Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


A DP Endress and Hauser flow transmitter is always tripping
pump at low flow. set point is 74 cubic meter/hr. Thorough
impulse line flushing and zero calibration has been done,
yet problem persists. What do you think is the problem and
how do you rectify this fault?

Answers were Sorted based on User's Feedback



A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic..

Answer / carl ellis

The stated question assumes that the design criteria for a
low flow alarm SP at 74m^3/hr is valid. It is not clear
whether the problem is limited to the instrumentation
without a clear statement that the pump has been determined
to be operating properly. Since this is an instrumentation
exam, I'll assume the problem is in the instrumentation.

If the instrumentation is the problem, then the DP's
indicated DP/flow rate has to be lower than the alarm SP.
What can cause a DP transmitter to indicate a lower
DP/flowrate than it should?

If the equalizing valve is not tightly closed or leaks at
the valve seat, the DP will be lower than it should be as
the DP approaches zero, depending on the leak rate.

Damaged orifice plates read low, resulting in low indicated
DP readings.

Lower line pressure than the "design" line pressure will
reduce the indicated DP reading.

Someone changed out the orifice plate (OP)with an OP with
bigger bore or re-installed the correct OP backwards.

Since DP operation is "high side pressure minus low side
pressure equals indicated DP", a leak anywhere on the high
side will reduce the high side DP pressure and result in a
low indicated DP. That could be
- leak in the high side impulse line or its fittings
- manifold valve flange gasket leak on the high side or on
the process side
- vent leak
(however liquid leaks are usually visually evident)

In a mis-configured system, the PLC/DCS might have square
root extraction in addition to square root extraction on the
DP transmitter, which would cause a low flow rate indication
at the PLC/DCS.

Tell 'em Carl sent you.

Is This Answer Correct ?    7 Yes 0 No

A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic..

Answer / mohamed

You should see the time delay of the alarm itself and the time lag of the transmitter

Is This Answer Correct ?    3 Yes 0 No

A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic..

Answer / mukesh singh

increase the tripping time,your transmitter might be malfunctioning..follow the trend of DP.

Is This Answer Correct ?    1 Yes 0 No

A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic..

Answer / ntia

Check the strainer of your pump..remember that your pump supplies the pressure...if the pump strainer is dirty...it will be be giving low flow and since your dp was set to shutoff the pump at a low flow..then your dp will continue to shut off the pump until the pump is cleaned and the fault is rectified.

Is This Answer Correct ?    0 Yes 0 No

A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic..

Answer / samir

If it is a malfunction of flow transmitter then you should cross check with portable ultrasonic flow transmitter. Whether it is showing correct or not. & then you can follow previous advise.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

send me model hpcl questions pleas..........my mail id mohideen.dharvesh@gmail.com

0 Answers   HPCL,


why is negative range given to measure the steam drum level

2 Answers   Jindal,


what is absolute pressure, gauge pressure and atmospheric pressure?

2 Answers   Mother Dairy,


what is the process for double acting cylinder pneumatic for 32' v/v

0 Answers  


PLEASE PROVIDE SAMPLES OF CHEVRON SKILL TESTS

0 Answers  


what are the different types of communication cables used in automation and what are the difference in the cables

1 Answers   KN,


What is the principle of a Pressure gauge?

2 Answers   CCIE,


What is Vena contracta?

3 Answers   CCIE,


If you calibrate a pneumatic pressure transmitter, how many adjustments are normally necessary or mandatory?

1 Answers  


Operational amplifiers

0 Answers   CCIE,


what is HVAC?

1 Answers  


Which is your favourite subject & explain any one topic of it.

0 Answers   L&T,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)