how to calculate generator capacity?(kva)
Answers were Sorted based on User's Feedback
Answer / aamod tripathi
first the total load to be catered is taken in kw
the load factor
diversity factor
efficiency of the generator
power factor is to be known
then calculate the kva rating of the generator by
kva= (kw*load factor)/(power factor* efficiency* diversity
factor)
AFTER THIS CALCULATION A CONTINGENCY FACTOR OF 10-20%
| Is This Answer Correct ? | 28 Yes | 5 No |
Answer / farrukhwaheed
kw*load factor)/(power factor* efficiency* diversity
factor)
| Is This Answer Correct ? | 9 Yes | 7 No |
Which standard i will refer for size of earthing conductor for equipment? (Eg:415V Switchgear, MCC, DB shall be 50x6mm GI flat)
What is the purpose of a process loop? What is the controllers responsibily?
could mail me the question papers for the test.
How halogen & merquery lamp works.
wat is the difference between BE &BTECH.
plz tell me Motor IP formula
how to fit 3 HP crompton gear motor with conveyor with the use of staring delta starter or ordinary starter?
explain why the armature voltage changes when the field rheostat is varied in self excited DC generator
What is the function of a pressure Switch in a Substation?
how do we select a copper power cable for a 10 HP, 1440 rpm, 440V, 3 phase AC motor?
What is pi controller?
WHAT IS MVA RATING OF KOTHAGUDAM THERMAL STATION POWER TRANSFORMER?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)