Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calculate busbar size & what is the procedure we
make for determine that?

Answers were Sorted based on User's Feedback



How to calculate busbar size & what is the procedure we make for determine that?..

Answer / shilesh kumar

Generally current carrying capacity of Al. is 0.8A per
sqmm and Copper is 1.6A per Sqmm.

Suppose we need bus bar for 630A, and we are going with
Aluminium bus bar

= 80*10*.8=640A
where 80*10 is size if bus bar usually available is the
market.
so we can use 80x10sqmm al. busbar per phase for 630A.

for TPN- (3.5)x80x10


If we are going with Copper bus bar
than we will use = 40x10sqmm per phase

= 40x10x1.6=640A
where 40*10 is size if bus bar usually available is the
market.
so we can use 40x10sqmm copper busbar per phase for 630A.

for TPN- (3.5)x40x10

Is This Answer Correct ?    0 Yes 1 No

How to calculate busbar size & what is the procedure we make for determine that?..

Answer / vijaykumarht

Depending on the maximum load current the busbar size will
be determined. Usually for copper it is taken as 2 to 4 Amps
per square mm and for alluminium it is taken as 1 to 2 Amps
per sqmm.
The normal availability and design of the busbars is
25*5mm,50*5mm,50*10mm,60*10mm.

Is This Answer Correct ?    57 Yes 61 No

How to calculate busbar size & what is the procedure we make for determine that?..

Answer / john philip

As per the load we have to calculat but we should choos a
good conducter with low resistenc value

Is This Answer Correct ?    11 Yes 16 No

How to calculate busbar size & what is the procedure we make for determine that?..

Answer / lalit

.8mm=1 amp.

Is This Answer Correct ?    39 Yes 62 No

How to calculate busbar size & what is the procedure we make for determine that?..

Answer / hasan 325

to calculate bus bar u must follow this formula :

wiedth x thickness x1.6 A

And also u can use this information :
A/mm2
100A = 2.5mm2
100-500 A=1.75mm2
500-1000A=1.2mm2
1000-above=1.1mm2

Is This Answer Correct ?    40 Yes 80 No

Post New Answer

More Electrical Engineering Interview Questions

What is auto transformer?

7 Answers   L&T,


What is a roll of adopter panel in terms of h.t. Panel ???

1 Answers  


What is quadrantal symmetry?

0 Answers  


How seriving & testing of the HT & LT breakers are done. What are the standard Ir values on which we can come to know the test is passed or failed?

0 Answers  


what will be the magnetizing current in the testing of 27 MVA transformer?

1 Answers  


In a 3 phase,400v,4 wire system, 2 incandescent lamps, one having 230v,100w and the other 230v,200w are connected between r phase- neutral and y phase-neutral respectively. If neutral wire breaks which lamp will fuse first and why?

3 Answers   Eskom, SSC,


what are the differant std sizes of cable trenches?

0 Answers  


WHAT IS THE THUMBRULE FOR FINDING OUT THE CURRENT CAPICITY OF A COPPER WIRE?? 2.5, 4, 6MM SQUARE ETC...

5 Answers  


how to crack cgpsc,which type of knowledge it is required,where i can get systematic study material and some tips?

1 Answers  


the distance from my office to d.g is aprox 400mtrs and voltage drops ibn my office near about 40 volt what should i do p[ls suggest.

6 Answers  


Can we use the ceiling fan regulator to run drill machine having 2000 watt power consumption?

2 Answers  


Show Details FROM:Muhammed Ikram TO:qa@allinterview.com Message flagged Saturday, June 4, 2011 10:07 PMMessage bodyHello all, i want to ask a question to all of you that what is VMM (voltage monitoring module )? how it work,s? i heard somewhere that it compare 1 phase voltage to other phase voltage. but there is also some setting on it. how to set it,s setting. please tell me briefly. Thank,s and Regard,s. Muhammed Ikram.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)