Dear sir/mam
Iwant complete details of Naintenence of 33kv/433v
Transformer having 1250 KVa
Dear friend,
In routing maintenance you should take care of the
following .
Daily .
1. Percentage loading of a transfomer
2. Make sure the bucholze realy is full with oil no inert
gas is there if there then purge the same.
3. Check the record the Reading of OT & WT
4. Check manualy for any leakage from any part of the
transformer.
5. Check for any abnormal heating & noice in transformer.
Quarterly.
1. Check & change the silica gel of the breather .
2. Check teh Safety function tripping of HT breaker related
to transformer. ( tripping point of OT , WT & Tranfomer )
Annualy.
1. Check & fillter the Trasformer oil
2. with complete shut down take the reading of insulation
resistance of the transformer winding.
3. Open & check the condition of transformer HT & LT
bushing for any cracks or damage.
4. Chceck the condition of the earthing pit & take the
earthing resistance value for all the earthing pit (
Neutral & Body earth )
Do the same as directed & have a trouble free operation of
the transformer for a long period of time
| Is This Answer Correct ? | 3 Yes | 0 No |
maintenance parameters of sewage treatment plant
When we give supply to a transformer 11 kv and we get 415v from it, so when we give supply to same transformer 415v on ht side what we get? and When we gives supply to any transformer to L.T. side 415v or 220v What supply is on H.T. side?
how does the terminal voltage of transmission lines increase when a capacitor is connected???? This happens not only in transmission lines but also in all circuits. How??? When a capacitor is connected in a transmission line, capacitor also takes energy from the same supply. But how is it able to increase the terminal voltage??? Practically What sequence of events happen during increase in voltage???
What is the maximum current carrying capacity for both copper and aluminium cables for 1sqmm?
What meant by lagging and leading? When if they are occurred what preventive methods should be taken?
14 Answers ABB, L&T,
what is the role of energy meter in distribution system ???? technical and non technical losses in distribution system????
for compensate 315mh inductance ,how many capaciance required?
What is 11 N1 and 12 N2 in single phase Transformer ?
Transformers with dc supply
i want the formula of total eletical knowledgement
What is instrumental error?
what is the responsibilities of electrical project engineer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)