what is the meaning of reverse action and forward action of
control valve...
Answers were Sorted based on User's Feedback
HhHHH
Hi my dear friend the valve action depends on the
service.If the PV increasing the valve opening also
increasing, the action is direct action.If the PV
increasing, the valve opening decreasing i.e reverse action.
For example if you used one valve to fill the tank.if the
PV increasing, you have to close the valve.i.e your valve
action is reverse to the PV value.
If you used valve in discharge line of the tank.If the PV
increasing, you have to open the valve. i.e your valve
action is direct to the PV value.
SP-PV=Error=Reverse action
PV-SP=Error=direct action
Is This Answer Correct ? | 33 Yes | 6 No |
Answer / hvkkumar,mtech instrumentation
for pressure increases the % of valve opening increase in
direct action .but in case of reverse actoin pressure
increases the % of valve opening decrease.
Is This Answer Correct ? | 27 Yes | 11 No |
Answer / alexpandian
Hi,
We r using direct&reverse actuion in many places:
Control vlv- By giving air, if the stem of actuator moves
down then its dircet acting actutor & if stem moves up then
it is reverse acting.
Controller-
DIRECT: If the PV is less than SV then MV will
decrease.Mainly using in vent valve application.
REVERSE; If the PV is less than SV then MV will
increase.using in normal control loops.
PV-process value SV-set value MV-manipulated value
Is This Answer Correct ? | 12 Yes | 3 No |
Answer / saravanan
Direct acting valve
Air to close -- Spring to open --- Failed Open (FO)
(increasing air pressure pushes down diaphragm and extends
actuator stem)
Reverse acting valve
Air to open -- Spring to close --- Failed Close (FC)
(increasing air pressure pushes up diaphragm and retracts
actuator stem)
Is This Answer Correct ? | 10 Yes | 2 No |
Answer / j arumugam
if control variable(CV) INCREASES process variable
INCREASES is called Direct acting (Gain < 0)
if control variable(CV) INCREASES process variable
DECREASES is called Reverse acting (Gain > 0)
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / naganaresh katta
If PV>SV then MV Increases in direct action
IF PV<SV then MV Decreases in reverse action.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / www.islamqa.com
For linear motion valves
Direct acting valve:
====================
valve opens when stem is drawn out of the body
Reverse acting valve:
=====================
valve closes when stem in pushed into the body
reference:
Lessons in industrial instrumentation - version 4 - page:713
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
CELL.: 00 2 0121367310
Is This Answer Correct ? | 6 Yes | 9 No |
Answer / vinayak
Hi ...
Revese action normally used in AIR Fail to Close valve.
Direct acttion normally used for Fail Open valve.
It is very important to define reverse or direct action as
per process requirement.
DIRECT ACTION :
20 MA DC = 0 % VALVE CLOSE
16 MA DC = 25 % VALVE OPEN
12 MA DC = 50 % VALVE OPEN
8 MA DC = 75 % VALVE OPEN
4 MA DC = 100 % VALVE OPEN
REVERSE ACTION :
4 MA DC = 0 % VALVE CLOSE
8 MA DC = 25 % VALVE OPEN
12 MA DC = 50 % VALVE OPEN
16 MA DC = 75 % VALVE OPEN
20 MA DC = 100 % VALVE OPEN
Is This Answer Correct ? | 8 Yes | 11 No |
REVERSE ACTION CV = AIR TO CLOSE = AIR FAIL TO OPEN
DIRECT ACTION CV= AIR TO OPEN =AIR AIL TO CLOSE
Is This Answer Correct ? | 20 Yes | 31 No |
Emergency Shutdown Systems/ Plant Shutdown System.
how can leve transmetter calibate in feild .and also put cv and flow plz .....
A pressure differential gauge type of instrument has a manifold with 2 isolation valves (hp and lp),2 vents(1 each for hp and lp) and 1 equalizing valve. Determine the position of each valve(either fully closed or fully open) when troboulshooting to: 1. zero the transmitter. 2. determine if there is a block in the impulse line. 3. determine if the gauge is functioning properly. The process fluid is water.
in control valve is constructed as per API 6D or API 6A, then which standard is used for fire testing of valve?.
Explain the usage of the PLC system?
how to tune the closed pid loop?
what are the documents(Construction point of view for a process plant) submitted by contactor initially entering in to new site for client?
What is 1:1 redundancy ?
how to work gas chromatography explain principle ?
If a flow transmitter (magnetic type FT) that can measure flow and temperature, then why in some industries people use flow transmitter and temperature transmitter in the same line 1 after another? Even after 1 single flow FT is capable of measuring flow as well as temperature.
1 Answers Process Control Technologies,
Why rtd out put is ohm how create the ohm
If a transmitter is installed 10 m below its tapping point how much pressure exerted if fluid is water?