How to calculate busbar size & what is the procedure we
make for determine that?
Answers were Sorted based on User's Feedback
CURRENT DENSITY OF CU=1.2A/MM2
CURRENT DENSITY OF AL=.8A/MM2
FOR EX: DESIGN REQUIREMENT OF 400A MAX.CAPACITY.
CONSIDER THE BUSBAR IS CU.
AREA OF THE BUSBAR=400A/1.2=333.33MM2
APPROX. VALUE= 350MM2
SO THAT, THE STANDARD SIZE IS 50MMX8MM
| Is This Answer Correct ? | 33 Yes | 9 No |
Answer / khan
Usually busbar sizes selection depends mainly on two
factors. Which is current + temperature. The size which you
are going to select must carry the current you need and
must not create much heat which excess the limits.
Our formula , we use 1.5 A / 1 sqmm.
| Is This Answer Correct ? | 28 Yes | 9 No |
Answer / jk
Aluminum current transfer capacity :0.8 amps/sq mm
Copper current transfer capacity :1.6 amps/sq mm
Example:640 amps
x= 640 / .8 = 800 sq mm
800/10 (Say 10 mm Width)
L=80 MM, W=10 MM
| Is This Answer Correct ? | 17 Yes | 5 No |
Answer / jad
Please Give the references........otherwise its very
confusing....!
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / renukaswamy
We have consider so many factors to calculate Busbar sizing.
a) Current carrying capacity : for that Copper can go upto
1.6A/Sq.mm and Aluminium is 1A/Sq.mm
b) Ambient temp. and temp. rise to considered.
c) Heat loss to be considered.
d) Short circuit current to be considered.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / dubai
The bus bar size normally for copper 1sqmm=1.25Amp and
aluminium is 1sqmm=0.8Amp
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / karim halawa
simply the dinesty of the copper equal 2A/mm2 or 1.5A/mm2
accprding purity of the substance so using mentioned
formula to get size of bus bar .
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / gajanan
I want to ask to vijay that is there any relation between
current denesity of copper and material purity.
also is ther any standard which defines the standard
current denesity of material.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / rohit bhardwaj
Thumb rule for copper is 1.25 Amps per sq.mm and for Aluminum 0.8 amps for sq.mm
| Is This Answer Correct ? | 8 Yes | 3 No |
what is diffrence between MH LAMP and HELLOZEN LAMP
th how could we differentiate between armoured copper and armoured aluminium cable what is the basic application? why we prefer the armoured copper as compared to armoured aluminium.
how many types of ratings are there of transformer
What Happen When We provide Dc Supply to Ac Motor
How check electrical motor winding.
tube light how its working.,?
When the DG is running at the time we can connect to capacitor banK? why it is required or not
difference b/w series¶llel
what is the difference between unarmoured & Flexible cable? How to identified?
0 Answers Priyanka Electricals,
What is difference between miniture circuit breaker and module case circuit breaker up to 63Amp.
what is the form factor of DC voltage
why firewall is build up between two transformer (220/11kv,50MVA)?what should be the firewall height?what is the clearance between firewall and transformer?
2 Answers Siemens, Tous Stadt,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)