculated. For 1000 KVA , KW is 800. The
ampere rating is =1000x KW/240 for Single phase and for 3
phase =1000xkw/440. The Efficiency can be calculated on the
basis of load ampere it can withstand.
| Is This Answer Correct ? | 25 Yes | 14 No |
Answer / jag
The generator efficiency is calculated by units
generated/diesel consumed.
| Is This Answer Correct ? | 16 Yes | 8 No |
Answer / faisal
Step 1
Determine the amount of fuel consumed in an hour by the generator. You can use a diesel fuel consumption chart to calculate how much fuel is used in an hour by generators of various sizes.
Step 2
Determine the total electrical power load consumed during an hour. This can be done by connecting a kilowatt-hour meter to the output of the generator, or by referencing the electrical output label on the generator.
Step 3
Convert the amount of fuel used to British Thermal Units, or BTUs. The Oak Ridge National Laboratory has a chart that has the number of BTUs in various types of fossil fuels.
Step 4
Convert the fuel's BTU value to kilowatt-hours by using the conversion factor of 1 kWh = 3413 BTU.
Step 5
Divide the output of the generator in kWh by the input value of the fuel used in kWh. Multiply this figure by 100 to express it as a percent.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / naresh kumar
dear all i want to know the effiency of 250kva dg set
| Is This Answer Correct ? | 8 Yes | 5 No |
You did not say what efficiency, whether you get good KWH/ diesel consumption or whether the genset is loaded efficiently
Whatever, you need a KWH METER AND DIESEL CONSUMPTION METER.If you run your 1000KVA gen set for 20 hrs.your genset say at 0.8 pf it could have generated;
1000kva x 0.8 =800KWH per hr .SO FOR 20 Hrs s 16000KWH. If YOUR KWH generated reading says 12000kwh than your generator usage effiociency is 12000/16000 =75%
If the diesel consumption was 600ltrs than kwh/l is
12000/600 =20KWH/Litre diesel. you have to calculate seperately for both of them.
| Is This Answer Correct ? | 36 Yes | 34 No |
Answer / sanat khan
Answer
# 4 Units generate/litres consumed
Thanks for Marking this Answer
Answer
# 1 The diesel generating set efficiency is calculated
interms
of units generated per liter of diesel consumed.
To monitor either you need to have a diesel flow meter
fitted in the supply as well as the return line after the
governer and the KWHr ( Units )generated.
For less accurate measurement a dip readings can be take
along with the units generated predetermined time.
Thanks for Marking this Answer 0 M.s.srinivasan
| Is This Answer Correct ? | 8 Yes | 9 No |
Answer / manjunatha ac
units generated/ diesel consumed
EX=1000 units generated /350 ltrs consumed
1000/350=3.5 IS dg efficiency.
| Is This Answer Correct ? | 3 Yes | 9 No |
Answer / p prudvi krishna
dg set efficiency can be caluclated using forumala that number of units generated divided by total disel consumption ,
disel consumption include on time disel level + pumping during set running-offtime disel level any generator from 320 kva gives an average efficiency of 3.6 to3.8 units per litere
| Is This Answer Correct ? | 3 Yes | 10 No |
can u give me a brief idea about power line carrier communication ??
who & how the notations given as RYB to 3phase power supply.
we use 400/5A ct and 35/roor3KV,/0.1/root3KV,0.1/root3KV pt ratio. What is the multiple factor of this meter.
Why star delta starter is preferred with induction motor?
What type interview questions ask in Electrical technicians
what is saturation? what role it plays in operation of ct's,motors etc and how its affects the behaviour of the same.
How to put breaker in service / test position.
how to select the automotive wire size by mathematical calculation. for xenon headlamp with ballast. the ballast given data voltage 10-17v,current permenant 6amp, run up phase is 15amp, peak at swicth on max 400micro sec is 40amp.the sum of cable resistance is 150mohm.please provide referenc document if any for relating the peak at switch on current,time & wire wire size
how can we measure rotor current of a 3phase wound rotor induction motor connected to liquid resistance starter
anybody can give the voltage value for 1M ohm
which bulb is greater iluminited, 60w and 100w are conected in series?
In Aeroplane what circuitry or method use for earthing?
9 Answers Bhel, EDA, Wind World,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)