in which application we use bigger size actuator
Answers were Sorted based on User's Feedback
Answer / instru
Bigger size actuator are required whenever thrust required
for control valve is higher. Thrust required is higher
whenver control valve has to open against high differntial
pressure. Also whenver type of packing is Graphite , large
size actuators are required because packing friction is
higher compared to PTFE.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / ku
Normally the selection of the actuator is governed by the
maximum dp shutoff for any service, You have find out what
could be maximum possible inlet pressure to the control
valve and minimum possible downstream pressure, which will
provide you maximum delta P that your actuator should
handle, for example you have a column operating at pressure
P1 and a pump is taking suctionfrom this column and the
control valve is at outlet of the pump, the pump is
discharging this material to a drum with certain pressure,
in this case you will take the shutoff pressure of the pump
as inlet pressure and minimum pressure that can be at the
drum. This will automatically result in an actuator sizing
and selection suitable for this service. I am not sure why
you mentioned bigger size actuator as actuator should
be "big enough" to handle the maximum delta P across the
control valve.
| Is This Answer Correct ? | 3 Yes | 0 No |
for high pressure application we use the the bigger actuator is wrong concept, mostly in the early days days we used this kind of actuator, mostly used for diaphragm and piston type actuator , if u use diaphragm type then u need big cascade, for high pressure , but we should change the cascade for regular intervel. in our company we control the 220 kg/cm2 of pressure in the small actuator only, bigger actuator is disturbance only large space is needed and difficult to calibrate. thanks
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / rahul
when valve size is more,
mostely for control valve
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / joby
if the valve is in higher size ,we have to go for higher
actuators for operating the valve.
FOR ESD VALVES
if the valve size is more than 18" mostly the suppliers
prefer hydraulic systems for operating the actuator
instead of air.The pressure required to operate the higher
size actuator will not be sufficient ,if you are using
plant air.
| Is This Answer Correct ? | 1 Yes | 3 No |
why t/c is connected parallel and what is the purpose of it
what is the calibration procedure for transweigh make weigh feeder?
what is formula for calculating flow if i have pressure and pipe diameter?
how we can measure the interface level?is it possible to measure interface level with dp or pressure transmitter?
Why DP transmitters are subjected to high static pressure test of 100 bar. Though they will be used for very small pressure range
how to design orifice plate?what is the equation?
what is the deferance between LCN and UCN.
Isometric drawings are generated during _________________ phase of a project
in my company organisation in plan to take new PLC system for replacing old relay system , for that what I/P needsd to submit to the system house of PLC supplier?
what is the current pay package for an instrumentation engineer having 2 years of experience in cryogenic technology???????
what is Best Among SINK Or SOURCE Type Design In Digital Signal, Either Iput Or Output? WHY?Can any one..
why we use npn sensor in vibration monitoring system
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)