Answer / instru
Bigger size actuator are required whenever thrust required
for control valve is higher. Thrust required is higher
whenver control valve has to open against high differntial
pressure. Also whenver type of packing is Graphite , large
size actuators are required because packing friction is
higher compared to PTFE.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / ku
Normally the selection of the actuator is governed by the
maximum dp shutoff for any service, You have find out what
could be maximum possible inlet pressure to the control
valve and minimum possible downstream pressure, which will
provide you maximum delta P that your actuator should
handle, for example you have a column operating at pressure
P1 and a pump is taking suctionfrom this column and the
control valve is at outlet of the pump, the pump is
discharging this material to a drum with certain pressure,
in this case you will take the shutoff pressure of the pump
as inlet pressure and minimum pressure that can be at the
drum. This will automatically result in an actuator sizing
and selection suitable for this service. I am not sure why
you mentioned bigger size actuator as actuator should
be "big enough" to handle the maximum delta P across the
control valve.
Is This Answer Correct ? | 3 Yes | 0 No |
for high pressure application we use the the bigger actuator is wrong concept, mostly in the early days days we used this kind of actuator, mostly used for diaphragm and piston type actuator , if u use diaphragm type then u need big cascade, for high pressure , but we should change the cascade for regular intervel. in our company we control the 220 kg/cm2 of pressure in the small actuator only, bigger actuator is disturbance only large space is needed and difficult to calibrate. thanks
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / rahul
when valve size is more,
mostely for control valve
Is This Answer Correct ? | 4 Yes | 3 No |
Answer / joby
if the valve is in higher size ,we have to go for higher
actuators for operating the valve.
FOR ESD VALVES
if the valve size is more than 18" mostly the suppliers
prefer hydraulic systems for operating the actuator
instead of air.The pressure required to operate the higher
size actuator will not be sufficient ,if you are using
plant air.
Is This Answer Correct ? | 1 Yes | 3 No |
Can anyone convert a 5/2 way or 3/2 way valve into an ISO valve?
steps for installing orifice plate?
0 Answers Bhushan Power Steel,
what is intrument termination what is commisioning
defffrence between instruments and instrumentation
flow transmitter range is 0 -500 mmwcc but the transmitter shows 12 ma for o mmwc instead of 4 ma ...how to solve this problem when we apply 375 mmwc it shows 16 ma
1)What is the suitable MOC for flow meters working at temperature between 200 - 250 cen. 2)In which application the mass flow meters are not advisable 3)Is it advisable to use radiation type or radar type instrument for non contact application
Can you explain drawbacks between P,I,D & PID controller
1 Answers JSW, Priya Cement, TPL,
What are all the type of vibration measurement measuring in turbine, what is the output of vibration sensor.
what is difference b/w Earth and ground
Describe how to use megger to measure the earth resistance and insulation resistance
Sir, I am working as a Instrument Engineer in Grasim Industries. Can any body provide question answer for interview purpose
what is cascade system ?