how to claculate earth strip size for 1500kVA transformer
for neutral and body

Answers were Sorted based on User's Feedback



how to claculate earth strip size for 1500kVA transformer for neutral and body..

Answer / chandan tripathy

As per IS 3043, Cross Section Area of Earthing Conductor
(A) =(If x√t) / K
Where:
t = Fault current Time (Second).
K = Material Constant.
Example: Calculate Cross Section Area of GI Earthing Conductor for System has 50KA Fault Current for 1 second. Corrosion will be 1.0 % Per Year and No of Year for Replacement is 20 Years.
Cross Section Area of Earthing Conductor (A) =(If x√t) / K
Here:
If = 50000 Amp
T = 1 Second
K = 80 (Material Constant, For GI=80, copper K=205, Aluminium K=126).
• Cross Section Area of Earthing Conductor (A) = (50000×1)/80
• Cross Section Area of GI Earthing Conductor (A) = 625 Sq.mm
• Allowance for Corrosion = 1.0 % Per Year & Number of Year before replacement say = 20 Years
• Total allowance = 20 x 1.0% = 20%
• Safety factor = 1.5
• Required Earthing Conductor size = Cross sectional area x Total allowance x Safety factor
• Required Earthing Conductor size = 1125 Sq.mm say 1200 Sq.mm
• Hence, Considered 1Nox12x100 mm GI Strip or 2Nox6 x 100 mm GI Strips

Is This Answer Correct ?    25 Yes 5 No

how to claculate earth strip size for 1500kVA transformer for neutral and body..

Answer / bala.a

you will follow as per State electricity board norms - 50
x 6 mm Cu for Nu and 50 x 6 mm GI FOR body 0r
you will calculate as per short circuit calculation
Formula 0.0054 x root t x I
Where
t =1 second
I = SHORT CIRCUIT CURRENT
example
Fault current- 33kA( assumed )
0.0054 x root 1 x 33000= 178.2 mm
so you will recommended 50 x 4 mm Cu

Is This Answer Correct ?    14 Yes 9 No

how to claculate earth strip size for 1500kVA transformer for neutral and body..

Answer / k.prakashchandra

For above 750 KVA ,earth lead is determined as per I.S.1886

Is This Answer Correct ?    4 Yes 1 No

how to claculate earth strip size for 1500kVA transformer for neutral and body..

Answer / nitin

Mr. Bala,
what is 0.0054factor? Is it root3 divided by current rating
in A/sq.mm? Then for Cu it is 205 A/sq.mm and so root 3
divided by 205 comes to 0.0084. OK?

Is This Answer Correct ?    0 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

What is the purpose of earthing Truck ? How does it work for busbar and cables?

1 Answers  


when the control mechanism is present for an ammeter(1-10A) and 1A current is apllied what will be the reading of the meter?

2 Answers   GATE,


how is classified voltage level in generation,transmission & distribution system?,

7 Answers   Adani,


pls send previous bhel electrical papers

0 Answers   Siemens,


Is a current transformer step up or step down ?

2 Answers  






circuit diagram of trip circuit supervision relay

0 Answers  


What is meant by harmonic distortion?

0 Answers  


The specific heats of the gas at constant pressure and constant volume are respectively 1.0 kJ/kg K and 0.72 kJ/kg K; the value of R for the gas is

0 Answers   Caterpillar,


I have a question, I visit 01 site and face a problem, there is 2.5 ton Air Con working, when air con compressor is running at that time rectifier voltages are increasing upto 290-295 v and rectifier is giving main high alarm (rectifier is APC single phase, before starting compressor rectifier voltages was 230v. when air con is going off rectifier voltages are decreasing smoothly at its actual voltages 230v. Load on Genset phases is this: Red-13.5 amp AC (Air Con load), Yellow-1.7 amp AC (BTS lights etc.) and Blew-4 amp AC (telecom system load), Genset phase to phase and neutral to phase voltages are also ok. These are 10 sites having same system and same rectifier APC brand at every site 02 genset are working but the problem is same at all these 10 sites. What will be the reason behind???

1 Answers  


I have done my m.tech in electrical engg discipline. Can any one please suggest me how should I prepare for getting into phd in iit or nit.How should I prepare for getting into lecturership

0 Answers  


Why we use Electrical energy rather than any other type of energy, mostly? Explain behavior of open secondary CT and short circuited secondary PT in energized condition?

0 Answers  


which INDIAN STANDERD in Mention the earth test value?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)