Dear Friends,
Need your help for connecting APFC panel,
Quotation : I have 2 No’s 1000 KVA Transformers, both transformers are having separate APFC panels, ( Tr-1,400KVAR, TR-2,450 KVAR)
Now I want to stop One transformer, present load is 650Amps, Max, So One transformer is enough, I have switched OFF TR-1, but PF is not maintaining properly, its 0.5, So now I want to connect TR-2 APFC also in TR-1 Loads, Can any one answer for my Quotation with drawing, how to connect TR-2 APFC panel in TR-1 Loads,
Answers were Sorted based on User's Feedback
Answer / moh
Please use a bus-coupler circuit breaker between the circuit breaker of TR1 and the circuit breaker TR2 with interlock (mechanical or electrical). When one TR is out the another TR will connect to another load and APFC by the bus -coupler circuit breaker
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / moh
Please use bus -coupler circuit breaker between the o/p of the circuit breaker TR1 and the o/p of the circuit breaker of TR2 with mechanical and electrical interlock between the circuit breakers.When one TR gone out the another TR will connect to another load and APFC by the bus-coupler circuit breaker. good luck
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / qamar abbas
you may switch on capacitors manually from APFC 2 to control the power factor. if you have the same bus bar connected to both transformers
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / srinivasvemana
Dearsir
you placed one ct tr -1 incoming ct connection given in Apfc-2 and apfc-2 power also take from tr-1.after you have 2 apfc panels working on one transformer.
| Is This Answer Correct ? | 1 Yes | 2 No |
What is DPR relay, And what for??
How the annunciator works ? How to do its wiring
A 2D array X(7,9) is stored linearly column wise in a computers memory.Each element requires 4 bytes for the storage of the value.If the first byte address of X(1,1) is 3000,what could be the last byte adress of X(5,8)?
If the soil resistivity is more large, how can we earthing our 11 k.v. transmission line?
What are the types of Transformer? Name them.
what is busbar and its function/
if we put a energy meter in 500 kvar capacitor bank ,then how much units show in energy meter per day.
why dont we use the same pylon to carry 400 kv plus 220kv and 33 kv ?
2 Answers Focus, Focus Energy,
could mail me the question papers for the test.
Why the CT Secondary is rated as 5A generally?
What are the advantages of autotransformer?
For a 6.6kV Motor it is recommended to do megger test with 500 V d.c and not more than 5kV d.c but the Hi voltage withstand test should be performed by 12kV AC. Why the dc voltage test should be limited but AC voltage withstand test could be with such a high voltage?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)