Answer / ashish negi
the above calculation is correct but if we have to give our
demanded load to electricity dept. than the load should be
greater than the load as on starting motors , motors take 2-
3 times the full load cureent and at that time your MDI
(maximum demand index)will go beyond the calculated load.
so in that case your have to pay the penalty. so your
demanded load should be between 2500-3000 KVA.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rakesh maharjan
Remember the formula
KW=1.732 x V xI x PF
or
KW= KVA x PF, where PF = 0.8
connected load KW= Full load kw x 80%
Here in your case, connected load KW= 15000kw
so full load KW= 15000/80%=18750 KW
KVA= KW/.8
KVA=18750/.8=23437 KVA, this is the demand sanction.
I am junior Engineer.
Please verify by senior designer also.
Is This Answer Correct ? | 5 Yes | 3 No |
Only the connected is mentioned and not the peak load.
Maximum demand is registered only if that apparent load
lingers for more than 15 to 30 minutes (as set).You have to
consider load factor(?) also .Apply for 12000 KVA MD
initially and you can apply for higher ,later.Once you get
the MD sanctioned, you can not get it reduced during the
agreement period.
Is This Answer Correct ? | 1 Yes | 0 No |
WHAT MEANT BY SEVICE FOCTOR?
Explain Creepage Distance of Insulator
what is lumped and distributed elements?
I COMPLITED MY B.TECH AND 10TH CLASS WITH 70%MARKS BUT 12TH CLASS 55%MARKS..CAN I GET INDIAN RAILWAY RECUREMENT EXAMINATION?
If Earthing is poor in a DB of of Residential Building, will residents feel a leakage voltage in a Electrical Ssytem? is this statement true?
1 Answers Dolphin International,
what is function of rtu?
why ht11kv supply needs discharging during shut down time
what is the healthy specific gravity of lead acid battery used in DG sets ?
3 Answers Bhushan Power Steel,
How can we do megger test of cable??
what should be the minimum rating for using HT Motors?
What happens if fuse is connected to neutral wire
Whether cable is designed for different fault currents?