What should be the BDV value of a new transformer oil
Answers were Sorted based on User's Feedback
Answer / pradyumna chandra panda
For 11kv suppy it is 40kv/2mm at normal temprature is ok. As per my experience it is reach upto 125kv/2mm at 40°c after filtration but we keep it 60kv/2mm NB-Below 24kv/2mm is rejected oil.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / koti
As per IS : 335-1993, it is 30 KV(unfiltered)
and 60 KV(After filtration).
| Is This Answer Correct ? | 2 Yes | 0 No |
What is the general power factor & min. power rating of TV,LCD type TV, CRt type TV, Scanner, printer?
what is power factor in ac ckt ?
what is 6 pulse and 12 pulse inverter? Explain brifly
What is the important parts of SF6?
Why do we perform an open-circuit test and short-circuit test on the transformer?
Why electrical engineer use Cu Strip for transformer neutral why not GI Strip? What if we use GI instead of Cu does it affects the transformer performance.
Full form of bdv test?
what will happen if there is a voltage leakage or current leakage in an electrical train
how to calculate cable bending angle in a trench?
What are safety features considered for Lifts during emergency?
what is the difference in using the 125% and the 250% factor of safety in calculating circuit breakers capacity for motors,which is more reliable to use the 125% or 250%??
What is the difference between bushing and insulators.? what is the creepage distance?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)