why we take 4 to 20 mA as out put of every instrument like
pressure transmittre ?why we cant take 0 to 20mA as output?
Answers were Sorted based on User's Feedback
Answer / ritheesh kumar.p
why not take 0-20mA the reason for this is when 0 is
considered as minimum value then we will get 0 as output
when no signal is coming,when the instrument is not working
or there is any fault in it we get 0.inorder to ensure that
the instrument works we choose 4-20mA as standard output
value.4 corresponds to no signal from the instrument. 20mA
is the maximum value because below 20mA we will be able to
avoid schocks and short circuits
| Is This Answer Correct ? | 32 Yes | 2 No |
If we use 0 to 20ma, then 0 will be the minimum value and 20
will be maximum value.. In case if there is any problem in
the transmitter or in the cables, we get the value 0 but we
think it as a minimum value..we cant able to know that
there is problem in transmitter.. In order to overcome these
constraints, we went for LIVE ZERO concept as 4ma.
0 ma will be consider as DEAD ZERO.
| Is This Answer Correct ? | 24 Yes | 0 No |
Answer / haridass (kwt)
Including the above answers the reason for selection of 4-
20mA for the transmitter signal is, the LINEARITY.
From 0-4mA the signal will not be much linear (in graph we
can come to know),
from 20+ mA is the indication to conclude that the
measuring signal is above to its range or loop fault.
Only from 4-20 the mA signal is with perfect slope.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / guhan
AS PER OHMS LAW V=IR...WE R USING THE SIGNAL IN DCS 1 TO 5 VOLTAGE DC..SO WE KNOW THE RESISTANCE VALUE 250 OHMS...OK
VOLTAGE=1,2,3,4,5,V DC..RESISTANCE S 250 OHMS...FIRST STEP S VOL=1 V, R= 250, SO V=IR, 1=I*250,I=1VDC/250 OHMS...SO 1000MA/250 = 4 MA..( HERE 1 V DC S = 1000MA) ...SAME LIKE 2V S 8 MA,3 VOLS S 12 MA, 4 VOL 16 MA, 5 VOL 20 MA....THAT S WHY WE USE 4 TO 20 MA...
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / caarpus
ABOVE MENTION IS CORRECT ANSWER.AT SAME TIME NORMALLY WIRE
CAN GIVE 1 OR 2 mA WHEN CONNECT TO ANY SIGNALLING
CIRCUIT.WITHOUT ANY INPUT THEY WILL PRODUCE THE MILL VOLT IS
WRONG ONE.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / dinesh regar
when a 0-20mA used therefore insturment is not working i am
not indetified.there insturment are faulty ya supply
problem not sure.
therefore we used the 4-20ma .when supply will coming &
insturment not working.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is the main three inputs of DCS?
Give Detail information about plc,dcs,and scada system?
which type signal come control valve
what is the meaning of reverse action and forward action of control valve...
9 Answers Honeywell, Yokogawa,
what is the relation between flow and pressure.for example relationship between level and pressure is p = phg like that i want ans for this question.and also how to calculate orifice sizing and flow transmitter. pls some one ans for this questions.
what is the usage of QDV & VOLUME BOOSTER
How many are the types of instrument cables in terms of No. of pair.
1. Pl. send details about different types Gas Analyser, like Co2, O2, SOX/NOX, etc. with calibration procedure. 2. How to calibrate H2S gas detector in field?
why use MMWC unit
Why we are using 4-20 mA as Analog signal transmission other than 3 to 19 or 2 to 18 or 6 to 22 like wise ? What is the reason behind using 4 & 20 mA? Can anyone give proper technical reply ?
Explain Gas Turbine startup and shutdown sequences
Can anyone explain about ELectropneumatics principle?
1 Answers Forbes Marshall, Step,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)