Answer / mahesh sali
THE CAPACITY OF TRANSFORMER USED FOR SITE APPLICATION SHALL
BE CALCULATED BY FOLLOWING CONSIDERATION;
CAL.TOTAL CONNECTED LOAD
BASE ON KW & ASSUMATION OF 0.8 P.F.
CAL. THE KVA/ MVA RATING OF X'MER I.E. KW/0.8
AFTER GETTING KVA/MVA ADD THE 20% IN CAL.KAV/MVA
I.E. KVA/MVA + 0.2*KVA/MVA
20% EXTRA AS PER IEEE RULE
AS PER IEEE NORM ,UR TRANSFORMER SHOULD BE LOADED AT 80% OF
UR FULL CAPACITY OF UR TRANSFOMER.
I HOPE ABOVE INF. IS SUFFICIENT.
THANKING U
| Is This Answer Correct ? | 26 Yes | 1 No |
Answer / vathnak kong
Example
We have Power load 2300KVA
So
Transformer Capacity=2300×1.4
1.4 is Power rate
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / sivaguru
Hi Mr.Mahesh
Can you please forward the IEEE rule showing the
transformer loading of 80% of full load as you
discussed....Kindly forward it to my email id
sivaguru_691984@yahoo.co.in...
Even we haven't took tr. loading factor for all our
projects and we will be really educated by pupil like you
for the need of consideration of transformer loading
factor...
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / thanigai1984
Now a days...
we calculated the connected load ...in KW and 40%
assumption load will be added
Transformer cap=60% load connected +40%
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / sunil biswal
Calculate all connected loads(KW) Assume Fans as 65Watt,15A sockets as 1000Watt, 5A Sockets at 1ooWatt, TV at 120 Watt Computer at 120Watt, Printer/Scanner/Copier at 1000Watt, A/C 1.5 Ton at 1.5KW
Apply diversity Factor since all loads will not be working at the same time always
Divide the single phase loads into 3 parts. (KW)
Then add three phase loads and i/3rd single phase loads(KW)
add 20% extra to this calculated gross KW
Divide by power factor 0.8 to get KVA Rating of transformer.
At this point you may add another 20% to the rating as a factor of safety and reliability since most machine work comfortably at 75 to 80% loading
Now decide the actual rating of transformer in proper slab as the standard ratings transformer are available in are 10KVA,16KVA,25KVA,63KVA,100 KVA, 125KVA, 160KVA, 200KVA, 250KVA, 500KVA in 11KV range.
| Is This Answer Correct ? | 1 Yes | 0 No |
What is a captive power plant?
What is the full form of CNC in electrical mechines.......?
FRIENDS, I am doing DEEE (part time)final year. Give me some ideas for project
How big (size) can the tertiary winding be in transformer? Can we load the tertiary winding, if yes then how much we can load it?
How to calculate meter constant @ HT yard
WHAT IS counter flux IN CT?
what is the advantage of using 3 phase line rather than using 2 phase line?
can a 12v dg starting battery(150 AH) be replace by 6 nos of 200AH batteries each of 2v connected in series.
what is the difference b/w ground & virtual ground?
Define stepper motor. What is the use of stepper motor?
How to calculate the size of earth cable to earth the neutral of UPS ?
please tell me formula of 3 phase induction motor under condition{1]when we 3 phase motor starts without load in star or delta connection?thanks
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)