In case of 3Phase Supply,
Voltage R-Earth/Neutral - 220
Y-Earth/Neutral - 220
Z-Earth/Neutral - 220
Total is -> 660Volts
Then Why it is said that 3Phase supply is 440
Answers were Sorted based on User's Feedback
Answer / sachin mahangade
this voltage measure in R-Y 440v Y-B 440v RB-440 v so this
said that 3 phase R-Y-B supply is 440 v
| Is This Answer Correct ? | 25 Yes | 5 No |
Answer / jmdt
we are calculating in phase to pase oly , so r-y, y-b, b-r
is 440 volt
| Is This Answer Correct ? | 17 Yes | 5 No |
Answer / zubair
in three phase supply there are three phases (here R, y,
and z) and only one neutral.
the voltage between any one phase and neutral is 220.
and the voltage between remaining two phases is 440.hence
the 3 phase supply is 440
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / padmavathi
If we measure R-Earth/ Neutral that is 1 PH. 3 Phase, 440V
means we have to measure Phase - Phase i.e. R-Y, Y-B, R-B
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / vinoth
the vole meter have 2 terminals only.... then how can we
mesure in 3 phase voltage... only chance mesure in 2 phases
only the 2 phase voltage 440
| Is This Answer Correct ? | 4 Yes | 5 No |
Answer / n
220 Multiply by root three is equal to 281.4 volts. for 440
volts single phase voltage up to 254 volts.
| Is This Answer Correct ? | 3 Yes | 8 No |
why we cant use AC supply products in DC supply?
if step down transformer step down the voltage,will current will also be proportional step up. If yes then how transformer handle such a large current?
what is diff. b/w of earth & neutral?. why we are separately using ?
What is the different between feeder & bus?
what is the use of permanent magnet generator in exciter
what the Microsoft .NET framework is?
What is the minimum distance between taransformer (say 2000 kva)and its earth pit?
What will happen if apply dc source for power transformer
How can we calculate D.C.Load current in terms of A.C. load current?
1.what is the reason for transformer and lightning arrester blast in 33kv system
what happens when power factor leads or lags to electical or home appliances
HAI,I HAVE 6,60KW MOTOR FEEDERS IN MY MCC PANEL.HOW CAN I DO MY SETTINGS FOR OVERLOAD,SHORTCIRCUIT,GROUNGFAULT,INSTANTANEOUS TRIP FUNCTION IN MY 4000A CIRCUIT BREAKER?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)