I find that underground strip-armoiured,4core,LT PVC cables
in an earthed power distribution sytem are occasionly found
in charred condition-with no trace of it except ash. Is
this because of no proper earth connection/continuity
(giving rising to high armour resistance)in the joint
enroute or because of insufficient capability (again due to
high armour resistance)of cable-armour to carry fault
current or due to neglected /unprotected overloading of the
cable or due to high armour currents caused by power thefts
where only phase(s) are unauthorisely tapped & at the point
of poer consumption earth terminal is established by
burring underground a not so good earthing rod (or using an
underground water pipe for the purpose)
Answer / k.prakashchandra
Do not earth both the ends of armour ,only one end is to be
earthed
| Is This Answer Correct ? | 0 Yes | 0 No |
What is an order of a system.
explain working principle of earth leakage relay
0 Answers Divis Laboratories, SMIORE,
A electrical meter has load 500 kw. In 2 hr what rading will come on meter.
DEAR SIR, HOW TO CALCULATE WELDING TRANSFORMER CAPACITY IN KW OR KVA (POWER). TWO WELDING TRANSFORMER USED WHAT TYPE OF DG SET CAPACITY LIKE ( 45 KVA OR 62.5 KVA), PLEASE TELL THE WELDING TRANSFORMER RATEINGS. I AM REFINARY (TANKS WELDING) THANKING YOU
if the armature current in a dc generator is ac ( sinusoidal ) why doesnt the sjhape af armature mmf a sinusoidal (ni) ? armature mmf in case of a dc machine is triangular.
I have a situation to design sub-Distribution board/Panel meant for feeding power sockets. In the incomer CAN i Take TP MCCB with Neutral Link and All the outgoing feeders with to sockets with TP MCCB and Neutral Link? P.S : My System is IT Earthing
A shopkeeper allows 10% discount on the price of an article and sells it for Rs 7,600. What is the marked price of the article?
how to calculate the kw, Amps consumed by a capacitor, give me the formula for KVAr into capacitance,KVAr into KW & KVA, Amps
what is the formula for calculation of sac?
how nautral is provided for return path is 3 phase induction motor
why we don't discuss power facter in dc?
what is the breakdown voltage value in BDV test in transformers?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)