1. what is 3 point calibration & 5 point calibration?
2. If we use hart communicator to set the LRV & URV of a
smart transmitter, did we calibrate the transmitter? why?
3. Make a complet list if meterials needed to properly
connect a pressure gauge to a steam pipe using 1/2 inch
stainless steel tubing. The gauge connections is 1/2 inch
NPT-M and the steam pipe tap has a 1/2 inch female coupling,
compression fittings are use.
4. What are the tools in loop checking?
5. What would the ISA symbol of a square root extractor look
like?
6. What would you do to completely prepare for the
configuration?
7. What safety measures must you undertake when doing
configuration?
8. what are the two most commonly use programming languages
used when we configure a PLC?
9. What would you do if you accidentally skipped a step in
the configuration procedure?
10. How would you know if the configuration were sucessful?
11. Name at least 3 selections available when we configure
the burnout protection of a controller?
Answers were Sorted based on User's Feedback
1. 3 POINT CALIBRATION:
Calibration is generally adjusting the output
according to the input ranges.
3 point calibration means calibrating our instruments in 3
ranges- lower, higher and working range
5 POINT CALIBRATION:
in 5 point calibration are very precise calibration
in which we will calibrate our instruments at 5 different
levels to view the response.
0%, 25%, 50% 75%, 100% of the input ranges.
| Is This Answer Correct ? | 42 Yes | 3 No |
Answer / anand.r biocon limited
1. 3 & 5 point calibration
When calibrating the field instruments or device under test only 3 process reading compared with master instrument for 5 point calibration you should do comparison for 5 process values with master instrument
2. If we use hart communicator to set the LRV & URV of a
smart transmitter, did we calibrate the transmitter? why?
This is not calibration of transmitter we can say this is configuring BASIC parameters to the TX.
3. Make a complet list if meterials needed to properly
connect a pressure gauge to a steam pipe using 1/2 inch
stainless steel tubing. The gauge connections is 1/2 inch
NPT-M and the steam pipe tap has a 1/2 inch female coupling,
compression fittings are use.
By using sypon and 1/2 " nipple you can mount the pressure gauge on steam line if the line is vertical you should have 45 deg angle to the process line to reduce the pressure drop across the instrument.
8.. what are the two most commonly use programming languages
used when we configure a PLC?
Ladder logic
FBD- Functional block diagram
| Is This Answer Correct ? | 14 Yes | 0 No |
I need to know steps to Calibration Valve Guard......
Types of contol loops
a pressure transmitter with a range of 0 to 2500kpag has a specified accuracy of 0.5 % of span.It is to be calibrated using a comparison gauge to have an accuracy of 0.1% of span.The comparison gauge has a range of 0 to 3000kpag What is the accuracy ratio? is this ratio acceptable?
Can any body tell me about SAP MAINTINANCE MODULE. WHAT IS its function and application. And study material Source about it. I shall be very thankful.
whether radar level transmitter is applicable for the open tank
what is bms?
Determine the manipulated variable, controlled variable, and the measured variable given a description of various typical industrial processes.
what is "smart" in smart transmitter ?
how control valve works?
what barrier is used in process industry.
3 Answers ADMA OPCO, Process Industries,
what are level of automation & how these are distinguished ?
What is the function of SMPS
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)