How to calculate busbar size & what is the procedure we
make for determine that?
Answers were Sorted based on User's Feedback
Answer / sujata wagh
Generally current carrying capacity of Al. is 0.8A per
sqmm and Copper is 1.6A per Sqmm.
Suppose we need bus bar for 630A, and we are going with
Aluminium bus bar
= 80*10*.8=640A
where 80*10 is size if bus bar usually available is the
market.
so we can use 80x10sqmm al. busbar per phase for 630A.
for TPN- (3.5)x80x10
If we are going with Copper bus bar
than we will use = 40x10sqmm per phase
= 40x10x1.6=640A
where 40*10 is size if bus bar usually available is the
market.
so we can use 40x10sqmm copper busbar per phase for 630A.
for TPN- (3.5)x40x10
| Is This Answer Correct ? | 246 Yes | 46 No |
Answer / ashraf majid
The busbar size will be determined by the total loads
connected to the bus.This will require a comprehensive
study of nature of loads plus the surroundings of place.
The general procedure will be such that the operating
parameters don't voilate the maximum safety limits of the
bus.
| Is This Answer Correct ? | 145 Yes | 65 No |
Answer / kajajohn
to calculate bus bar size normally for copper 1 sqmm =1.3 A
for aluminium 1 sqmm =0.8 Amps
| Is This Answer Correct ? | 129 Yes | 49 No |
Answer / bhavin shah
busbar sizes can not be calculated only from overall size.
there are various derating factors like arrangment of
busbar, nos of busbar, spacing, enclouser size, ventilation
in room, temp rise, skin effect, proximity effect etc.
which need to be consider while designing the busbar.
| Is This Answer Correct ? | 64 Yes | 15 No |
Answer / akmal
i want to add in vijay answer that the qulity of copper also
depend on amper rating of coper bar
| Is This Answer Correct ? | 65 Yes | 22 No |
Answer / jaydev jena
current density= .8 amp/sqmm.that does mean 1sqmm can carry
0.8 amp current .if sisze of busbar is 100mmx 10 mm then it
can carry 800 amp.
| Is This Answer Correct ? | 61 Yes | 25 No |
Answer / nikhan
The bus bar size normally for copper 1sqmm=1.3Am and
aluminium is 1sqmm=0.8Amp
| Is This Answer Correct ? | 53 Yes | 20 No |
Answer / waves
Generally current carrying capacity of Al. is 0.8A per
sqmm and Copper is 1.6A per Sqmm.
Suppose we need bus bar for 630A, and we are going with
Aluminium bus bar
= 80*10*.8=640A
where 80*10 is size if bus bar usually available is the
market.
so we can use 80x10sqmm al. busbar per phase for 630A.
for TPN- (3.5)x80x10
If we are going with Copper bus bar
than we will use = 40x10sqmm per phase
= 40x10x1.6=640A
where 40*10 is size if bus bar usually available is the
market.
so we can use 40x10sqmm copper busbar per phase for 630A.
for TPN- (3.5)x40x10
| Is This Answer Correct ? | 40 Yes | 7 No |
can you give any example at any parameters?
| Is This Answer Correct ? | 62 Yes | 37 No |
Answer / md.mahmudul hasan
we need to consider short ckt(KA) also. Say short ckt level
is 20KA then we need to select busbar accordingly.
| Is This Answer Correct ? | 30 Yes | 5 No |
What is the tolerence limit between neutral and earth in 230 V AC System?
If a rotary UPS is in line through grid power; What would be the impact on Power Factor if the load through rotary ups is 25% , 50% , 75% & 100%. Will the power factor reduce with less load?
Why the CT Secondary is rated as 5A generally?
We are designer please help me calculate the size of 11kv cables from step up transformer to M.V panel, total load is 5 mega watt distance 900 feet (used aluminum type cables) please provided formula for calculate the cable with example.
kva/kvr
in thermal power plant the steam produced is made to cool after falling on the turbine blades. my question is why this is done while the same is needed to heat up again. "jab pani ko wapis garam hi karna hai to thanda kyu karte hai"
Why an ac solenoid valve attract the plunger even though we interchanges the terminal? Will the poles changes?
Why the earth terminal pin is larger than phase and neutral in three pin plug top>
Why relay connected R phase and B phase.?
why we earth only one side of a power cable. And which side is advisable to earth.
how to measure the dc current?
WHICH SUPPLY IS BETTER FOR 4 MW LOAD. 1)TO TAKE NEARER AVAILABLE 11 KV SUPPLY OR 2)TO TAKE 33 KV SUPPLY WHICH IS AVAILABLE AT 10 KM DISTANCE BY INVESTING NEARLY 50-60 LACKHS
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)