Dear Friends,
Need your help for connecting APFC panel,
Quotation : I have 2 No’s 1000 KVA Transformers, both transformers are having separate APFC panels, ( Tr-1,400KVAR, TR-2,450 KVAR)
Now I want to stop One transformer, present load is 650Amps, Max, So One transformer is enough, I have switched OFF TR-1, but PF is not maintaining properly, its 0.5, So now I want to connect TR-2 APFC also in TR-1 Loads, Can any one answer for my Quotation with drawing, how to connect TR-2 APFC panel in TR-1 Loads,
Answers were Sorted based on User's Feedback
Answer / moh
Please use a bus-coupler circuit breaker between the circuit breaker of TR1 and the circuit breaker TR2 with interlock (mechanical or electrical). When one TR is out the another TR will connect to another load and APFC by the bus -coupler circuit breaker
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / moh
Please use bus -coupler circuit breaker between the o/p of the circuit breaker TR1 and the o/p of the circuit breaker of TR2 with mechanical and electrical interlock between the circuit breakers.When one TR gone out the another TR will connect to another load and APFC by the bus-coupler circuit breaker. good luck
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / qamar abbas
you may switch on capacitors manually from APFC 2 to control the power factor. if you have the same bus bar connected to both transformers
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / srinivasvemana
Dearsir
you placed one ct tr -1 incoming ct connection given in Apfc-2 and apfc-2 power also take from tr-1.after you have 2 apfc panels working on one transformer.
| Is This Answer Correct ? | 1 Yes | 2 No |
Why HT cable have only 3 core ?
how much resistence in proper earthing?
can u guys pls suggest a good material for learning abt switch yard and its components
what is diffrence b/w -48vdc and +48vdc ?
IR value for 30kw lt motor
Electromotive force is provided by:(a) Resistance’s(b) A conducting path(c) An electric current(d) An electrical supply source
Can we use a absolute encoder to show rpm of a motor ? what about the condition when power is off ? what is difference if a incremental one is used ?abanirout@gmail.com
what is mean by NPS (Negative phase sequence)fault? what is the difference between EFR & OCR faults?
0 Answers TNEB Tamil Nadu Electricity Board, Vestas,
Tan delta point in transformer to be earth or not?
Main CT ration is 400/5, meter CT ratio is open type: -/5A. What is the Multiplying factor of the meter, considering same PT ratio.
difference between ac and dc generators
what happens when the phase and earth wires comes in contact? and why
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)