How to calculate the diesel generator efficiency? what
details are required to identify the running diesel
generator sets with 1000 kVA & 180 kVA?
Answer Posted / sanat khan
Answer
# 4 Units generate/litres consumed
Thanks for Marking this Answer
Answer
# 1 The diesel generating set efficiency is calculated
interms
of units generated per liter of diesel consumed.
To monitor either you need to have a diesel flow meter
fitted in the supply as well as the return line after the
governer and the KWHr ( Units )generated.
For less accurate measurement a dip readings can be take
along with the units generated predetermined time.
Thanks for Marking this Answer 0 M.s.srinivasan
| Is This Answer Correct ? | 8 Yes | 9 No |
Post New Answer View All Answers
Keywords: Die, Card, Coin, B/N 2 To 12
in shunt clippers why a resistor is used in sereis with the input
what is the meaning of vcc
difference between semiconductor & conductor & insulator?
How may I enrol or get admission to your program?
We need to current density & short circuit calculation at 65kA for aluminium & copper busbar.
how to meas-our losses for L.T & H.T
What are the types of the glands and difference between single and double compression type of cable Glands.
who can measure the size of power cable?
i have flexible wire. size of conductors is 0.190 mm & no.of conductors are 48. then size of wire comes 1.37 sqmm instead of 1.5 sqmm . the what is tolerance for this size.
How much kv gas generator is needed to run 2 hp and 1 hp airconditioners, plus a refrigerator and 4 Tvs
what is the sludge current
What is the working principle of CFL & T5 tube light & 40W tube light with electronic ballast?
How can we calculate the motor frame sizes?
anyone knows service engineer in chennai for EDM SPARKING MACHINE.CHMER PULSE CD 60 M.pL GIVE ANY CONTACT NOS