Answer / al kafaah
I think the transformers are soaked with normal operating
voltage level as testing with HV of the transformer
insulation, winding at site is impractical as well not
economical. Besides soaking allows the transformer
insulation to be tested for operating voltage such as oil
(so that oil inside is not breaking down) or winding
insulations, short circuits, inter-turn faults (though
these items are individually tested for its correctness at
site test, but not as a whole unit at Normal operating
voltage). Whereas the Switchgears and Cables which are
other Primary circuit components are tested with High
voltage even at site
| Is This Answer Correct ? | 25 Yes | 8 No |
Answer / japjeev
The soaking process is to determine the sufficiency of the
cooling oil for continuous operation under temperature and
duty cycles.
If an outage occurs placing heavy load currents on a
transformer it must be assured that it will survive without
exploding, melt-down, etc
| Is This Answer Correct ? | 15 Yes | 15 No |
Answer / larry dorich
Soaking a transformer before putting a load on it is Definitely old school. Transformer Mfg.'s recommended energizing with voltage even at 50% of rated Voltage @ 50/60 Hz for 24 hours .The 60 Hz allowed the oil to saturate all the paper insulation in the windings. With out doing this the paper would burn @ full load which really would de rate the Transformer & contaminate the oil.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / j.kesavan
sorry friend, soaking trs we are using in vsd drives why we
want to reduce the hormonics in power system.
| Is This Answer Correct ? | 0 Yes | 30 No |
could anybody able 2 send me jindal steels previous papers fr electrical steam....pls send 2 my id if possible....sirisha.shaik@gmail.com
what is sinwave ups
how to calculate the megger values for motors and cables?
what is difference between the buscoupler and bus raiser?
Is it good to short Neutral and Ground in the PLC or DCS main Power supply. Pls give YES or NO with reasons...? Simarpreet
what is the max. acceptable leakage current in 33kv bus bar
which fault current is maximum: 3 phase short circuit, LG, LL or LLG?? why?? in one of the problems that i have solved, 3 phase short circuit current on an unloaded generator came out to be less than the LG fault current. can anybody please explain why.
How do you convert the lt amps on a transformer to the ht amps?
A 400KVA transformer has 400 Hz frequency. If the frequency is changed to 50 Hz, then what will be the new KVA rating?
when the direction of a 3phase induction motor is reversed , is there any losses increases?
Can anyone explain, How will get positive to ground and negative to ground reference voltage in dc system
How cable from Kit-Kat to main switch, from starter to motor are designed?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)