If we have 15000kw connected load in a factory than how much
power demand sanction should be taken from electricity board.
Pls provide complete calculation.
Answers were Sorted based on User's Feedback
Answer / ashish negi
the above calculation is correct but if we have to give our
demanded load to electricity dept. than the load should be
greater than the load as on starting motors , motors take 2-
3 times the full load cureent and at that time your MDI
(maximum demand index)will go beyond the calculated load.
so in that case your have to pay the penalty. so your
demanded load should be between 2500-3000 KVA.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rakesh maharjan
Remember the formula
KW=1.732 x V xI x PF
or
KW= KVA x PF, where PF = 0.8
connected load KW= Full load kw x 80%
Here in your case, connected load KW= 15000kw
so full load KW= 15000/80%=18750 KW
KVA= KW/.8
KVA=18750/.8=23437 KVA, this is the demand sanction.
I am junior Engineer.
Please verify by senior designer also.
| Is This Answer Correct ? | 5 Yes | 3 No |
Only the connected is mentioned and not the peak load.
Maximum demand is registered only if that apparent load
lingers for more than 15 to 30 minutes (as set).You have to
consider load factor(?) also .Apply for 12000 KVA MD
initially and you can apply for higher ,later.Once you get
the MD sanctioned, you can not get it reduced during the
agreement period.
| Is This Answer Correct ? | 1 Yes | 0 No |
why armature is placed in stator but not in rotor in synchronous generator ?
why the transformer ratings in kva
What is the problem of internal failure in ship engine telegraph system norcontrol?
Ceiling fan motor wiring Hi, I have 2 ceiling fans broken. The receiver/control units burned out due to lightening. One Harbor Breeze and one Hunter's I took them apart (remove receiver units). Now on both of the motor I see 4 wires coming out from each motor I really want to know the function of each wire. Are there anyway I can test to see which is which? After searching forums I know these 4 wires are from 2 sets of coils inside the motor, one is Start winding and the other is Runing winding I could not find the receiver/control unit any where, so I am planing to buy Capacitors and universal remote controls to make the fans run again. Anyone has any idea how to do the wiring, please help Thnks
transformer is working or not with supply of DC?
What do you mean by class of CTs and what is the meaning of cl 1.0, cl5P10, cl 10P10 CTs?
What information we need to prepare relay coordination chart
What is a soft start?
In alternator generally we give DC voltage to field of alternator but field (excitor)produce Ac & converts into DC by rotating rectifier(RR ) then fed to rotor .my question is why we cannot give dc voltage directly to rotor instead of Excitor & RR ?
The ohm is the unit of:(a) Charge(b) Resistance(c) Power(d) Current
what you mean by frequency of an igbt& how to find it?
why+ve is earthed in electrostatic precipitator in thermal power plant
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)