which type signal come control valve
Answers were Sorted based on User's Feedback
Answer / mani
from dcs we give 4 to 20 ma to i/p converter. from i/p we give the 3 to 15 psi pnematic signal given to cv.
Is This Answer Correct ? | 23 Yes | 0 No |
Answer / bert
The type of signal going to control valve is either a
pneumatic or electronic signal. For a pneumatic signal its
3 to 15 PSI or 0.2 to 1.0 kg/cm2. For electronic signal its
4 to 20 mA.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / abdulbasit137@hotmail.com
two types signal come control valve 1.pneumatic signal 3 to
15 psi (2)electronic analog signal 4 to 2o milla amp
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / parag pathak
Control Valve is final control element of clost loop. So
signal coming to control valve will be in pneumatic form
but depends on size of Valve. It can be 3-15 PSI or 0.2 -
1kg/cm2 but it is not fixed. There is one instrument called
Positioner which will convert 3-15 PSI signal to desired
siganl depending on Control valve.
For any Contol Valve signal will come from Control room in
the form of 4-20 mA. this 4-20 mA signal was converted to 3-
15 PSI signal by instrument called I/P converter. This
siganl will go to positioner and the positioner o/p is
given to valve actuator to get desired opening and closing.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rajkumar.diice
The signal type depends on
the location of control valve!
For explosive hazard area the
signal be pneumatic and be 3
to 15psi! The converters be
mounted in somewhat
distanted area! For all control
valves the signal be 4to 20mA
over 1to 5 volts from a
control room! For inbuild
current to pressure
converters control valves the
signal be 4to20mA over 1to
5volts dc
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / susant
from dcs analog output signal 4-20ma dc provided to control
valve
Is This Answer Correct ? | 3 Yes | 6 No |
What is the difference between HMI and MMI?
what is thermopile?
What is the constant voltage unit?
Any Transmitter Range (Span value) start from 2?
What is the reason for not giving very High Proportional Gain Kp in PID Controller?
what is the diffrence between mmwc and kg/cm2 for pressure measurment when we are using mmwc and when kg/cm2 and why????? ?? what is the reason
19 Answers Ecoboard, Jindal, Sepco,
What is minimum distance between three thermocouples (2oo3) mounted on same pipe line (20")? Technically accepted by stright line mounted or circler mounted?
wht is Zero Elevation and Zero Suppression?
Hi, I am Newely Joined in Construction company instrument engineer? Any one can Plz tell me How can I advanced preparation for Releated Engineering and construction Documents?
HOW TO CHOOSE FREAQUENCY IN FMCW TYPE RADAR INSTRUMENTS. DESIGN BASIS OR DESIGN CALCULATONS ?
How to measure density of oil in your kitchen. i.e indirectly to verify the quality of oil using min. gadgets available in the kitchen/house.
Sitrans LR460 Radar level transmitter getting level out or disturbed level during moisture present in the material ie coal in the pccb bunker in CHP.Any suggestions for this problem...????