Answer / anjireddy boduggam
VCB - vacuum ckt. Breaker , Quenching medium - Vacuum,
ACB - Air ckt. Breaker , Quenching medium - Air,
OCB - oil ckt. breaker , Quenching medium - Oil
above in all ckt. breakers different quenching medias are
using.
The above all ckt. Breakers principle is same, but medias
are used for arc quenching purpose.
OLR - over load relay , when current exceeds over setting
point, then action will be started and disconnected the
load supply by relay action.No medium is used in the OL
relay, but it works on bi-metallic action.
Is This Answer Correct ? | 18 Yes | 1 No |
Answer / zubair
ACB MEAMS AIR CIRCUIT BREAKER.
VCB MEANS VACCUM CIRCUIT BREAKER.
OCB MEANS OIL CIRCUIT BREAKER.
ALL THE ABOVE USED TO TRIP THE CIRCUIT,WHEN EVER THEIR IS A
FAULT AT THE LOAD SIDE, like short circuit,excess current
consumption beyond the rated value
THE DIELECTRIC STRENGTH OF VCB IS HEIGHER THAN ACB.THE ARC
EXTINGUISHER CAPACITY OF VCB IS HEIGHER THAN ACB.HENCE VCB
IS USED FOR HIEGHER VOLTAGES AND RATINGS.
THE OLR(OVER LOAD RELAY)IS ALSO USED TO TRIP THE
CIRCUIT ,WHEN EVER THE LOAD TAKES HIGER CURRENT BEYOUND
RATED VALUE, BUT THE APPLICATION IS LIMITED TO 20A.
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / sanjay kumar
Transformer Mai oil konsa hota Hai Transformer oil temperature winding temperature kitna hona chahiye on load
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / priti ranjan mohapatra
V.c.b - it stands for vaccum circuit breaker. It used in mv line as 36, 33 kv. In this the contact point of the cb remains in vaccum when it is off.
Is This Answer Correct ? | 8 Yes | 8 No |
what is the reason for indication of light in the earth lamps of main switchboard.if there is an earth why does one lamp get dim and the other two bright.
Is the installation of the filter cloths necessary before spreading the gravels at the transformer yards?
What is difference between start imitation and start interlock for 3 phase motor protection ?
We use MCCB not MCB for motor starters because MCCBs has capablity to drawout the motor starting current which is 5-6 times the full load current of motor for 1sec. Then why we use SDF in starter panel means MCC panels. Pls reply if any one knows this answer.
HOW WE WILL CONNECT THE PHASE CTS AND NEUTRAL CTS TO REF RELY
What is the difference between earth and neutral
4 Answers ABB, Tamboli Engineers,
in india why the generating voltage is like 11kv,22kv etc
what is the full Form of AAC ant conductor?
how many types of cbs?with pcific ratings?
why a motor rating in KW?
What is Biased Generator Differential Relay?
If you see the HRC fuse name plate. Its shown ampere rating shown which is in many KA (like 80KA and so on). any body explain what is meaning of this value?