What are the technical reasons for soaking transformers for
various times before allowing them to pick load after a
fault ?
Answers were Sorted based on User's Feedback
Answer / al kafaah
I think the transformers are soaked with normal operating
voltage level as testing with HV of the transformer
insulation, winding at site is impractical as well not
economical. Besides soaking allows the transformer
insulation to be tested for operating voltage such as oil
(so that oil inside is not breaking down) or winding
insulations, short circuits, inter-turn faults (though
these items are individually tested for its correctness at
site test, but not as a whole unit at Normal operating
voltage). Whereas the Switchgears and Cables which are
other Primary circuit components are tested with High
voltage even at site
| Is This Answer Correct ? | 25 Yes | 8 No |
Answer / japjeev
The soaking process is to determine the sufficiency of the
cooling oil for continuous operation under temperature and
duty cycles.
If an outage occurs placing heavy load currents on a
transformer it must be assured that it will survive without
exploding, melt-down, etc
| Is This Answer Correct ? | 15 Yes | 15 No |
Answer / larry dorich
Soaking a transformer before putting a load on it is Definitely old school. Transformer Mfg.'s recommended energizing with voltage even at 50% of rated Voltage @ 50/60 Hz for 24 hours .The 60 Hz allowed the oil to saturate all the paper insulation in the windings. With out doing this the paper would burn @ full load which really would de rate the Transformer & contaminate the oil.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / j.kesavan
sorry friend, soaking trs we are using in vsd drives why we
want to reduce the hormonics in power system.
| Is This Answer Correct ? | 0 Yes | 30 No |
What happens if we give ac supply to dc shunt and series motors individually
Wat is power factor exact meaning in terms of technical terms plz explain ?
What are the probable causes for failure of heating elements
what happen when power factor of 2 parallely operated transformer become equle?
What type of tranformer generaly at soft wares like capacity 2000 kva 1800 kva etc iam confused it CT or PT OR distribution tranformer
why we use end termination kit for ht xlpe cables
What is NDR in HT capacitor panels.
toughest decision you ever had to make
If there is volagte between earth and neutral, what should be the reason ? and solution * What should be allowable limit in case, if the voltage between earth and neutral exist ? / OR what is limit for safe voltage between earth and neutral?
What is difference between A.C & D.C Resistance ?
WHAT IS THE DIFFERENCE BETWEEN NUTREL AND EARTHING
can i have the methods of speed controls for 3 phase AC MOTORS.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)