why do we use LPF wattmeter not UPF in the experiment of no load and blocked rotor test of 3phase slipring induction motor?
Answers were Sorted based on User's Feedback
Answer / pritish
in case of no load test, the supply voltage is rated but the current drawn by the induction motor is very less; no load current, which produces only the core loss of the stator and some mechanical loss. in no load condition, the angle between V and I are high as a factor the pf will be less. hence to calculate the pf accurately LPF wattmeter is used. during loaded condition current increases and angle decreases hence pf increases.
any more clarification regarding this should be sent to pritish.nath@gmail.com
Is This Answer Correct ? | 36 Yes | 3 No |
Answer / saurabh wani
We use LPF only for no load test because at no load only reactive component of current flows in any machine. In 3 phase induction motor magnitude of reactive component current is more because of air gap. So power factor under no load operation is low and we use LPF wattmeter . If we use here UPF then it will give reading at time of starting only and after 3to 4 sec pointer will stable at zero no deflection.
Is This Answer Correct ? | 3 Yes | 1 No |
what is maximum demand.
In electric motors, according to the no. of compartments, The no. of input's (pantagraph collector's) were increased, why?
why transformer ratinh is in KVA????/
8 Answers Apollo, Priyadarshini, Reliance,
what is charger supervision and control supervision?
HOW DO I CALCULATE THE SETTINGS FOR THE DIFFERENTIAL PROTECTION OF A 12kV/6.6kV, 6MVA,DYN11 XMER WITH PRIMARY SIDE CTR 400/1 AND SEC SIDE CTR 600/1?
while calculating the power absorbed by a resistor connected to the output of a half wave rectifier circuit should we use rms or average current? explain with reason.
How to calculate Earth busbar size & what is the procedure we make for determine that?
WHAT IS THE ANALYSIS OF FREE WHEELING DIODE IN FULL WAVE CONROL RECTIFIER?
How to connect the chemical earthing and complete process tell me plz
where can i get vijaya electricals limited in hyderabad interview auestions can u give me the website address plz
how much current does 3ph. 10 hp ac motor draw.
Why the transformers are rated in KVA ? in new view