Dear Friends,
Need your help for connecting APFC panel,
Quotation : I have 2 No’s 1000 KVA Transformers, both transformers are having separate APFC panels, ( Tr-1,400KVAR, TR-2,450 KVAR)
Now I want to stop One transformer, present load is 650Amps, Max, So One transformer is enough, I have switched OFF TR-1, but PF is not maintaining properly, its 0.5, So now I want to connect TR-2 APFC also in TR-1 Loads, Can any one answer for my Quotation with drawing, how to connect TR-2 APFC panel in TR-1 Loads,
Answers were Sorted based on User's Feedback
Answer / moh
Please use a bus-coupler circuit breaker between the circuit breaker of TR1 and the circuit breaker TR2 with interlock (mechanical or electrical). When one TR is out the another TR will connect to another load and APFC by the bus -coupler circuit breaker
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / moh
Please use bus -coupler circuit breaker between the o/p of the circuit breaker TR1 and the o/p of the circuit breaker of TR2 with mechanical and electrical interlock between the circuit breakers.When one TR gone out the another TR will connect to another load and APFC by the bus-coupler circuit breaker. good luck
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / qamar abbas
you may switch on capacitors manually from APFC 2 to control the power factor. if you have the same bus bar connected to both transformers
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / srinivasvemana
Dearsir
you placed one ct tr -1 incoming ct connection given in Apfc-2 and apfc-2 power also take from tr-1.after you have 2 apfc panels working on one transformer.
Is This Answer Correct ? | 1 Yes | 2 No |
If you touch at the end welding machine, will you have shock ?
what are the different sizes of U.G. cable & where these cabl;es are used according to voltage ..
What is deference between MCB & MCCB & ISOLATOR
0 Answers Prakash Industries, Standard Chartered,
For Bus duct hi pot test, where we want to connect the return and ground leads?
for distribution line ratio of x/r 1.<0.1 2.>10 3.>1 4.<0.01
Who are the manufacturer for Nitrogen based Fire Protectio/explosion prevention for Oil Filled Transformers? India and international both?
I am going to appear for the RRB Chennai Section Engineer online exam. Please send me the question papers from 2001 to date to my mail id: vsujith_rajan@yahoo.co.in
Can we connect two CT'S to one energymeter?
WHAT IS THE WINDING PROCEDURE OF ELECTRICAL MOTOR
what is the use of switch disconnector fuse
What is inductance?
WHAT HAPPENING TO TRANSFORMER???? i have the step down transformer rating 230/12v, power rating something.,,, ok. suppose iam giving 12v to secondary side,what will happen on primary side.,,,