30 kVA and voltage 380/220VAC how to find out kA?
Answers were Sorted based on User's Feedback
Vipul Kumar your answer is wrong.
W is not = 1.732x380xI. W =1.732x380xIx PF. You left off
the power factor
Bala your answer is wrong also.
KA is not equal power/ (1.732*400*% of Impedance)Note
spelling of impedance. Where did you go to school?
Amps = 30 KVA/ (0.380 x 1.73)or 30000 va/380 x 1.73
Amps = 46
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / simon
30Kva=30,000va
30,000 VA=440V*68.1818 Amp*1 (Pf)
Hense Ka=0.068
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vipul kumar rai
W=1.732x380xI
30x1000=1.732x380xI
I=30000/658.16
I=45.581 ( FOR THE PRIMARY CURRENT )
W=1.732x220xI
I=78.731 ( FOR THE SECONDRY CURRENT )
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / bala
we need to know the Impedance of the TxR.Becos the Formula for Determine the KA value is
=power/ (1.732*400*% of Impedence)
For EX-
Power = 1500 KVA
Voltage = 400V
Impedance = 6%
short circuit = 1500*1000/(1.732*400*0.06)
= 36085A or 36 KA
Is This Answer Correct ? | 0 Yes | 2 No |
from which formula we select a capacitor rating?
what is the rating of Insulation tester for measure 15 KW, 3 phase 415V 50 HZ induction motor?
thermal power station operation in general
11 Answers AJ Square Inc, Jindal, NTPC,
How will polarity test of Dy5 Transformer ?
what is the difference between electrical & electronics
245 Answers Axon Constructions, Banking, GDA Technologies, Infosys, MBA, Satyam, Satyam Tech, Snow White, TCS,
what is the formula for calculating the phase clerance between two phases and phase to earth how to calculate the cable for a motor
why dc did not flows to earth?
what is the range of using dol starter & star delta starter.
Post possible questions for Power Factor Panel FAT / SAT
A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e in running condition) whether there is actual earth fault in rotor or not.
why we are using DC supply in megger?
What sort of protection scheme do you suggest for the protection of a 10 HP motor?