Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What is working principal of V.C.B., O.C.B., A.C.B & Over load
relay?

Answers were Sorted based on User's Feedback



What is working principal of V.C.B., O.C.B., A.C.B & Over load relay?..

Answer / anjireddy boduggam

VCB - vacuum ckt. Breaker , Quenching medium - Vacuum,
ACB - Air ckt. Breaker , Quenching medium - Air,
OCB - oil ckt. breaker , Quenching medium - Oil
above in all ckt. breakers different quenching medias are
using.
The above all ckt. Breakers principle is same, but medias
are used for arc quenching purpose.

OLR - over load relay , when current exceeds over setting
point, then action will be started and disconnected the
load supply by relay action.No medium is used in the OL
relay, but it works on bi-metallic action.

Is This Answer Correct ?    18 Yes 1 No

What is working principal of V.C.B., O.C.B., A.C.B & Over load relay?..

Answer / zubair

ACB MEAMS AIR CIRCUIT BREAKER.
VCB MEANS VACCUM CIRCUIT BREAKER.
OCB MEANS OIL CIRCUIT BREAKER.
ALL THE ABOVE USED TO TRIP THE CIRCUIT,WHEN EVER THEIR IS A
FAULT AT THE LOAD SIDE, like short circuit,excess current
consumption beyond the rated value
THE DIELECTRIC STRENGTH OF VCB IS HEIGHER THAN ACB.THE ARC
EXTINGUISHER CAPACITY OF VCB IS HEIGHER THAN ACB.HENCE VCB
IS USED FOR HIEGHER VOLTAGES AND RATINGS.
THE OLR(OVER LOAD RELAY)IS ALSO USED TO TRIP THE
CIRCUIT ,WHEN EVER THE LOAD TAKES HIGER CURRENT BEYOUND
RATED VALUE, BUT THE APPLICATION IS LIMITED TO 20A.

Is This Answer Correct ?    9 Yes 0 No

What is working principal of V.C.B., O.C.B., A.C.B & Over load relay?..

Answer / sanjay kumar

Transformer Mai oil konsa hota Hai Transformer oil temperature winding temperature kitna hona chahiye on load

Is This Answer Correct ?    5 Yes 0 No

What is working principal of V.C.B., O.C.B., A.C.B & Over load relay?..

Answer / priti ranjan mohapatra

V.c.b - it stands for vaccum circuit breaker. It used in mv line as 36, 33 kv. In this the contact point of the cb remains in vaccum when it is off.

Is This Answer Correct ?    8 Yes 8 No

Post New Answer

More Electrical Engineering Interview Questions

In case of 3Phase Supply, Voltage R-Earth/Neutral - 220 Y-Earth/Neutral - 220 Z-Earth/Neutral - 220 Total is -> 660Volts Then Why it is said that 3Phase supply is 440

6 Answers   Hindustan Unilever Limited,


What are formula we can apply to determine the HT/LT current of 11KV/433V transformer except KVA/LV×√3. ?

2 Answers  


How to derive detailed design of Suitable bus Bar for 100A for 6.6KV?

0 Answers  


pre arcing time of ehv breaker

0 Answers  


Power systems

0 Answers   LB Engineering,


what is the power factor used by the PHCN in nigeria? 2. what is the difference between an alternator and generator. 3. Generation of poweris in KV but how is transmission is in MW. 4.If the transmission of power is 20,000MW how can it be increaesed to 80,000MW

0 Answers  


why do we use LPF wattmeter not UPF in the experiment of no load and blocked rotor test of 3phase slipring induction motor?

3 Answers   Matrix,


I find that underground strip-armoiured,4core,LT PVC cables in an earthed power distribution sytem are occasionly found in charred condition-with no trace of it except ash. Is this because of no proper earth connection/continuity (giving rising to high armour resistance)in the joint enroute or because of insufficient capability (again due to high armour resistance)of cable-armour to carry fault current or due to neglected /unprotected overloading of the cable or due to high armour currents caused by power thefts where only phase(s) are unauthorisely tapped & at the point of poer consumption earth terminal is established by burring underground a not so good earthing rod (or using an underground water pipe for the purpose)

1 Answers  


in Contactor opearation Why there is a difference in the values of the operate and release voltage in case AC supply

0 Answers  


How to calculate the current carrying capacity of sized cables, and there is any formula. please send to 'than.achu@yahoo.com'

1 Answers   Blue Star,


how will i find Transformer rating if supply voltage is 11k.v and how will i find incomer if transformer rating is 12MVA

3 Answers  


How to calculate transformer capacity requirement for a project site?

5 Answers   ABB,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)