how to calculate generator capacity?(kva)
Answers were Sorted based on User's Feedback
Answer / aamod tripathi
first the total load to be catered is taken in kw
the load factor
diversity factor
efficiency of the generator
power factor is to be known
then calculate the kva rating of the generator by
kva= (kw*load factor)/(power factor* efficiency* diversity
factor)
AFTER THIS CALCULATION A CONTINGENCY FACTOR OF 10-20%
Is This Answer Correct ? | 28 Yes | 5 No |
Answer / farrukhwaheed
kw*load factor)/(power factor* efficiency* diversity
factor)
Is This Answer Correct ? | 9 Yes | 7 No |