How to calculate the diesel generator efficiency? what
details are required to identify the running diesel
generator sets with 1000 kVA & 180 kVA?
Answers were Sorted based on User's Feedback
Answer / m.s.srinivasan
The diesel generating set efficiency is calculated interms
of units generated per liter of diesel consumed.
To monitor either you need to have a diesel flow meter
fitted in the supply as well as the return line after the
governer and the KWHr ( Units )generated.
For less accurate measurement a dip readings can be take
along with the units generated predetermined time.
| Is This Answer Correct ? | 63 Yes | 33 No |
Answer / rajendra marathe
Efficiency is the ratio of Outpur/Input. In terms of
Generator, it is considered the efficiency is 80%. 1000KVA
is the Vertual power of Generator. KiloWatt is the actual
power of the generator.On basis of KW the ampere rating
load capacity is calculated. For 1000 KVA , KW is 800. The
ampere rating is =1000x KW/240 for Single phase and for 3
phase =1000xkw/440. The Efficiency can be calculated on the
basis of load ampere it can withstand.
| Is This Answer Correct ? | 25 Yes | 14 No |
Answer / jag
The generator efficiency is calculated by units
generated/diesel consumed.
| Is This Answer Correct ? | 16 Yes | 8 No |
Answer / faisal
Step 1
Determine the amount of fuel consumed in an hour by the generator. You can use a diesel fuel consumption chart to calculate how much fuel is used in an hour by generators of various sizes.
Step 2
Determine the total electrical power load consumed during an hour. This can be done by connecting a kilowatt-hour meter to the output of the generator, or by referencing the electrical output label on the generator.
Step 3
Convert the amount of fuel used to British Thermal Units, or BTUs. The Oak Ridge National Laboratory has a chart that has the number of BTUs in various types of fossil fuels.
Step 4
Convert the fuel's BTU value to kilowatt-hours by using the conversion factor of 1 kWh = 3413 BTU.
Step 5
Divide the output of the generator in kWh by the input value of the fuel used in kWh. Multiply this figure by 100 to express it as a percent.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / naresh kumar
dear all i want to know the effiency of 250kva dg set
| Is This Answer Correct ? | 8 Yes | 5 No |
You did not say what efficiency, whether you get good KWH/ diesel consumption or whether the genset is loaded efficiently
Whatever, you need a KWH METER AND DIESEL CONSUMPTION METER.If you run your 1000KVA gen set for 20 hrs.your genset say at 0.8 pf it could have generated;
1000kva x 0.8 =800KWH per hr .SO FOR 20 Hrs s 16000KWH. If YOUR KWH generated reading says 12000kwh than your generator usage effiociency is 12000/16000 =75%
If the diesel consumption was 600ltrs than kwh/l is
12000/600 =20KWH/Litre diesel. you have to calculate seperately for both of them.
| Is This Answer Correct ? | 36 Yes | 34 No |
Answer / sanat khan
Answer
# 4 Units generate/litres consumed
Thanks for Marking this Answer
Answer
# 1 The diesel generating set efficiency is calculated
interms
of units generated per liter of diesel consumed.
To monitor either you need to have a diesel flow meter
fitted in the supply as well as the return line after the
governer and the KWHr ( Units )generated.
For less accurate measurement a dip readings can be take
along with the units generated predetermined time.
Thanks for Marking this Answer 0 M.s.srinivasan
| Is This Answer Correct ? | 8 Yes | 9 No |
Answer / manjunatha ac
units generated/ diesel consumed
EX=1000 units generated /350 ltrs consumed
1000/350=3.5 IS dg efficiency.
| Is This Answer Correct ? | 3 Yes | 9 No |
Answer / p prudvi krishna
dg set efficiency can be caluclated using forumala that number of units generated divided by total disel consumption ,
disel consumption include on time disel level + pumping during set running-offtime disel level any generator from 320 kva gives an average efficiency of 3.6 to3.8 units per litere
| Is This Answer Correct ? | 3 Yes | 10 No |
define digital electronic
different between electrical and electronics Engineering????
if main CT is of ratio 50/5, and meter CT is -/5 what will be overall multiplying factor of meter.PT is 11000/110 .
hi frienda We have 250kva cater pillet dg set we are fasing one diffrent proublam in dg we are start dg set after one mint applying load around 450a load but dg was run 3 Or 4 mints after 3 mints dg was shuding down automatic how to face this proublam pls tel any budy
Why MCCB is Getting tripped sometimes when there is no load in the Midnight ?
what parameters should we check to reduce the power bill
Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..
Why DC Currents are not used in transformer?
Help need in transformer !? Hello Friends The parameters of 2300/230 v 50hz t/f is R1=0.286 ohm R`2=0.319 ohm Rc=240 ohm X1=0.73 ohm X`2=0.73 ohm Xm=49.2 ohm Secondary Load impedance ZL=0.387+J0.29 solve the exact equivalent circuit with normal voltage across primery.. I know every thing but i cant find CURRENT I1=? and I`2=? Please help me give solution or only Formula please please...
Which Machine u will prefer to use at a place where flammable gases are coming out & why ?
a induction motar has 30-35% exciting current at no load but in transformer it is only 2-3% ofbrated current why any reason?
What are the commercial names of overhead conductors used in India?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)