I find that underground strip-armoiured,4core,LT PVC cables
in an earthed power distribution sytem are occasionly found
in charred condition-with no trace of it except ash. Is
this because of no proper earth connection/continuity
(giving rising to high armour resistance)in the joint
enroute or because of insufficient capability (again due to
high armour resistance)of cable-armour to carry fault
current or due to neglected /unprotected overloading of the
cable or due to high armour currents caused by power thefts
where only phase(s) are unauthorisely tapped & at the point
of poer consumption earth terminal is established by
burring underground a not so good earthing rod (or using an
underground water pipe for the purpose)
Answer / k.prakashchandra
Do not earth both the ends of armour ,only one end is to be
earthed
Is This Answer Correct ? | 0 Yes | 0 No |
HOW TO CALCULATE HV CABLE SIZING?
how to decide no of electrodes for 1600A LT Main incomer panel
What is the simplest formula to calculate the rotor diameter of a synchronous generator?
defination of a.c filter
1-What is the difference between absorption factor and polarization factor in insulation resistance test in transformers? and why we inject until ten minutes to get polarization factor?
What aturn on methods of scr?
How can we find out earth leakage,(shock)in side the house?.. (with out ELCB)
Why current Transformer is rated by 100A/5A/5A?
Is KCL applicable for close circuit?
How select ELCB for 32amp. socket having quantity 12Nos. We have to do this wiring in PLANT. Please Also explain the incoming cable specification.
0 Answers Gulf Industrial Services Company GISCO,
Benifits of 3ph 4 wire metering over 3ph 3 wire
In case of 3 phase motor why it is called single phasing by failure of one phare unless there is rest two phase are acting. ?