To measure insulation resistance of 11KV cable between core
& armour, what should be the test voltage & duration?
Answers were Sorted based on User's Feedback
Answer / v.senthilkumar
To measure insulation resistance of 11KV cable between core
& armour, we can use 5kv megger for 60 Sec.
| Is This Answer Correct ? | 22 Yes | 2 No |
Answer / thowsif_emerson_csm team
To measure insulation resistance of 11KV cable between core
& armour,
Test voltage is 28KV(RMS Value)
Duration is 300 Sec...
| Is This Answer Correct ? | 10 Yes | 6 No |
11 kv cable resistance we can measure
Test voltage is 10 kv to 20 kv (RMS Value)
And time is depend on which voltage you are selected.
if 10 kv then time should be 120 sec..........
And resistance valu also going opposit to voltage..
if suppose volt is 10 kv then megger valu 2gomh, And if volt
20 kv and valu 1gomh then cable is ok both are same valu....
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / sujeet pandey
To measure the insulation resistance of 11kv cable, we need
to keep Megger test voltage at 1kv and take 2 readings; one
at a interval of 15 sec and other at an interval of 1 min.
This will give Absorption Factor which is equal to ratio of
resistance at 1 min to the resistance at 15 sec. If the A.F.
is less than 1.2(a/c to Indian Standards) then the
insulation is not good and we must take the remedy action.
| Is This Answer Correct ? | 0 Yes | 1 No |
What do you mean by PT-100?
Is CBCT protect human life? If yes than how?
What is the Current equation in series RLC circuits.
How much depth we will take in 33kv sub station and why.
what is full wave bridge?
in 5 mva transformer 33/11 kv s/s what rating of capacitor bank is required & what is the fourmula for rating
i applied for the ap transco please forward the freqventley asked QA
dielectric strength of vacuum is greater than SF6 but for 132Kv uses sf6 breaker & for 33kV uses vaccum breaker why such a contradiction?
2 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
What are the difference between C-Curve and D-Curve for MCB's.
17 Answers ABB, DLF, Essar, GK companies, Nissi Engineering Solution,
why connecting surge unit in contactor coil
HAI,HOW TO SET THERMAL OVERLOAD RELAY FOR DOL STATRTER FEEDER AT START AND RUNNING?
how instantanious short circuit current is calculated ? its formula.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)