Wat is power factor exact meaning in terms of technical
terms plz explain ?
Answers were Sorted based on User's Feedback
Answer / sachin
Power factor Basics
In all industrial electrical distribution systems, the
major loads are resistive and inductive.
Resistive loads are incandescent lighting and resistance
heating. In case of pure resistive loads,
the voltage (V), current (I), resistance (R) relations are
linearly related, i.e.
V = I x R and Power (kW) = V x I
Typical inductive loads are A.C. Motors, induction
furnaces, transformers and ballast-type
lighting. Inductive loads require two kinds of power: a)
active (or working) power to perform
the work and b) reactive power to create and maintain
electro-magnetic fields.
Active power is measured in kW (Kilo Watts). Reactive power
is measured in kVAr (Kilo
Volt-Amperes Reactive).
The vector sum of the active power and reactive power make
up the total (or apparent)
power used. This is the power generated by the SEBs for the
user to perform a given amount of
work. Total Power is measured in kVA (Kilo Volts-Amperes)
The active power (shaft power required or true power
required) in kW and the reactive
power required (kVAr) are 90° apart vectorically in a pure
inductive circuit i.e., reactive power
kVAr lagging the active kW. The vector sum of the two is
called the apparent power or kVA, as
illustrated above and the kVA reflects the actual
electrical load on distribution system.
The ratio of kW to kVA is called the power factor, which is
always less than or equal to
unity. Theoretically, when electric utilities supply power,
if all loads have unity power factor,
maximum power can be transferred for the same distribution
system capacity. However, as the
loads are inductive in nature, with the power factor
ranging from 0.2 to 0.9, the electrical dis distribution
network is stressed for capacity at low power factors. So
COS PHI= KW/KVA
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / balu
power factor is the ratio between active power and apparent
power. apparent power = active power + reactive power.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mubeen
a angle between voltage and current on running load is
called power factor.If its value is increase performance of
motor or equipment will improve.
| Is This Answer Correct ? | 0 Yes | 3 No |
What is the size of cable to be used for a Space Heater in UPS 160KVA of carrying 10 Amps current with 240 V ,1 Phase?
i am electrical engineer i cant get job in pure electrical industry ,but i got job in instrumentation field whether there is good scope for me, as i am fresher i m not well with the industrial trends so any experienced engineer pls reply me
what is defference by mcb,mccb and mpcb
types of transformer ?
what is the difference between ac and dc generator
AT THE TIME OF INSTALLING THE POWER PLANT POWER IS TAKEN FROM NEARBY GRID AND GIVING THE SUPPLY TO THE GENERATOR WHICH ACTS AS MOTOR. WHAT IS THE NEED OF RUNNING THE GENERATOR AS MOTOR?
In a generator (Synchronous) does the rotor speed (frequency) corresponds to the speed of the water (in hydro). does the torque on the turbine relate to the flow of water?
which winding aply in an alternator?
What is Residual Voltage & Residual Current?
Why 1/3 is used in symmetrical components?
PAC and simple Ac different
what is difference b/w squirrel cage rotor and wound rotor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)