1. what is 3 point calibration & 5 point calibration?
2. If we use hart communicator to set the LRV & URV of a
smart transmitter, did we calibrate the transmitter? why?
3. Make a complet list if meterials needed to properly
connect a pressure gauge to a steam pipe using 1/2 inch
stainless steel tubing. The gauge connections is 1/2 inch
NPT-M and the steam pipe tap has a 1/2 inch female coupling,
compression fittings are use.
4. What are the tools in loop checking?
5. What would the ISA symbol of a square root extractor look
like?
6. What would you do to completely prepare for the
configuration?
7. What safety measures must you undertake when doing
configuration?
8. what are the two most commonly use programming languages
used when we configure a PLC?
9. What would you do if you accidentally skipped a step in
the configuration procedure?
10. How would you know if the configuration were sucessful?
11. Name at least 3 selections available when we configure
the burnout protection of a controller?
Answers were Sorted based on User's Feedback
1. 3 POINT CALIBRATION:
Calibration is generally adjusting the output
according to the input ranges.
3 point calibration means calibrating our instruments in 3
ranges- lower, higher and working range
5 POINT CALIBRATION:
in 5 point calibration are very precise calibration
in which we will calibrate our instruments at 5 different
levels to view the response.
0%, 25%, 50% 75%, 100% of the input ranges.
Is This Answer Correct ? | 41 Yes | 3 No |
Answer / anand.r biocon limited
1. 3 & 5 point calibration
When calibrating the field instruments or device under test only 3 process reading compared with master instrument for 5 point calibration you should do comparison for 5 process values with master instrument
2. If we use hart communicator to set the LRV & URV of a
smart transmitter, did we calibrate the transmitter? why?
This is not calibration of transmitter we can say this is configuring BASIC parameters to the TX.
3. Make a complet list if meterials needed to properly
connect a pressure gauge to a steam pipe using 1/2 inch
stainless steel tubing. The gauge connections is 1/2 inch
NPT-M and the steam pipe tap has a 1/2 inch female coupling,
compression fittings are use.
By using sypon and 1/2 " nipple you can mount the pressure gauge on steam line if the line is vertical you should have 45 deg angle to the process line to reduce the pressure drop across the instrument.
8.. what are the two most commonly use programming languages
used when we configure a PLC?
Ladder logic
FBD- Functional block diagram
Is This Answer Correct ? | 14 Yes | 0 No |
Instrumentation symbols interpration, P& ID, Logic diagram analysis, Electrical drawing analysis.
Explain , how timer based pneumatic control valve will work ?
How can test or measure the probe and extension cable to identify if the problem at the probe or cable or at the driver it self? (pleast notify the measuring method)
defination of plc
how to calibrate pressure gauge(we can not able to fixed by pointer screw adjustment and pointer re fixing method)
what is mean by TDC-3000
Why we are using thrust bearing at turbine side?
what is the diffrence between LCN and UCN
What is meant by cold float of compressor shaft.
Example of dry contacts & wet contacts?
how flame detectors sense the flame.
I have installed a RTD whose length is 2250mm(RTD stem length), but it's upper 200 -250mm is out of the reactor, and this upper 200mm stem is surrounded by atmospheric temp. And the lower portion i.e. 2000mm is in contact with the measuring fluid, then does the final measuring temp. Gonna change as the upper 200mm RTD stem is out of reactor?
1 Answers Process Control Technologies,