Hai friends I have dought for O2 analyser how to working in boiler area. And what is the basic principles
Answers were Sorted based on User's Feedback
Answer / rambalaji
1. zirconia oxygen analyzers determine oxygen concentration using the conductivity of a zirconia ceramic cell. Zirconia ceramic cells only allow oxygen ions to pass through at high temperatures (750oC). With reference gas on one side and sample gas on the other, oxygen ions move from the side with the highest concentration of oxygen to that with the lowest concentration. The movement of ions generates an EMF (Electro Motive Force) which can be measured to determine the oxygen content
2. The sensor does not actually measure oxygen concentration, but rather the difference between the amount of oxygen in the flue gas and the amount of oxygen in the air. Rich mixture causes an oxygen demand. this demand Causes high voltage to build up due to transportation of oxygen ions through the sensor layer. Lean mixture causes low voltage since there is oxygen Excess. Sensor working in Nernst Principle
In flue gas side O2 is low : High Voltage
In flue gas side O2 is high : Low Voltage
High Concentration : O2 + 4 e 2O2 -
Low Concentration : 2O2 - O2 + 4 e
0% O2 = 0.82 mv
5% O2 = 0.40 mv
21% O2 = 0 mv
| Is This Answer Correct ? | 4 Yes | 0 No |
. When temperature increases the content of oxygen decreases.- principle.
Reference gas(span gas) instrument air 21% O2.
1% gas should provide from cylinder for cal purpose.
| Is This Answer Correct ? | 3 Yes | 1 No |
Can combine control system for Emergency control system (ESD)and Fire & Gas System ( F & G) is possble to built and offer to client? Can such system is as per Norms in India?
what is control valve input and out put
How can I zero check of wet leg type DP Tx ?
what type problems create in radar level transmeter and what is its solution
Example of dry contacts & wet contacts?
What is DCS and PLC scanning time?
Displace type LT to be calibrated in workshop, wt. 40, dia- 60 mm, density- 0.8kg/cm3.
which one is best profibus or RS485 for communication?
what is differential pressure transmitter and transducer? how to work?
what is thermopile?
What are the Components of Siemens S7 300 Series PLC system ?
1.what is controller proportional gain 2.what is the controller intergral action time. 3.A proportional plus derivative controller that has a proportional band of 20% and a derivative action time of 0.1 minutes. Construct the shape of the output waveform for the triangular input if the input rises and falls at the rate of 4 units per minute.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)