Answer / ashish negi
the above calculation is correct but if we have to give our
demanded load to electricity dept. than the load should be
greater than the load as on starting motors , motors take 2-
3 times the full load cureent and at that time your MDI
(maximum demand index)will go beyond the calculated load.
so in that case your have to pay the penalty. so your
demanded load should be between 2500-3000 KVA.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rakesh maharjan
Remember the formula
KW=1.732 x V xI x PF
or
KW= KVA x PF, where PF = 0.8
connected load KW= Full load kw x 80%
Here in your case, connected load KW= 15000kw
so full load KW= 15000/80%=18750 KW
KVA= KW/.8
KVA=18750/.8=23437 KVA, this is the demand sanction.
I am junior Engineer.
Please verify by senior designer also.
| Is This Answer Correct ? | 5 Yes | 3 No |
Only the connected is mentioned and not the peak load.
Maximum demand is registered only if that apparent load
lingers for more than 15 to 30 minutes (as set).You have to
consider load factor(?) also .Apply for 12000 KVA MD
initially and you can apply for higher ,later.Once you get
the MD sanctioned, you can not get it reduced during the
agreement period.
| Is This Answer Correct ? | 1 Yes | 0 No |
Dear sir, please tell me how many day use CTPT transformer
1 Answers Daya Engineering Works,
whats was the problem if neutral and earth got 2volt from the ups output
what is pressure relief valve in D.G ?state its function?
-What is leakage current . how much leakage current is allowed.
why transfromer rating gives in MVA Or KVA? Why not in MW or KW?
How can I calculate the Mega watts required to run a plant having many electric motors and other electrical components.
Why only 1ph,2ph,3ph supplies are universally used?? Why not 4ph or 5ph??
How to calculate size of HT breaker with the help of Amp (current)? Please provide answers with examples.
How much no load current of synchronous motor
0 Answers Nirma, Sulphur Mills,
Seamless tubes are made by?
How to know about the rating(voltage and other) of induction motor if its name plate is missing at the manufacturing site.
why ac wave is sinusoidal not square or triangular wave what will be reason
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)