Why we use 250 ohm resister in series
hart communicator?
Answers were Sorted based on User's Feedback
Answer / carl_ellis
HART communications requires a minimum of 230 ohms to
develop a sufficient voltage drop for the 1200 baud FSK HART
signal to be 'seen' by a HART communicator/modem.
The capacitance in a DC power supply acts as a low pass
filter which filters/strips off the FSK HART data.
Additional loop resistance is needed for HART communications
to take place.
If there is insufficient loop resistance, the HART
communicator/modem will fail to establish HART communications.
In normal field work, it is assumed that the analog input
to which the field instrument is wired will provide the
minimum resistance necessary. Most DCS analog inputs have
an input resistance of 250 ohms. But not all devices do.
And when bench testing/configuring HART instruments it is
not uncommon to connect a DC power supply, but not an analog
input. A HART communicator/modem will not work with just a
power supply powering a HART field instrument. The loop
requires a minimum of 230 ohms.
A 250 ohm resistor is commonly used for a bench
test/configuration because they're commonly available in the
instrument shop.
Carl Ellis
Measure First
Is This Answer Correct ? | 15 Yes | 1 No |
Answer / carl_ellis
Answer #2 is not correct because the HART communicator is
not an analog input, it does not use a 1-5Vdc signal. A
HART communicator gets and display a transmitter's primary
variable (or other variables) as a digital value; NOT as an
analog value, not as a 1-5Vdc signal developed across an
analog input's resistor. I repeat, HART communications is
NOT analog in nature, it is digital.
The HART Foundation specifies a minimum resistance of 230
ohms, as described in answer #1, in order to develop the
1200 baud HART signal, that rides on top of the DC loop
current signal.
It's easy to prove that 250 ohms (for 1-5Vdc) is not a
requirement for HART communications as a bench test.
Take a 2 wire loop powered HART transmitter, connect a DC
power supply and use a 330 ohm resistor in series in the
loop. The communicator will work and the primary process
variable will be correct. Then try a 470 ohm resistor.
The 470 ohm resistor will work, as well, and the primary
variable will be correct.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / mmuhammad habibullah
hart comunicator read 1 to 5 volt thats why we use 250ohm resistance
in control loop this resistnace already aad in loop
Is This Answer Correct ? | 4 Yes | 4 No |
what is a device net.
What is the difference between mmwc and mmwg?
I want to use 1/2 inch SS316 tube in my high pressure & temperature (64 kg/cm2 & 500 deg C)after condensate pot in pressure tranmistter. 1) Is it possible to use 1/2" ss316 tube in high pressure and temperature line. Tube manufacturer is local vendor. 2)On sarting the plant, We need to do system fluse that time condesate is not in the condesate pot so steam is directly contact with the tube. We have no exact calculation to know our tube is ok or nor at this time. pleae,reply.
PLS TELL ME THE FUNCTION OR PRINCIPLE OF CREEP RELEIF VALVE..
What is the SCAN time of a DCS/PLC? What is the typical value for scan time of DCS and PLC?
6 Answers Essar, Gasco, Siemens,
For crude application in floating roof tank, how to calibrate a DP Transmitter? How is the floating roof weight considered?
in plc source and sink meaning?
what is the main supply source for pressure transmitter?
what is the working principal of pribe
How many mode are in ups?
What types of thermocuple are mostly used?
what is unit and element of viberation?