How to calculate the diesel generator efficiency? what
details are required to identify the running diesel
generator sets with 1000 kVA & 180 kVA?
Answer Posted / m.s.srinivasan
The diesel generating set efficiency is calculated interms
of units generated per liter of diesel consumed.
To monitor either you need to have a diesel flow meter
fitted in the supply as well as the return line after the
governer and the KWHr ( Units )generated.
For less accurate measurement a dip readings can be take
along with the units generated predetermined time.
| Is This Answer Correct ? | 63 Yes | 33 No |
Post New Answer View All Answers
State nyquist stability criterion.
Difference between a pilot wire and a normal conductor?
what is the effect of power factor of machines in starting current
Explain the propagation of harmonics in the network and influence of phase angle of harmonics.
What will be the output voltage of a transformer if it is primarily energized from a square wave voltage source?
What is MSL designation of a motor and same may be provided in details.
what is the formula for computing cable tray size & capacity
1.why we are using metal oxide gapless block in lightning arrester,2.What is minimum and maximum rating of metal oxide blocks using in india
how indusrial diesel generator work
why we use condenser in the thermal power plant, althrough the same vapour will be again heated
what ispositive, negative, zero sequence impedence?
1)Explain why the cradle guard is used on railway crossing in overhead line construction?
ROC converges if poles and zeros lie inside a. Origion b. Z=1
ho can we calculate the conductor insulation value according to their ratings like voltage,current etc.how insulation value related with voltage,current and power of amachine
what is the size of cable for 15kw motor and 85 meter cable length using with vfd