Difference Between B Curve & C Curve in MCB.
Answers were Sorted based on User's Feedback
Answer / raghavendran
MCB's have tripping curves like B,Cand D.
Curve B type of MCB's are used where maximum sensitivity is
needed and the initial starting current is 3 to 5 times the
rated current.
curve c MCB's are used where close protection is not
required and the starting current is 5 to 10 times the rated
current.these may be used while tripping the circuit due to
high starting inrush current.
curve D MCB's are used where the starting current is very
high 10 to 20 times the rated current, like high capacity
motor installation where initial starting voltage dip may be
very high.
Is This Answer Correct ? | 98 Yes | 4 No |
Answer / anil tandon
The MCBs are classified as per the Holding Currents and thus their usage are define accordingly,
B-Curve MCB:- They have a Holding current of 2 times of rated current and are used for Lighting Loads
C-Curve MCB:- They have a Holding current of 5 times of rated current and are used for motoring Loads.
The MCBs are classified as per the Holding Currents and thus their usage are define accordingly,
B-Curve MCB:- They have a Holding current of 2 times of rated current and are used for Lighting Loads
D-Curve MCB:- They have a Holding current of 10 times of rated current and are used for High Inrush currents E.g -Control Transformer etc
Is This Answer Correct ? | 47 Yes | 6 No |
Answer / arshath
B curve using for domestic
C curve using for industrial
Is This Answer Correct ? | 23 Yes | 5 No |
What is dynamo function in DG sets and draw block diagram?
Please define ohm’s law for a.c (alternating current)?
what does vector group Dyn11 tell us? also tell me how will u differentiate between phase lead and phase lag thru this vector group
3phase motor can be used as a Prime mover for alternator.
what is the advantage of connecting capacitors in delta than in star?
How to calculate the slip ring induction motor rotor current and voltage.
why two over current realy used in vcb.
how much current does 3ph. 10 hp ac motor draw.
When Neutral exceeds or equals the phase current in both single phase * three phase system?
30 kva ups may kitne output voltage hote h
I am an electrical power engineer and arranged power system for a data center, I installed MCB, ELCB and erthing system TN-C-S. But some times several ELCBs Disconnect circuits at the same time! what may be the reason? (the ELCBs are 25A ,30mA)
In a company has been installed an analog amperemeter, this company was suplied by generator X, there is no problem in the ampere meter, rigth now this company's supplied by generator Y then the pointer in amperemeter vibrating. What happened? Why? Thank's