I find that underground strip-armoiured,4core,LT PVC cables
in an earthed power distribution sytem are occasionly found
in charred condition-with no trace of it except ash. Is
this because of no proper earth connection/continuity
(giving rising to high armour resistance)in the joint
enroute or because of insufficient capability (again due to
high armour resistance)of cable-armour to carry fault
current or due to neglected /unprotected overloading of the
cable or due to high armour currents caused by power thefts
where only phase(s) are unauthorisely tapped & at the point
of poer consumption earth terminal is established by
burring underground a not so good earthing rod (or using an
underground water pipe for the purpose)
Answer / k.prakashchandra
Do not earth both the ends of armour ,only one end is to be
earthed
| Is This Answer Correct ? | 0 Yes | 0 No |
Why should we hire you over the others waiting to be interview?
which motors is used in mixies
a simple c++ program to calculate simple interst with its data members as private
why overload relay is not tripped at time of starting of motor allthough staring current is too high?
Explain the advantages and disadvantages of thermal power plant?
Is it mandatory statutory requirement of transformer oil filtration annualy despite oil is withstanding required dieelectrical strenth and all others parameters
Why Delta Star Transformers are used for Lighting Loads.
In Power Line Communication (PLC) the wave trap is used to block communication signals from entering neighboring lines. My question is this: Why do they allow for different filtering arrangements on these wave traps? Isn't it always going to be a low pass filter since we want the power frequency to go through, and the comm signal blocked?
URGENT PLEASE//////////A WORK SHOP IS HAVING A 100 KVA TRANSFORMER 11KV/415 VOLTS, AND THE CONNECTED LOAD OF THE WORK SHOP IS 80 KW WITH INDUCTIVE LOADS, LIGHTING LOADS,ETC., HOW MANY EARTH ELECTRODES ARE NEEDED AND WHAT IS THE EARTH RESISTANCE OF EACH EARTH ELECTRODE AND COMBINED EARTH RESISTANCE in normal soil. AT 11 KV SIDE AND AT LT SIDE. HOW TO CALCULATE.
If current and resistance in a circuit is increased by 20%, what will happen to its voltage drop??
From reading, Under voltage relay used also as phase sequence relay now, Why I use under voltage and phase sequence relay in the same circuit (ATS)?
I am working in transmission network, one of my 66kv line having short distance about 6km, when sending end voltage is 67kv receiving end get 69kv, i want to know that, does distance affects in this matter, please explain in this matter & if possible answer me on my mail id, kaushikkumar.vanavi@getcogujarat.com, kaushik.vanavi@gmail.com
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)