If P will increase then what will happen with PID?
Answer / warren holden
Increasing P (proportional gain) will result in faster,
more aggressive, control dynamics with potentially more
overshoot and longer settling time to steady state
condition in the closed-loop response (assuming that I
(integral action time) and D (derivative action time)values
are held constant whilst P is increased).
| Is This Answer Correct ? | 3 Yes | 0 No |
how can we calibrate RADAR LEVEL transmitter 0% to 100%
3 Answers Chevron Phillips, Honeywell,
If an Instrument has 550 ohm internal resistance and the cable used for that instrument is 0.5 ohm per meter resistance. If the voltage is 12volt.How much length cable can be used? Please tell me its Calculation formula.
Any can guide for QA/QC Inspector in oil & gas region, the procedures, formats standards, design criteria, i search in all enginees but i can't found wat i need?????????
4 Answers Aramco, Asian Paints,
what effects a surging can produce in the compressor
in my company organisation in plan to take new PLC system for replacing old relay system , for that what I/P needsd to submit to the system house of PLC supplier?
list of flame proof certification ?
A PLC is programmed to drive three motors A, B and C as follows : After running motor A for an hour, motor B should get ON and motor A should get OFF. And after running motor B for an hour, motor C should get ON and motor B should get OFF. And after running motor C for an hour, motor A should get ON and motor C should get OFF. (That is, a cyclic repetition with time period one hour) Now, the second condition is: If any motor gone faulty and is tripped, the consecutive motor should get ON and the faulty (tripped) motor should be eliminated from cyclic repetition. The remaining two motors should bear the cyclic repetition of one hour each. (For healthy motor take logic as high and for tripped motor take logic as low) Now, the third condition is: When motor A load(Amps) exceeds 60% of its rated load, motor B should get ON in parallel to motor A. And when both motors A & B are running in parallel, and if their load exceeds 60% of their rated load, motor C should also start in parallel to A & B. [Here the cyclic repetition is eliminated, until their loads become normal(40%)] [Take logic high(1) for load at 60% and logic low(0) for load at 40%] Now draw a flow chart or a ladder diagram to fulfill the above condition.
If I want to buy a pressure switch & 3-way valve for hot water application then witch parameter I should consider.
how can you set a zero and span of transmitter?
how to calibrate control valves & power cylinders & ultra sonic level transmitters
Why we are using sqare root in flow?
why we used for range in pnumatic 3-15 psi and current 4-20 ma?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)