How to calculate the diesel generator efficiency? what
details are required to identify the running diesel
generator sets with 1000 kVA & 180 kVA?
Answers were Sorted based on User's Feedback
Answer / imran mazhar
You did not say what efficiency, whether you get good KWH/
diesel consumption or whether the genset is loaded
efficiently
Whatever, you need a KWH METER AND DIESEL CONSUMPTION
METER.If you run your 1000KVA gen set for 20 hrs.your
genset say at 0.8 pf it could have generated;
1000kva x 0.8 =800KWH per hr .SO FOR 20 Hrs s 16000KWH. If
YOUR KWH generated reading says 12000kwh than your
generator usage effiociency is 12000/16000 =75%
If the diesel consumption was 600ltrs than kwh/l is
12000/600 =20KWH/Litre diesel. you have to calculate
seperately for both of them.
Is This Answer Correct ? | 18 Yes | 27 No |
draw the restricted earth fault protection circuit install on power transformer and identify its parameters and draw C/C curve of it
In industries Power factor is maintained by installing a suitable KVAR bank, How is the PF maintained for domestic use, where is the capacitor bank connected
y we use neutral,all r told its used to for closed path..k its a just used to closed path,in a transmission line y we put same conductor used n both phase and neutral..if we use less than phase conductor in neutral mean we ll reduce cost its right r wrong..if we use mean any problem occur in transmission line..
what is basic difference betmeen normal & flame proof motor??
What are the different towers used in 132kv transmission line? what are the differences between the P,R,S towers used in 132KV and detailed explanation
hi if anybody got model questions for cpcl Grade'A' electrical engineer position.send it to my mail please krishkumar22@gmail.com
Please help me.What are the difference between two wire, 3wire, and 4 wire in electric meter?
What is the purpose of shunt trip in ACB function?
what is single phase motor?
How can we prevent the (Home)inverter supply flow to the main supply line?
how many desk top computer can connect to a 25kva 3phase generator?
in dc series motor if field wdg is shorted then