what is megar testing
Answers were Sorted based on User's Feedback
Answer / muili ibrahim
Megger tester is a device normally used to measure insulation resistance conductors such electric motor coils, cables, busbar, etc.
| Is This Answer Correct ? | 29 Yes | 2 No |
Answer / n.k baghel
Meger is adevice by which we calculate the high valuw of insulation. and we are use for motor.cable etc.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / suraj kumar
Meger is the Device for Resistance measurement of Motors, LT Cables , HT Cables and Bus bars etc. We Can Confirm faults in Line According to the resistance value with the help of a meger .
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / monu singh
Meger is a device it is measure the insulation capacity of cble
| Is This Answer Correct ? | 10 Yes | 6 No |
i have one source transformer with the capacity of 50KVA, connected with two loads 10kw and second one is 15kw.. how can i calculate first load in KVA and second one in KVA .. because Kva rating, power factor rating of of transformer is different from the load… there must be some way to calculate load KVA rating and power factor….
What is Single Phasing fault???(not single-phase fault)
what is the acceptable insulation resistance for motor/transformer?
2 Answers Reliance, Tata Motors,
Am using an electronic digital display to see the RPM of ABB ACS 550 drive, which is showing negative value when the motor & drive in stop mode but it is showing correct value during the run mode. can anyone help me out??
2 Answers Bala Power Solutions,
during installation time of transformer and alternator which points we have to observed?
Explain types soft starters?
which will glow brighter?bulb 1 (110v,100w) and bulb 2 (230v.200w) series connection
Why is reating of t/f in kva but for inverter in kw ?
Why the dc voltage drop during starting of emergency lube oil pump? The Voltage drop from 135kv to 125 kv for one min. before re-establish to 135kv?
How to calculate the heat load for a electrical room
what is the formula for converting KW into KWH ?
How to calculate mf when meter equipment and meter are connected
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)