Why the power factor of the alternator in power plant is kept .8 lagging. Can't we maintain it at 1.
Answers were Sorted based on User's Feedback
Answer / sidharth
The pf is maintained at 0.8 because generator has to supply reactive power to the connected transmission line if pf is maintained at 1 then the distribution transformers would not be energized as it requires some reactive power for its core to produce magnetic flux.Also the due to line capacitance the receiving end voltages will get higher than the sending end voltages. For more reference consult reactive power control topic.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / lokeshraj
We use the capacitor bank to maintain the power factor at .8 when it goes below this value, capacitor compensate the reactive power needed, and improves the power factor. Why don't we use this much value of capacitor that the pf becomes unity. Because if we use the capacitor at the load end and makes the pf unity the losses in the line will be decreased and the load capacity of the line will be increased.
Only in unloaded or lightly loaded condition the receiving end voltage of the line becomes higher than the sending end voltage.
| Is This Answer Correct ? | 1 Yes | 0 No |
For transmitting power with low value of ferrenty effect .power generating station pf should kept 0.85 -0.80
| Is This Answer Correct ? | 0 Yes | 0 No |
What is the In door to Out door Sub Station.
For testing 33kv cable hipot testing. How much kv we have to Apply .Give in details.
how to calculate generator capacity?(kva)
What shall be minimum thickness of firewall in between two transformers and which code specifies it ?
How will you justify IR value and Charging voltage of any motor,transformer and Cables.......???? . . . . . . . . Plz tell me any body Baljeet Singh, engineer_89@refiff.com
what is fuction static switch in ups and tell me use parts name and fucion
To measure insulation resistance of 11KV cable between core & armour, what should be the test voltage & duration?
what is the meaning of electrical maintenance?
3 Answers GE Healthcare, MAHINDRA,
what happens if dc supply is given to the transformer?
What is DC series motor?
how do u gauge the size of the cable ?for eg. consider a 300 sqmm L.T Cable.How do u determine the size of the cable seeing it pratically?
0 Answers Bhel, Jai Balaji, Rashmi Group,
How to calculate the electrical load for a standard telecom BTS shelter and choose the DG set capacity for the same load?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)