the destination of any signal will be a Controller.
Take DCS, its input supply will be 1-5V.
from instruments, across a 250ohm resistor, the value will
reach DCS as desired 1-5V.
expl:
say 4ma is the output of transmitter.
V=IR,
V=4ma * 250 ohm
V= 1V,
say 20ma,
V=20ma*250ohm
V=5V.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / dhanabalan
It is where the linearity is maintained (4-20 mA Signal).
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / t.naveen babu
The reasons for the 4-20 mA standard (and, before it, the
10-50 mA standard) have a lot to do with the original 3-15
psi/20-100 kPa air
signal. The origin of the suppressed or "live" zero in the
pneumatic system was two-fold - if you want to reduce a
passive pneumatic signal quickly, you need to maintain some
differential between the pressure and the "sink" - in this
case, atmospheric air. The basic characteristic of a
flapper-nozzle assembly also has a bit to do with it -
the "linear" range of the flapper pressure is about 3 - 15
psi for a 20 psi supply. Next question - why a 20psi
supply? Anyone else remember 6-30 psi equipment for
final actuators needing a bit more grunt??
The original electronic instruments were direct imitations
of the pneumatic systems with bellows replaced by magnet-
coil assemblies. The first I came across were used in a
geothermal power project (1958 vintage)where the pressure
at the power station was controlled by manipulating valves
in the steam field 1 1/2 miles or so away. The flapper-
nozzle was replaced by a
contact moving between positive and negative terminals - I
guess a bity of mains hum in the amplifier kept it
jittering. In the mid-70's Foxboro produced a range of
pressure transmitters using the magnetic principle which
used the same basic mechanism as their pneumatic equipment -
but the size of the coils made the assemblies a lot
bigger ...
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / abhishek
this 3-15 psi later used in electronic signal as 4-20mA. 4mA
used as live Zero , & 20mA is current so
20mA*24V=480mWatt. this power if we increase any signal
wire can cause such type of arc that can cause Fire.
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / ahmad
1- Any electronic circuit having its error, here Ico=3.85 ma(aprox=4 ma). that is why we do start from 4 ma.
2- it is also convertable to 1-5 volt, with precision resistance of 250 ohms.
| Is This Answer Correct ? | 0 Yes | 0 No |
what the differant between Wet Leg /Dry Leg
How to convert 0-2500mmH2o into kg/hr? Or how to convert mmH2O into kg/hr,t/hr etc
How to find the range of DP cell Transmitter for measurement of level in closed vessel.
I want to know if flowrate increases in 16' pipe line what will happen to upstream pressure and why?
We have a Yokogawa Micro-XL DCS, which is having around 300 I/O, but whenever there is any wire gets grounded in field, the 24v supply to all loops gets dipped & all the indications at DCS goes to IOP(shows input open), at present we have fixed 500mA fuses in all the lines but which does not working. Does it required to replace with lower amps fuse, then how much or is there any other solution for this.
How to calibrate Field bus transmitter? procedure ?
How can corrosion alter the accuracy and precision of a C- Bourdon tube pressure gauge?
how to wire from pressure transmitter to marshalling panel and panel to controller and controller to dcs plz give the answer with example .
What is the purpose of LO overhead tank in turbines.
How can I map a tank? Tank 15m h and 42m dia. we just fixed radar type lit. its reading shows over range. Now its required mapping ?
whatis range of marcury filled tempereture gague
Displace type LT to be calibrated in workshop, wt. 40, dia- 60 mm, density- 0.8kg/cm3.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)