what happens if dc supply is given to the transformer?
Answers were Sorted based on User's Feedback
Answer / suresh
IF DC APPLIED ,as BACK EMF IS 0''NO INDUCED EMF IN
SECONDARY WDNG??.WHOLE SUPPLY APPLIED TO PRIMARY WDG.&
PRIMARY WDG BURNT OUT
Is This Answer Correct ? | 29 Yes | 4 No |
Answer / kishore kumar
T/f must not be connected to dc. bcoz if the PW of a t/fis
connected to dc supply mains, the flux produced will not
vary but remain constant & therefore no emf will be induced
in the SW except at the moment of switching on. thus the
t/f can not be used for raising or lowering the dc voltage
$ also no back induced emf in PW and therfore a heavy
current will be drawn from the supply mains whcih may
result in the burning out of the PW
Is This Answer Correct ? | 10 Yes | 3 No |
Answer / mittal
Nothing noticeable. DC power is not transmitted between the
coils of a transformer. There would be no current on the
other side of the transformer, unless the power of the
source was constantly modulated. bescause flux does not
change its state.
after some time excessive heat is produced and winding may
burn
Is This Answer Correct ? | 11 Yes | 5 No |
Answer / k.prakashchandra
as dc supply does not produce back emf ,the current wii be
equal to volage/ dc resistance which is very low
Is This Answer Correct ? | 15 Yes | 10 No |
Answer / vinod g
IF DC APPLIED ,only winding resistance coming across the
supply,remeber big transformer has ohmic value less than
one, so definetly the PRIMARY WDG will BURN OUT.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / b.sivayya
transformer is not connected to dc.in dc there is no
frequeny.there no changes in frequency and dc is given to
primary there flux is produced but these flux is not
change.so there is no back emf so the secondary current is
equal to primary current so large current is flows through
the windings .so the winding is burn..
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / raul
if a dc supply is applied across a transformer, there will
b no transfer of power from primary to secondary through d
core bcoz by applying dc there will no change in flux and
hence no emf produced in d primary by self-induction, no
magnetisation of the core and hence no emf in d secondary
by mutual induction.......so overall there will be no
transformation of energy from primary to secondary
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / abhinav dhiman
because flux will not change and hence e.m.f will not
induced,which opposes the applied voltage,and max. current
will flow and hence binding will burn
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / siva
dc power is not transmitted b/w the coils of the transfrmr there would be no current on the side of the transformer unless the power of the source
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shalini m
IF DC supply is given to transformer, there will be no
change in flux and there would be more leakage current in
the primary windings and hence the windings of the
transformers may burn out
Is This Answer Correct ? | 1 Yes | 3 No |
How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size of cable is used for this motor.
my field of interest is T&D. plz tell something about that.
If you see the HRC fuse name plate. Its shown ampere rating shown which is in many KA (like 80KA and so on). any body explain what is meaning of this value?
If we have 630kva step down transformer to operation 3 phase motor 150 kva which size of cable is used? at circuit breaker to 3 phase motor or to electrical board
can we run AC & DC cables in same tray
Dear All kindly let me know that I know about the DG Rating for Example 150 KVA,Now how i will know that how much Ampher load it can offoard.
How can we design MEP services for Commercial Building in area about 22 Acres of land?
I have two AC generators, the first rated 2680KVA for 380V/4345A/pf:0.7 and the second rated 3461KVA for 5500V/363A/pf:0.8. I want to parallel the two generator to a bus. The second generator passes through a transformer to down the voltage to 380V and a part of its power goes to another bus so that it's only a part of the total power of the second generator taht goes to the considered bus. I have two Basler DECS100 AVR regulator. How can I make the synchronization ? What others equipments must have ?
Explain the different methods used in the choice of rotor slots for reduction of harmonic torques in an induction motor.
why we connect dg neutral with ground?
How we calculate the average power factor if the one phase is lag and another one is in lead?
What are IP protections used for electrical panels, JB, equipments installed in explosive zones like Petrochemicals, Oil & gas