which type signal come control valve
Answers were Sorted based on User's Feedback
Answer / mani
from dcs we give 4 to 20 ma to i/p converter. from i/p we give the 3 to 15 psi pnematic signal given to cv.
| Is This Answer Correct ? | 23 Yes | 0 No |
Answer / bert
The type of signal going to control valve is either a
pneumatic or electronic signal. For a pneumatic signal its
3 to 15 PSI or 0.2 to 1.0 kg/cm2. For electronic signal its
4 to 20 mA.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / abdulbasit137@hotmail.com
two types signal come control valve 1.pneumatic signal 3 to
15 psi (2)electronic analog signal 4 to 2o milla amp
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / parag pathak
Control Valve is final control element of clost loop. So
signal coming to control valve will be in pneumatic form
but depends on size of Valve. It can be 3-15 PSI or 0.2 -
1kg/cm2 but it is not fixed. There is one instrument called
Positioner which will convert 3-15 PSI signal to desired
siganl depending on Control valve.
For any Contol Valve signal will come from Control room in
the form of 4-20 mA. this 4-20 mA signal was converted to 3-
15 PSI signal by instrument called I/P converter. This
siganl will go to positioner and the positioner o/p is
given to valve actuator to get desired opening and closing.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rajkumar.diice
The signal type depends on
the location of control valve!
For explosive hazard area the
signal be pneumatic and be 3
to 15psi! The converters be
mounted in somewhat
distanted area! For all control
valves the signal be 4to 20mA
over 1to 5 volts from a
control room! For inbuild
current to pressure
converters control valves the
signal be 4to20mA over 1to
5volts dc
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / susant
from dcs analog output signal 4-20ma dc provided to control
valve
| Is This Answer Correct ? | 3 Yes | 6 No |
what is the use of glycol filling in seal pot (or) condensate pot in instrument impluse line?
Differentiate between PLC, SCADA and DCS systems
1 Answers Mumias Sugar, SRF, Trimula Industries,
what is the input of conductivity sensor and meter during the calibration time and what is the output?
how will you segregate the alarm levels in alarm management system during factory Acceptance Test
Please send the all question with answer related for interview.
Identify and use the ANSI/ISA-S5.1 consensus industrial standard process symbols.
how to use one 4-20mA signal for two indicater or controller & give necessary precaution.
Can a pneumatic control valve work without positioner?
Why Pressure Transmitter is NOT installed before up-stream of an ORIFICE PLATE? in a flow measurement.
how to calibrate steam control valve in steam turbine
what are the problem's will accure in dcs or plc hadware and what are the solution for it?
can a control valve works without positioner?why need tunning of c/v?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)