can any one tell me the formula for calculating the power
and unit consumpetion
Answers were Sorted based on User's Feedback
Answer / mubashar ali
total KW * total runing Hours= unit
for example
5 lamp 100 watt each onload for 6 hour
AC 3000W onload for 3 hour
Motor 5HP (5*746=3730W) onload for 2 hour
than
500/1000 * 6= 3
3000/1000 * 3= 9
3730/1000 * 2= 7.46
total unit = 19.46 * Rs.
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / ramesh gaur
one unit is equal to one kwh(1000w per hour)
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / vinothbabu.k
P=(1.732*VOLTAGE*AMPS)/1000,
FOR UNIT CONSUPTION:
KWATTS*HOURS=UNIT-ITS FOR INDUCTIVE LOAD,
FOR RESISTIVE LOAD THE ABOVE IS CORRECT,LAMP HEATER IS
RESISTIVE LOAD,
IT DEPANDS ON TYPE OF LOAD.
AND FOR CAPACITIVE & INDUCTIVE LOAD NO OF WORKING HOURS
WILL BE VARRY,FOR EXAMPLE TAKE FRIDGE WAS WORKING FOR 2
HOUR IT TAKE 750W MEANS WE SHOULD NOT
CALCULATE .750*2=1.5KWHR/UNIT,FRIDGE IS A CAPACITIVE LOAD
IT WILL ON OPPROXIMATELY 35 MIN FOR EVERY PER HOUR SO WE
SHOULT TAKE FOR 2 HRS IT WILL ON 1.05HRS FOR 2 HRS,
SO 750*1.05=0.787 UNIT
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mad sarfaraj
power(p)=dw/dt(this is the basic formula 4 power)
and it's S.I. unit is joule/second or watt.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / balaji
Power=i^2*R(resistor multiplied with square of current)
Is This Answer Correct ? | 0 Yes | 0 No |
where any change in supply line due to the incipient faults in three phase induction motor
WHY WE CAN GENERATE POWER IN 3PHASE MODE ONLY NOT IN 4 OR 5PHASE
Load transfer in 11kv double busbar switchgear - operation.
Natural frequency of a system gives... 1) nature of transient 2) overshoot 3) oscillations 4) speed of response
Size of the power cable like 1.5,2.5,4 sq.mm which area calculated from whick area or how specified the size?
How to find Cable size? Caterpillar generator produce (Two generators) 127*2=254 amp at 11 kv . What would be the cable size (XLPE) to supply 256 amp at 11 kv? Air or surrounding Temperature is 32 degree C. Cable will go under ground at 2.5 feet depth. Group Rating Factors is 3 cables. Clearance between cables is 7 cm. Soil Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2 K.m/W I would like to use 3 separate single core instead of using 3 core cable. Some says I should use three separate single core 120RM cables. Some says 70RM .some says 95. I m totally confused. Is there ant specific rule to determine cable size? What would be the LT cable size to flow 500 Amp current? Ifte My e mail address is ifte13@yahoo.com Anyone please send me the answer to my e mail address, i will be very glad.
Double Busbar Scheme for outdoor switch yard system (132kv) step up power plant Hi friends 1. in this system both busbars energized all the time. 2. what is the meaning of main BB and transfer BB, 3. step up transformer connect main bus bar all the time or both BB connected through DS switch . 4.bus sectionalization means ? thank you.
Why 60Hz frequency is used in America what are all the benifits?
How the PF control while running DG set with load
what is the std. earthing resistance for 440V system or m/c, 33000/440 Volt substation? What is the std.?
Explain the process of commutation in a dc machine.
suppose MCC (Motor control center)panel work on field the relay on this damage or not work and earth fault occurs in this and no indication in relay panel given below. than MCB trip or not and what effect the panel how find relay will damage or not work.