Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Dear Friends,

Need your help for connecting APFC panel,
Quotation : I have 2 No’s 1000 KVA Transformers, both transformers are having separate APFC panels, ( Tr-1,400KVAR, TR-2,450 KVAR)
Now I want to stop One transformer, present load is 650Amps, Max, So One transformer is enough, I have switched OFF TR-1, but PF is not maintaining properly, its 0.5, So now I want to connect TR-2 APFC also in TR-1 Loads, Can any one answer for my Quotation with drawing, how to connect TR-2 APFC panel in TR-1 Loads,

Answers were Sorted based on User's Feedback



Dear Friends, Need your help for connecting APFC panel, Quotation : I have 2 No’s 1..

Answer / moh

Please use a bus-coupler circuit breaker between the circuit breaker of TR1 and the circuit breaker TR2 with interlock (mechanical or electrical). When one TR is out the another TR will connect to another load and APFC by the bus -coupler circuit breaker

Is This Answer Correct ?    0 Yes 0 No

Dear Friends, Need your help for connecting APFC panel, Quotation : I have 2 No’s 1..

Answer / moh

Please use bus -coupler circuit breaker between the o/p of the circuit breaker TR1 and the o/p of the circuit breaker of TR2 with mechanical and electrical interlock between the circuit breakers.When one TR gone out the another TR will connect to another load and APFC by the bus-coupler circuit breaker. good luck

Is This Answer Correct ?    0 Yes 0 No

Dear Friends, Need your help for connecting APFC panel, Quotation : I have 2 No’s 1..

Answer / qamar abbas

you may switch on capacitors manually from APFC 2 to control the power factor. if you have the same bus bar connected to both transformers

Is This Answer Correct ?    0 Yes 0 No

Dear Friends, Need your help for connecting APFC panel, Quotation : I have 2 No’s 1..

Answer / srinivasvemana

Dearsir
you placed one ct tr -1 incoming ct connection given in Apfc-2 and apfc-2 power also take from tr-1.after you have 2 apfc panels working on one transformer.

Is This Answer Correct ?    1 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

suppose we using 3 phase motor of 440 v means what range of C.T. is require for measuring current , the rating of motor is 1HP ?

5 Answers  


What size cable (based on voltage drop) is required to supply a 40 A three phase boiler if the wiring system is 75V single insulated cables installed in non-metallic rigid conduit 56m from the main switchboard? Voltage drop in the consumer's mains is 8V.

0 Answers  


list of tests to be carried out at manufacturers end while purchasing a step up transformer of 11kv to 66kv ,2MVa Capacity.

0 Answers  


List examples of voltage source?

0 Answers  


How can we calculate the capacity of the capacitor bank attached with the Main panel, when we know the capacity of the panel installed in KVA Rating?

2 Answers  


What is the form name of 'c' license, I want to download in web

0 Answers   BMM, Ceebros Hotels,


what is difference between vcb and mccb

4 Answers   APTransco,


Which type of air compressor is used now a days in the market. Keeping in mind of energy efficiency and maintenance points. Relevant documents may also be sent on mentioned email ids.

0 Answers   DAE,


Where can I get Iidian straderd specifications for electrical items or works in web? please help me.

0 Answers  


how a resistor resists to flow the current?how an inductor oppses the sudden change in current?how a capacitor opposes a DC voltage.

0 Answers   Hindustan Unilever Limited,


What is the amount of no load current of 630 kVA tranformer voltage ratio 11kV/440V ?

13 Answers  


I have a generator of 300kw.400V,50hz . what is means can i assume the load Red Phase with Neutral 300kw.Yellow phase with neutral 300kw and Blue with neutral also 300Kw. or - red with neutral 100kw same as yelloe and blue phase also giving 100kw with neutral respectively

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)