what is the meaning of reverse action and forward action of
control valve...
Answers were Sorted based on User's Feedback
HhHHH
Hi my dear friend the valve action depends on the
service.If the PV increasing the valve opening also
increasing, the action is direct action.If the PV
increasing, the valve opening decreasing i.e reverse action.
For example if you used one valve to fill the tank.if the
PV increasing, you have to close the valve.i.e your valve
action is reverse to the PV value.
If you used valve in discharge line of the tank.If the PV
increasing, you have to open the valve. i.e your valve
action is direct to the PV value.
SP-PV=Error=Reverse action
PV-SP=Error=direct action
| Is This Answer Correct ? | 33 Yes | 6 No |
Answer / hvkkumar,mtech instrumentation
for pressure increases the % of valve opening increase in
direct action .but in case of reverse actoin pressure
increases the % of valve opening decrease.
| Is This Answer Correct ? | 27 Yes | 11 No |
Answer / alexpandian
Hi,
We r using direct&reverse actuion in many places:
Control vlv- By giving air, if the stem of actuator moves
down then its dircet acting actutor & if stem moves up then
it is reverse acting.
Controller-
DIRECT: If the PV is less than SV then MV will
decrease.Mainly using in vent valve application.
REVERSE; If the PV is less than SV then MV will
increase.using in normal control loops.
PV-process value SV-set value MV-manipulated value
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / saravanan
Direct acting valve
Air to close -- Spring to open --- Failed Open (FO)
(increasing air pressure pushes down diaphragm and extends
actuator stem)
Reverse acting valve
Air to open -- Spring to close --- Failed Close (FC)
(increasing air pressure pushes up diaphragm and retracts
actuator stem)
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / j arumugam
if control variable(CV) INCREASES process variable
INCREASES is called Direct acting (Gain < 0)
if control variable(CV) INCREASES process variable
DECREASES is called Reverse acting (Gain > 0)
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / naganaresh katta
If PV>SV then MV Increases in direct action
IF PV<SV then MV Decreases in reverse action.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / www.islamqa.com
For linear motion valves
Direct acting valve:
====================
valve opens when stem is drawn out of the body
Reverse acting valve:
=====================
valve closes when stem in pushed into the body
reference:
Lessons in industrial instrumentation - version 4 - page:713
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
CELL.: 00 2 0121367310
| Is This Answer Correct ? | 6 Yes | 9 No |
Answer / vinayak
Hi ...
Revese action normally used in AIR Fail to Close valve.
Direct acttion normally used for Fail Open valve.
It is very important to define reverse or direct action as
per process requirement.
DIRECT ACTION :
20 MA DC = 0 % VALVE CLOSE
16 MA DC = 25 % VALVE OPEN
12 MA DC = 50 % VALVE OPEN
8 MA DC = 75 % VALVE OPEN
4 MA DC = 100 % VALVE OPEN
REVERSE ACTION :
4 MA DC = 0 % VALVE CLOSE
8 MA DC = 25 % VALVE OPEN
12 MA DC = 50 % VALVE OPEN
16 MA DC = 75 % VALVE OPEN
20 MA DC = 100 % VALVE OPEN
| Is This Answer Correct ? | 8 Yes | 11 No |
REVERSE ACTION CV = AIR TO CLOSE = AIR FAIL TO OPEN
DIRECT ACTION CV= AIR TO OPEN =AIR AIL TO CLOSE
| Is This Answer Correct ? | 20 Yes | 31 No |
which processor is used in dcs.
0 Answers ABB, Wave Distillery,
what is weighfeeder
How to calibrate the control valve.
is motorized valve closed when power shutoff?
I have a problem with a valve (air to close). When it is fully closed and try to open 1% it doesn't responce till 3% open suddenly more than 3% then back to 3%. I tried to tune positioner then removed it, the problem still exist. Any idea
What is the difference between a PLC (Programmable logic controller) and DCS (distributed control system)?
why most of the DP transmitters using maximum range as 0-2500mmwc?why not 1000 2000 3000 4000mmwc
hi... i'm about to learn siemens plc i came across following question in my mind ... plr ans 1. hw motor operated by plc 2. hw drive operated by plc explain dis by both ladder logic diagram and hardware config , connection
what is difference b/w Earth and ground
what is the advantage by using PID controller than P& PID?
how to install Differential pressure transmitter in gas line.i need transmitter down side.
Sir,I am going to sit for IOCL written test exam. recently.Can anyone tell me the name of 'Objective type Question Book on Instrumentation Engineering ' which will help me. Pl. mail to bidyut_71@rediffmail.com / bidyut.saha2008@indiatimes.com / bidyut.saha09@yahoo.in
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)