Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why we use 250 ohm resister in series
hart communicator?

Answers were Sorted based on User's Feedback



Why we use 250 ohm resister in series hart communicator?..

Answer / carl_ellis

HART communications requires a minimum of 230 ohms to
develop a sufficient voltage drop for the 1200 baud FSK HART
signal to be 'seen' by a HART communicator/modem.

The capacitance in a DC power supply acts as a low pass
filter which filters/strips off the FSK HART data.
Additional loop resistance is needed for HART communications
to take place.

If there is insufficient loop resistance, the HART
communicator/modem will fail to establish HART communications.

In normal field work, it is assumed that the analog input
to which the field instrument is wired will provide the
minimum resistance necessary. Most DCS analog inputs have
an input resistance of 250 ohms. But not all devices do.

And when bench testing/configuring HART instruments it is
not uncommon to connect a DC power supply, but not an analog
input. A HART communicator/modem will not work with just a
power supply powering a HART field instrument. The loop
requires a minimum of 230 ohms.

A 250 ohm resistor is commonly used for a bench
test/configuration because they're commonly available in the
instrument shop.

Carl Ellis
Measure First

Is This Answer Correct ?    15 Yes 1 No

Why we use 250 ohm resister in series hart communicator?..

Answer / carl_ellis

Answer #2 is not correct because the HART communicator is
not an analog input, it does not use a 1-5Vdc signal. A
HART communicator gets and display a transmitter's primary
variable (or other variables) as a digital value; NOT as an
analog value, not as a 1-5Vdc signal developed across an
analog input's resistor. I repeat, HART communications is
NOT analog in nature, it is digital.

The HART Foundation specifies a minimum resistance of 230
ohms, as described in answer #1, in order to develop the
1200 baud HART signal, that rides on top of the DC loop
current signal.

It's easy to prove that 250 ohms (for 1-5Vdc) is not a
requirement for HART communications as a bench test.

Take a 2 wire loop powered HART transmitter, connect a DC
power supply and use a 330 ohm resistor in series in the
loop. The communicator will work and the primary process
variable will be correct. Then try a 470 ohm resistor.
The 470 ohm resistor will work, as well, and the primary
variable will be correct.

Is This Answer Correct ?    7 Yes 1 No

Why we use 250 ohm resister in series hart communicator?..

Answer / mmuhammad habibullah

hart comunicator read 1 to 5 volt thats why we use 250ohm resistance
in control loop this resistnace already aad in loop

Is This Answer Correct ?    4 Yes 4 No

Post New Answer

More Instrumentation Interview Questions

In most instances, Inertia processes are quite uncommon. Give an example of a combined Resistance and Capacitance situation.Describe an application, which according to your understanding of the subject matter, comprises of both Resistance and Capacitance effects.

0 Answers  


what is modbus?and why use it?what benifit

2 Answers  


How we are deciding while programming in pid controller , What we are using heating or cooling.

1 Answers  


If you SOURCE your outputs from a PLC, would you have to make the output HIGH, or LOW, in order to switch an output ON?

1 Answers  


What is profibus?

0 Answers  


when a magnet is heated?

0 Answers  


how to calibrate an error for pressure transmitter, make it easy to understand

2 Answers   Descon,


Is it possible to convert 4 wire transmitter to convert to 2 wire with additional relay.Please send detial with drawing,i will appreciate.

2 Answers  


HELLO FRIENDS plz tell me which are the PROTOCOLS we are using in PLC

3 Answers  


where proximity sensor installed on tank in loading arm application

0 Answers   Kalpena Industries,


what are the inputs (drawings) we need to prepare loop schematics??

1 Answers  


what is Analog input/output & Digital input/output,

2 Answers   Bapco Bahrain Petroleum Company,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)